The diagnostic LED flashes 4 times when the fan comes on and the chart
says "thermal protection device open." The unit is cold with no
evidence of gas reaching the burners and no gas smell.
I see two modules, each with two yellow wires, located on both sides
of the gas ports. Are those heat sensors? Below are some pictures of
the unit that might help. Thanks for any advice if this is
user-fixable.
http://expresswave.tripod.com/misc/Trane_XE_80_parts.jpg
http://expresswave.tripod.com/misc/Trane_XE_80_codes.jpg
AJ
"AJ" <aj00...@tripod.com> wrote in message
news:8ip71u8cvom26uboh...@4ax.com...
"AJ" <aj00...@tripod.com> wrote in message
news:8ip71u8cvom26uboh...@4ax.com...
> I have a Trane XE 80 (1997 model) which stopped burning gas recently.
> Unless I turn it off at the wall control, the fan runs continuously,
> trying to circulate non-existent heat.
No..its doing as the control is programmed to do in the event of an overheat
condition..
It knows there is either, no heat there, or too much for the thermal limits.
>
> The diagnostic LED flashes 4 times when the fan comes on and the chart
> says "thermal protection device open." The unit is cold with no
> evidence of gas reaching the burners and no gas smell.
Again..there will not be with a roll out switch tripped.
>
> I see two modules, each with two yellow wires, located on both sides
> of the gas ports. Are those heat sensors? Below are some pictures of
> the unit that might help. Thanks for any advice if this is
> user-fixable.
Might be...check your air filter...dirty? Replace it.
If not, call the installing company to have them check it so you can get
your heat back. The sensors are tripped for a reason, and no..its not owner
repairable. While you might be able to get it to run, you have not found and
repaired the condition that caused it.
"AJ" <aj00...@tripod.com> wrote in message
news:8ip71u8cvom26uboh...@4ax.com...
>Check and make sure your filter is not plugged.
Thanks, I think you nailed it. Lazy cleaning in recent months let
impacted dust reach critical mass.
Now the question is, how do I reset the thermal protector? It doesn't
seem to be kicking back on automatically.
AJ
>Might be...check your air filter...dirty? Replace it.
>If not, call the installing company to have them check it so you can get
>your heat back. The sensors are tripped for a reason, and no..its not owner
>repairable. While you might be able to get it to run, you have not found and
>repaired the condition that caused it.
Yes, my air filter was totally clogged because of lazy cleaning
recently. I hope no permanent damage was done.
"Todd Legere" <toddl...@sympatico.ca> wrote in message
news:9BSQ7.2018$Us5.4...@news20.bellglobal.com...
"Scott Eslick" <scott...@hotmail.com> wrote in message
news:y5TQ7.105570$Ze5.50...@news1.rdc1.md.home.com...
And remember to change your filter every 30 days, everytime you make a
mortgage payment change the filter, the fresh hole in your wallet should
help to remind you for a while but if you tie it to some monthly event it
will remind you long after you've gotten over the sting.