Split level house with all zone loops higher than basement
Three zones - all thermostats working properly
Circulator pump on the cold/return side of boiler mounted just above
boiler inlet
comes on with furnace (zone independent)
Flo-control valve on the hot/supply side of boiler mounted near ceiling
Air separater right after main flo-control valve with bladder expansion
tank
Three additional zone circulator pumps connected to the thermostat
relays
Three zone flo-control valves, one right after each zone pump
The problem is that whenever any zone calls for heat there is flow thru
all three zones. I verified that each of the zone pumps are working
independently and correctly. He told me that the system has always
operated this way and he just sets the thermostat on the upper level to
50 so it never kicks on because he always gets heat up there.
There are no zone valves on any of the zones, only the flo-control
valves. The zone pumps, flo-control valves and thermostats appear to
be add-ons to the original system.
I would like to hear ideas on possible repairs or system changes that
would get the system to only heat the zone(s) that is calling for heat.
Find out what is letting hot water flow through non-calling
zones.
Fix it.
Any moe detailed advice than that requires someone who knows
what they're doing to be there and examine the system.
--
Click here every day to feed an animal that needs you today !!!
http://www.theanimalrescuesite.com/
Paul ( pjm @ pobox . com ) - remove spaces to email me
'Some days, it's just not worth chewing through the restraints.'
'With sufficient thrust, pigs fly just fine.'
HVAC/R program for Palm PDA's
Free demo now available online http://pmilligan.net/palm/
Doesn't having the pump(s) only on the outlet side of the boiler
increase the chance of a boiler overtemp?
I suppose I could just disconnect it and run each zone for 20 minutes
and see what happens.
Of course most of the houses in this area have the shingles overhanging
the sheathing by 1.5" so they hang in the gutter but that isn't right.
Could have been the previous owner had it 'zoned' because it was colder
in some parts and was sold all these extra circulator pumps and relays
when all he needed were a few zone valves.
http://www.weil-mclain.com/FTP/GOLD_Oil_Manuals/Wgoboilermanual.pdf
Bob
"RayV" <Nunya...@comcast.net> wrote in message
news:1162466333.1...@k70g2000cwa.googlegroups.com...
"RayV" <Nunya...@comcast.net> wrote in message
news:1162407528.5...@k70g2000cwa.googlegroups.com...
At the same level as the boiler inlet or lower.
>
> You're right about less air problems with the circ on the supply side.
> Do you know why that is?
Higher pressure from the hotter water raising the boiling point?
>
> Where should the fill valve be?
Close to the boiler inlet.
> Why?
Because it is easier to run the piping?
One pump on the return side at boiler inlet
Three pumps parallel on the outlet side after air separator/expansion
tank
Three flo-control valves after each pump on the outlet side
No zone valves but the flo-control valves are also check valves
http://www.bellgossett.com/Press/BG-flocontrol.asp
How would a 'check valve' on each pump discharge solve what seems to be
an unneeded pump on the inlet side that is pushing hard enough to lift
the flo-control valves in the two zones not calling?
I'm going to disconnect the pump on the return side of his system and
run the zones to see if that cures the problem of non-calling zones
always getting hot.
Thanks again.
I see what are you saying
check and examain valves see that valve is doing
what it it should be doing
Dido
--