I first thought the quality of A/C should all be the same. They should
either all be noisy or all be quiet. I decided to check around my
neighbor's A/C's. Indeed my contractor was correct. I found eight
Carrier 38CKC models in my neighbor, half of them are noisy and half of
them aren't.
Before I made the purchase, my contractor sold me the unit on the
compressor is "the quietest in the industry" per Carrier's published
data. Carrier claimed each Carrier unit's noise level is equivalent to 4
Lennex or 8 York's. I found this extremely deceiving. My 3.5 ton unit
may be so but definitely not the 2 ton unit.
Can any one on the net who is expert in Copeland Scroll compressor
comment on my situation? What makes the scroll compressor noisy? Scroll
compressor is known to be quieter than all other type, why some scroll
compressors are extremely noisy but some of them are very quiet? Would
adding compressor oil quiet down the unit? Should I insist on getting
the compressor replaced? Can you determine the new replacement
compressor is noisy or not before you install the compress into the
unit?
Thanks,
The dBA published by Carrier is a measurement for fan noise, not compressor
noise. Compressor noise is higher frequency which penetrate wall, window even if
it is less than 69 dBA is extremely annoying. The 1-800-CARRIER is completely
useless. The service manager was the most obnoxious person I've ever met. His
name is Ray Falk. He seems to be the only field person cover the entire western
region. His attitute is as if I owed Carrier money. His visit to my house is out
of his kindness. The compressor noise problem is normal and within their
spec.(even though the Carrier sales brochure said its Scroll compressor
virtually make no noise.)
The subcontractor has no authority to do any warranty repair without Carrier's
approval first. Carrier and the distributor Edward B. Ward refused to take back
the unit. My contractor can't replace compressor. But he won't get paid unless
he fixes the problem. So he is stuck.
The only thing I can say is the HVAC industry is SICK!!! The subcontractor is
totally at the mercy of large AC manufacturer.
--------------------------
Ricky Archuletta wrote:
> Compressor noise can be a result of many problems. Most of which are
> caused by the installer. Did he perform a vacuum to 400 microns?
> Ans: YES
> Is the expansion device and coil sized right for the condensor?
Ans: YES
> Is there an obstruction in the lines (I once found a pea sized piece of
> solder in a
> line installed by a contractor who told the customer some units just run
> longer than others.)
Ans: The unit is a Puron model. The installer did replace the piston. The
only possible mistake could be he install the piston reversed. But if so why
the unit still cools ok?
> Is the condensor on solid ground? Having
> vibration isolators can help if sized correctly if oversized they can
> cause more noise than they prevent.
Ans: My house has two stories. Each level has its own furnace. Both AC are
installed side-by-side on concret floor. The Carrier A/C compressor is
installed on a vibration isolators. This however does not help any on the
compressor pinning noise.
> If your contractor will not take the
> time to see what he did wrong you should contact Carrier. Chances are if
> its noisier its working harder and will not last as long.
Ans: My contractor actually is quite willing to try all of those simple
things. He did check to RLA which is actually lower than the rated spec
which seems to suggest the compressor wasn't overloaded. The only thing he
can not do is replace the compressor without Carrier's approval first. We
have contacted the distributor and Carrier. So far they refused to do
anything on the ground that the noise level is within its spec.
this is turtle.
call 1-800-carrier and discuss the matter with them. see what they
think
and see where it goes. your problem will get attention if you call.
TURTLE
--
Posted via Talkway - http://www.talkway.com
Exchange ideas on practically anything (tm).
> Compressor noise can be a result of many problems. Most of which are
> caused by the installer.
And if you have allergies, high blood pressure, high cholesterol or
cancer it was probably caused by the installer too.
Sent via Deja.com http://www.deja.com/
Share what you know. Learn what you don't.
Would a sound blanket have an adverse effect on the scroll
compressor? I know Carrier has used them on some units in the past. If
the sound is telegraphed through the refrigerant lines it probably wouldn't
help. What has been your experience? dz
<sf...@my-deja.com> wrote in message news:7mbuvg$e8m$1...@nnrp1.deja.com...
One thing I've noticed is that the harder a compressor has to work the
louder it gets. That could explain why your upstairs unit is louder.
Especially if you have one of these newer style homes that have a lot of
open space to the upstairs and allow all that heat an easy path to up
there.
Checking amp draw against the RLA is a waste of time most of the time. Very
rarely will you see a compressor drawing RLA [Rated Load Amperage]. To check
to see if the compressor is "overloaded", you must check performance against
the performance curvew that are published by Copeland in graphical format.
>We
>have contacted the distributor and Carrier. So far they refused to do
>anything on the ground that the noise level is within its spec.
Would they like to live in a house with a noise problem like that? My brother
had a problem with a Lennox heat pump many years ago. They changed the
compressor but the problem was still there. It's been so long ago that I can't
remember for sure, but it seems like the problem had to do with the way the
suction line was run. It took a lot of trial and error to quiet it down some,
but this was in the earlier days of scroll compressors.
My own A/C has the sound blanket. It is still relatively loud. Carrier
used to use them but they stopped some time in the past 2 years. BTW my
A/C is 2 years old.
Scot
>>ns: My contractor actually is quite willing to try all of those simple
>>things. He did check to RLA which is actually lower than the rated spec
>>which seems to suggest the compressor wasn't overloaded.
>
>Checking amp draw against the RLA is a waste of time most of the time.
Very
>rarely will you see a compressor drawing RLA [Rated Load Amperage]. To
check
>to see if the compressor is "overloaded", you must check performance
against
>the performance curvew that are published by Copeland in graphical format.
>
And to check performance, RLA is one of the pieces of data required.
Mike
UA local 370
Reply to, <ft...@accessflint.com>
Thanx
--
Steve @ NOON-AIR
Heating and Air Conditioning Service
Purvis MS
jsn...@netdoor.com
Noon...@hotmail.com
There are three kinds of men.
The one that learns by reading.
The few who learn by observation.
The rest of them have to pee on the electric fence for themselves
North Atl1 <nort...@aol.com> wrote in message
news:19990712150702...@ng-fv1.aol.com...
All the Puron units have them, as do the higher eff. units with scrolls.
At least up till today they did! Don't know about tomorrow...
You don't need RLA to check performance using the performance curves, but you
do need the actual system pressures, actual measured voltage and actual
measured amp draw.
RLA is used to calculate the Minimum Circuit Ampacity of an A/C unit and that's
about all it is worth. By electrical code, a condensing unit's Minimum Circuit
Ampacity = [ 1.25 x compressor's RLA ] + amp draw of the fan motor(s) and
crankcase heater if present
Respectfully submitted, Ron