How did you move it?
More seriously, tell us about this "moving the AC" bit? Moved by
whom, and did he check for leaks, superheat, subcooling, etc? Did
the AC mover clean the coils, charge by weight, or....
Tell us more.
--
Christopher A. Young
You can't shout down a troll.
You have to starve them.
.
<david.s...@gmail.com> wrote in message
news:1178850751.6...@p77g2000hsh.googlegroups.com...
: Just moved my 2.5 ton split unit upstairs, and only the bottom
:
I moved the system myself. Took the air handler/furnace/evaporator
to
the attic, moved the condenser to the side of the house, re-braized
the refer. lines, and added an extrenal liquid-line filter/dryer.
checked for leaks, and the pressure test checked out. I cleaned both
the condenser and evap. coils thoroughly. Didn't check for
subcooling
or superheating, that bit is beyond me. Haven't thought aboout that
stuff since thermodynamics in college... I did add about
10' of refer. line, which leads me to believe I need more referigant.
BUT, before I do any more work, I want to know if anyone has ever
experienced the same symptoms (only 1/3 of the A-coil is cold), and
does it make sense that this may be due to low refer. level. I won't
be able to get to my gauges or referigerant for another week, but I'd
like to close up the supply ducts in the mean time. Thanks for your
help!
On May 10, 10:44 pm, "Stormin Mormon"
<cayoung61**spambloc...@hotmail.com> wrote:
> Might have to do with the altitude. Try hooking an air compressor
> to the room and make sure the room is inflated to 14.7 PSI.
>
> More seriously, tell us about this "moving the AC" bit? Moved by
> whom, and did he check for leaks, superheat, subcooling, etc? Did
> the AC mover clean the coils, charge by weight, or....
>
> Tell us more.
>
> --
>
> Christopher A. Young
> You can't shout down a troll.
> You have to starve them.
> .
>
> <david.schaf...@gmail.com> wrote in message
So after you brazed the line set... did your pressure check...
What did you do next?
Ideas?? Sure I have several, and they all have to do with calling a
*competent*, licensed, insured, professionally trained, HVAC technician to
come fix your f*ck-ups.
Let me guess... a "*competent*, licensed, insured, professionally
trained, HVAC technician" like you? Thanks but no thanks, friend.
The above seems to mean you did NOT recover the old refrigerant, evacuate
the system, and re-charge with new refrigerant. Yes? No? (no... you can't
get to your refrigerant yet) But you cut the lines. Hmmmmm.....
If you don't have gauges, which implies 'other' fittings/adaptors as well,
how did you pressure test it properly? Tire pump? How'd you tell what
pressure you brought it up to?
How would having insufficient charge keep you from closing up the supply
ducts while you wait?
LLoyd
<david.s...@gmail.com> wrote in message
news:1178862596....@p77g2000hsh.googlegroups.com...
> Sounds like someone has a small penis.
>
> On May 10, 11:57 pm, "Noon-Air" <Noon-...@comcast.net> wrote:
>> <david.schaf...@gmail.com> wrote in message
Thats your choice. Just remember that when you have to make that call to get
it done right.
Close some ducts if you like. I'd be tempted to leave em all open
unless some rooms you don't use.
--
Christopher A. Young
You can't shout down a troll.
You have to starve them.
.
<david.s...@gmail.com> wrote in message
:
: On May 10, 10:44 pm, "Stormin Mormon"
: <cayoung61**spambloc...@hotmail.com> wrote:
: > Might have to do with the altitude. Try hooking an air
compressor
: > to the room and make sure the room is inflated to 14.7 PSI.
: >
: > More seriously, tell us about this "moving the AC" bit? Moved
by
: > whom, and did he check for leaks, superheat, subcooling, etc?
Did
: > the AC mover clean the coils, charge by weight, or....
: >
: > Tell us more.
: >
: > --
: >
: > Christopher A. Young
: > You can't shout down a troll.
: > You have to starve them.
: > .
: >
: > <david.schaf...@gmail.com> wrote in message
: > :
:
:
--
Christopher A. Young
You can't shout down a troll.
You have to starve them.
.
