this furnace has been erratic the last couple of weeks, the digital
thermostat is programmed at its factory setting, sometimes the heat
comes on and sometimes not, but the blower always works, when the heat
is set manually like at 72 it stops at 68, then i have to reset it
again to turn on the heat
the thermostat was installed only 6 months ago so i don't think it is
bad
i phoned the technician and he said i might have a bad switch and
quoted around $150 for the job
before having him do it, i thought i would get some advice
is this a job that is easy to do?
are there any other cause for the problem?
loose connections? venting?
any suggestion is greatly appreciated
> >any suggestion is greatly appreciated
Sounds like a dirty flame sense rod. Located above the burners to the
left. Wipe off with steel wool (no soap). These boards will retry
later so if it later comes on, proves the diagnosis.
--