Thomas Miller

unread,
Oct 9, 2004, 10:46:02 PM10/9/04
to
I am having problems with my Bryant 383KAV gas furnace

The owners manual can be found here:
http://www.gogeisel.com/geiselonline/support/Bryant/373LAV_376CAV_383KAV_395CAV_Gas_OM.pdf

My problem is that it won't heat or cool and the blower keeps running
non stop, even when the thermostat is set to OFF.

I think the problem is a result of switching the programmable
thermostat from HEAT to COOL or COOL to HEAT too quickly. I guess I
should have set it to off.

The Bryant 383KAV has a status LED code. The LED code is currently
reading:

"code 33" - "LIMIT OR FLAME ROLLOUT SWITCH IS OPEN
If limit switch is open longer than 3 minutes code changes to code NO.
13
Check for:
a)Blower motor failure
b)motor start capacitor
c)open flame rollout switch, manual reset
d)inadequate combustion air supply (flame rollout switch only)
e)dirty air filter
f)defective limit switch or connections
g)loose blower wheel"


The units blower has been running for about 5 hours non-stop and the
LED status is still "33". It has not changed to code 13 yet. Here is
what the manual says for code 13. "LIMIT OR FLAME ROLLOUT SWITCH
LOCKOUT- LIMIT SWITCH WAS OPEN LONGER THAN 3 MINUTES. AUTO-RESET WILL
OCCUR AFTER 3 HOURS. FLAME ROLLOUT SWITCH REQUIRES MANUAL RESET. SEE
#33."

I have already done the manual reset limit switch procedure and
restarted the furnace and the problem still exists. The fan blower is
running constantly and the error code is still "33"

What is the next step I should take? How do I test to see if it is a
bad capacitor or a bad switch or a bad board?

Oscar_Lives

unread,
Oct 9, 2004, 10:56:55 PM10/9/04
to

"Thomas Miller" <thomasami...@yahoo.com> wrote in message
news:5ead8b72.0410...@posting.google.com...

CALL A SERVICE TECHNICIAN.


Joel

unread,
Oct 9, 2004, 11:02:48 PM10/9/04
to

"Thomas Miller" wrote

> What is the next step I should take?


Try this:
http://tinyurl.com/4l5jh

p...@see_my_sig_for_address.com

unread,
Oct 9, 2004, 11:18:17 PM10/9/04
to
On 9 Oct 2004 19:46:02 -0700, thomasami...@yahoo.com (Thomas
Miller) wrote:

>I am having problems with my Bryant 383KAV gas furnace

Take it to alt.home.repair

Paul ( pjm @ pobox . com ) - remove spaces to email me
'Some days, it's just not worth chewing through the restraints.'

HVAC/R program for Palm PDA's
Free demo now available online http://pmilligan.net/palm/
Free Temperature / Pressure charts for 38 Ref's http://pmilligan.net/pmtherm/

Noon-Air

unread,
Oct 10, 2004, 7:54:28 AM10/10/04
to

> What is the next step I should take? How do I test to see if it is a
> bad capacitor or a bad switch or a bad board?

Call your local *competent*, licensed, insured, professionally trained, HVAC
technician to correctly diagnose and repair the problem.


Terry

unread,
Oct 10, 2004, 10:11:22 AM10/10/04
to
<p...@pobox.com> wrote...

> Take it to alt.home.repair
>

Take it to alt.control.freaks


Bubba

unread,
Oct 10, 2004, 11:57:43 AM10/10/04
to
On 9 Oct 2004 19:46:02 -0700, thomasami...@yahoo.com (Thomas
Miller) wrote:


Replace them all. Then maybe you will find your
problem................or not.
Bubba

Thomas Miller

unread,
Oct 10, 2004, 2:17:05 PM10/10/04
to
I fixed it by removing the limit switch, cleaning it, tapping on the
switch, screwing it back in and turning the circuit back on. Working
great now.

Steve@carolinabreezehvac

unread,
Oct 10, 2004, 2:23:45 PM10/10/04
to

"Thomas Miller" <thomasami...@yahoo.com> wrote in message
news:5ead8b72.0410...@posting.google.com...
> I fixed it by removing the limit switch, cleaning it, tapping on the
> switch, screwing it back in and turning the circuit back on. Working
> great now.


Big hint here fella...couple actually....

one, no legitimate tech would CLEAN a limit switch without finding out why
it got dirty....(lack of normal service by chance?)
and two..
Tapping on a stuck one does not fix it...why was it tripped to start with?

Now, (not to scare you...but fact) you MIGHT have a bad switch that is
telling you something, and you have failed to correct the problem, and wont
know about it till the furnace fails in a manner that might cost you life,
or home..

Spend the $70 or so to get it checked properly. or dont.....but this is why
we dont give advice here. Halfassed "repairs" by non qualified persons. Did
you check the CO output? Heat rise? Check for an exchanger issue?

if not..you didnt do anything.

@starband.net ~KJPRO~

unread,
Oct 10, 2004, 3:08:51 PM10/10/04
to
"Steve@carolinabreezehvac" <st...@removethis.carolinabreezehvac.com> wrote
in message news:G8fad.506$C4.1...@eagle.america.net...

I smell.....
....improperly installed unit!!

~kjpro~

Bubba

unread,
Oct 10, 2004, 4:28:03 PM10/10/04
to
On 10 Oct 2004 11:17:05 -0700, thomasami...@yahoo.com (Thomas
Miller) wrote:

Oh Christ! Another clueless homeowner that wants to chant,
"Nah-Nah-Nuh-Nah-Nahh" in our face and thinks he has fixed it but
doesnt have a clue about "Why did it happen?" and "What might be the
life removing consequences he has just hidden?"
Sleep well, idiot.
Bubba

Noon-Air

unread,
Oct 10, 2004, 6:05:02 PM10/10/04
to
You didn't "fix" anything... and all you did was to mask a symptom. What was
the cause of the problem?? What else was effected?? What other damage is
there??
I hope you have 911 on speed dial, but don't worry about your insurance, you
have just voided it along with any warranty that might be left on the
furnace. But you "fixed" your furnace didn't you.
If your real lucky, your furnace won't crap out on you and have to pay for
an emergency service call on a sunday or holiday afternoon when its 10
degrees out.