"Lloyd E. Sponenburgh" <llo...@mindspring.com> wrote in message
news:4644549d$0$4646$4c36...@roadrunner.com...
:
: The above seems to mean you did NOT recover the old
:
>I was thinking pumping the system down, but how to know when it's
>pumped, if you don't have a gage on the low side? A lot of this
>post doesn't add up, but I'm willing to play the game for awhile.
>
>
David, you have to have all the proper tools and test instruments and
know-how to do that job right.
No vac pump to properly evacuate the refrigerant lines and the
evaporator several times before releasing the refrigerant from the
condenser, assuming you did a pump-down?
http://www.udarrell.com/ac-trouble-shooting-chart.html - udarrell
--
WISDOM PRINCIPLE DIRECTED EMPOWERMENT COMMUNICATIONS -
THE REAL POLITICAL ISSUES and WISDOM BASED PEOPLE EMPOWERMENT
http://www.udarrell.com/
http://www.udarrell.com/my_pages2.htm
http://www.udarrell.com/recognizing_real_enemies.html
http://jesuschristsavior.net/Beatitudes.html
Reality Is Not An Easy Thing To Be Confronted With or to Accept!
Thanks for you help. What I did was supplement the original system,
which serviced the whole house, with a brand new 3 ton unit. The new
one now services the downstairs, and I moved the original one from
the
basement to the attic to service the upstairs. I left the original
refer lines in place and braized the new system to them. That has
been working perfectly for two seasons now, so I like to think I know
what I'm doing (kinda). Last weekend I finally got around to
installing the upstairs unit. Before I uninstalled it last year I
closed off the liquid valve and pumped all the referigant into the
condenser (Yes, I dust-capped all open tubing).
Last weekend I hooked up the gauges, pumped the lines and
evap coil down to 30 mm Hg with a vacuum pump while the the condensor
valves were closed, brazed up the lines at the condensor, and opened
the valves. Like I said, the new refer lines are about 10' longer
than
the original ones, so I bet you're right... I'm low on refrigant.
Just wanted to get the opinion of someone who has experienced my
problem before.
On May 11, 8:16 am, "Stormin Mormon"
<cayoung61**spambloc...@hotmail.com> wrote:
> I was thinking pumping the system down, but how to know when it's
> pumped, if you don't have a gage on the low side? A lot of this
> post doesn't add up, but I'm willing to play the game for awhile.
>
> --
>
> Christopher A. Young
> You can't shout down a troll.
> You have to starve them.
> .
>
> "Lloyd E. Sponenburgh" <lloy...@mindspring.com> wrote in messagenews:4644549d$0$4646$4c36...@roadrunner.com...
People _do_ it, but you know it's not a good idea to run a hermet under
vacuum? Arcy-sparky things can happen in the motor when the atmosphere gets
rarified. More likely to happen with air/nitrogen than freon, but still...
LLoyd
There was bound to be some refrigerant left on the low side, if you used the
compressor for the 'recovery' pump. That would have been what you lost when
you broke the lines; might be the source of the low charge. It ran for a
while... ok... but it might have been low from the git-go, and with some
slow leaks at the service valves/whatever, you lost enough more to send it
under the table.
LLoyd
>Stormin and Lloyd-
>
>Thanks for you help. What I did was supplement the original system,
WTF do you post everything three times for ????
Cause he's posting to the mormun and spongebob.
<david.s...@gmail.com> wrote in message
He's talking about TWO complete systems.
Glad you added the "(kinda)" behind "I know what I'm doing" as not many
people "that know what they're doing" will reuse the old line set.
--
Christopher A. Young
You can't shout down a troll.
You have to starve them.
.
"Lloyd E. Sponenburgh" <llo...@mindspring.com> wrote in message
news:46448cb4$0$4672$4c36...@roadrunner.com...
:
:
: There was bound to be some refrigerant left on the low side, if
:
--
Christopher A. Young
You can't shout down a troll.
You have to starve them.
.
<david.s...@gmail.com> wrote in message
news:1178897073....@o5g2000hsb.googlegroups.com...
: Stormin and Lloyd-
:
: Thanks for you help. What I did was supplement the original
system,
: which serviced the whole house, with a brand new 3 ton unit.
The new
: one now services the downstairs, and I moved the original one
from
: the
: basement to the attic to service the upstairs. I left the
original
: refer lines in place and braized the new system to them. That
has
: been working perfectly for two seasons now, so I like to think
I know
: what I'm doing (kinda). Last weekend I finally got around to
: installing the upstairs unit. Before I uninstalled it last
:
:
--
Christopher A. Young
You can't shout down a troll.
You have to starve them.
.
<david.s...@gmail.com> wrote in message
news:1178896933....@o5g2000hsb.googlegroups.com...
: Lloyd-
But, I bet *his* home is well air conditioned. LOL
>Just moved my 2.5 ton split unit upstairs, and only the bottom third
>of the evap. coil is cold. Would this implicate too little
>refrigerent?
yup
>Any other ideas? Thanks for your advice!
>
>DK
> I can't say as I've ever seen a perfect HVAC system, so it's
> likely to have been leaking.
How many would you like to see?
You have to remember hes use to seeing his hack ass call back shit day
after day.
I think you're stretching it a little "day after day".
It's probably more like once a month. <g>
Hopefully, for his victims sake..
It is a compressor fault, weak pumping (compression) check the
compressor pumping through discharge port of compressor, a good
compressor discharge pressure is between 350 to 450 psi and also when
you stop the compressor the discharge pressure should not drop below
350psi secondly it could also be due to clogged condensor, clean
condensor by using condensor cleaning liquid and water pressure.
Hope this helps
Joss Rock
Even if there's no refrigerant in the system? (or low on same?)
> you stop the compressor the discharge pressure should not drop below
^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
> 350psi ...
^^^^^^
Even after the gas on the high side cools and equalizes with the low side?
Really?
My compressors are a bit, um, "hard starting" under that much head. Maybe
you have really good "hard start" kits.
> secondly it could also be due to clogged condensor, clean
> condensor by using condensor cleaning liquid and water pressure.
With our customers, it's usually the evaporator that gets its fins linted
up... but I guess it could be fifteen years of dead lizards in there, so
yeah... just put it on full-strength from the jug, and let it soak for at
least an hour; put on plenty -- maybe even two or three applications. Then
use a hard stream of water... pressure washer is even better. Gets it
_really_ clean!
("So clean, glass seems to DISAPPEAR!")<G>
> Hope this helps
> Joss Rock
>
It confused me. I'm probably easily confused.
LLoyd
The rub it lightly with sandpaper, and throw some mild acid (
muriatic is good ) on it.
Paul- I tried that and the good news is that the warts are gone!
The bad news is that my penis is gone as well.
I think you misinterpreted my use of the word 'it'.
On a brighter note, you are now a Federally protected
minority.
Not on this NG. I see many people post here who have no
balls OR dick.
http://wrt-brooke.syr.edu/net/dianna/archives/Toothless%20Ricky.jpg
--
Christopher A. Young
You can't shout down a troll.
You have to starve them.
.
"B-Hate-Me" <B-Hate-Me@home> wrote in message
news:8sGdnVQEYKVeKdDb...@comcast.com...
:
: <.p.jm@see_my_sig_for_address.com> wrote in message
:
:
Bob
"Stormin Mormon" <cayoung61**spamblock##@hotmail.com> wrote in message
news:464e11f3$0$9923$4c36...@roadrunner.com...
> I had no problems with PJM's technique. Here is what I looked
> like after inhaling the fumes.
And here's one more hack! :-(
Just got my gauges back... A few ounces (OK more than a few) of R22
and I'm up an running! Man, it's cold up here. And to think, some
fools spent a whole weekend taking a class to get "licensed, insured,
professionally trained."
As I explained on the private e-mail you cluttered my in-box with;
OK, so if it was done right, what was your SST and your superheat?? If you
don't know what it is, then it wasn't done correctly.
If it was so easy, everybody would be doing it, don't you think??
You can screw with your R-22 system all you want, and waste all the R-22 you
want, but in just 2 1/2 years, the price is going to be a whole lot higher
to gas that system up.