This problem started last year, and the furnace is now six years old.
So far the repairman, in two trips, has replaced the "flapper," checked the
gas pressure and cleaned the filter. He has also checked the thermostat
anticipation setting, which is .6.
I have tried setting the thermostat way up, thinking that when it first
comes on, it might somehow vibrate off when the furnace comes on. No luck
with that either.
The exterior exhaust and air intake are not in any way blocked, and there is
nothing around these pipe which would cause the exhaust fumes to be drawn
back into the intake.
There is one other symptom which may or may not be associated with the
problem. The pulsing of the furnace is uneven whereas, as I recall, it
sounded with a steady hum when the furnace was first installed.
I would appreciate any ideas on this one before I call the repairman again.
Laird
Unfortunately your furnace is a pig to work on. Non Lennox dealers
don't have the knowledge to trouble shoot them. Do yourself a long
term favor and junk it. Parts are unique and expensive for this
furnace plus it's far and few between to where you will find that
certain tech that can troubleshoot and repair this furnace the first
time out.
Output.
I'm sure you will get all kinds of things that "may" be wrong from
this group but chances are none of them will be right. Its pretty
hard to fix something from here. I've seen posts where everything
under the sun is wrong and it turns out to be that the stat was off
LOL. Usually HO posts wanting a diagnosis over the net seldom gets
any *real* help but they are good for starting pissing contests. Now
if you want more input ask which furnace is better. Good luck.
Electricity.
Mike
UA local 370
Mike
UA local 370
On Fri, 3 Dec 1999 15:30:04 -0500, "Laird Allshouse" <lai...@penn.com>
wrote:
Mike
UA Local 370
reply to <ft...@usol.com>
Laird Allshouse <lai...@penn.com> wrote in message
news:mFV14.2192$8H.1...@newsfeed.slurp.net...
Brian S- wrote:
> Hi Laird,
>
> The problem you are describing is usually gas or combustion air
> related...Stoped up flue, exhaust and intake swaped, air flapper
> sticking, etc. You pretty much hit on all thoes. It's been a long
> time since I was the Pulse troubleshooter. I can remember times
> standing in front of a Pulse with problems like what you're
> describing, but I can't remember exactly what the problems were!
>
> The dealer needs to call Lennox and talk to one of their techs. They
> will be able to tell him exactly what to look at. The air flow switch
> was certainly a good start, since it probably had never been changed.
>
> And no, don't go ripping that furnace out (sorry Mike). With the
> exception of the solder fiasco in pre 1988 furnaces, the Pulse is as
> neary trouble free as they come. Problem is when someone doesn't
> understand something they talk bad about it, and most don't understand
> the Pulse. (Mike, how much Pulse training have you had? How many
> Pulse furnaces have you worked on?)
>
> And Laird, would you do us all a favor? When you get it fixed, let us
> know the problem.
>
> Brian
>
> "Laird Allshouse" <lai...@penn.com> wrote:
>
> >I have a Lennox Pulse 21 furnace (model G21Q4/5-100-3) which has an
> >intermittant problem. Frequently, when it starts up, it will only run for a
> >few moments, then shut down for about 30 seconds, then attempt to start
> >again. It may cycle this way for up to three times. At some times the
> >furnace will just "burp" and immediately shut down. In every case the
> >furnace finally does come on for good and run until the thermostat shuts it
> >down.
> >
> >This problem started last year, and the furnace is now six years old.
> >
> >So far the repairman, in two trips, has replaced the "flapper," checked the
> >gas pressure and cleaned the filter. He has also checked the thermostat
> >anticipation setting, which is .6.
> >
> >I have tried setting the thermostat way up, thinking that when it first
> >comes on, it might somehow vibrate off when the furnace comes on. No luck
> >with that either.
> >
> >The exterior exhaust and air intake are not in any way blocked, and there is
> >nothing around these pipe which would cause the exhaust fumes to be drawn
> >back into the intake.
> >
> >There is one other symptom which may or may not be associated with the
> >problem. The pulsing of the furnace is uneven whereas, as I recall, it
> >sounded with a steady hum when the furnace was first installed.
> >
> >I would appreciate any ideas on this one before I call the repairman again.
> >
> >Laird
> >
> >
--
MDamron,AllTemp Heating & Cooling
Visit our questions and answers bulletin board ...
( HVAC Q & A ) http://www.alltemphvac.net/board
Respectfully, Bob
Again, enjoyed your post !
Brian S- wrote:
> airf...@webtv.net wrote:
> >Exactly what is an air flapper?
>
> The Pulse furnace works by injecting a small amout of gas and air into
> a chamber, then lighting it with a spark. The flappers allow the air
> and gas into the chamber, but does not allow either back out. The air
> flapper is about 3" diameter, the gas flapper is about 1" in diameter.
>
> On a call for heat the inducer runs to purge all old gas products out
> of the system (the inducer pushes air rather than pulling the fumes
> out). Then the spark plug sparks, the gas valve opens, and air is
> pushed into the "chamber". This creates an explosion. (The marketing
> people thought "pulse" sounded better, thus the name.) The "pulse"
> pressurizes the chamber closing the flappers for the gas and air. The
> explosion is pushed up a pipe. As it goes into the pipe the chamber
> is now under negative pressure, so gas and air are sucked back in.
> The spark plug runs only a few seconds to start this process going.
> After that the last explosion itself ignites the next gas and air
> mixture that is being sucked in. The inducer also shuts off and is
> not turned on again untill the end of the heat cycle when used as a
> post purge.
>
> So, while operating the Pulse uses no inducer, no spark plug, and the
> air flow switches are normally closed. As long as air and gas are
> available, the combustion process will go on forever. The Germans
> invented this during WW2 (the old "buzz bombs").
>
> Hope this helps.
>
> Brian
The replaced control board got it running again until we can have it
completely tune-up and serviced. Lennox had updated the flue pipe on
this one but the furnace is a post Pulse after their exchanger problem .
: -)
> The most recent service call was on a Pulse in
>which the customer had already had two other service companies out before
>we arrived.
Hi Mell,
What did you find to be the problem on that call?
>> So, while operating the Pulse uses no inducer, no spark plug, and the
>> air flow switches are normally closed.
Something else....the fan in the heat mode is turned on by a good ole
Honeywell fan/limit. In cooling, the fan is turned on with a 24v
relay energized by the green wire. From the thermostat W terminal the
white wire goes thru 2 normally closed air flow switches, then
straight to the ignition module. The ignition module turns the
inducer fan on and off. I know this is much more than was orginally
asked, but just wanted to make the answer complete!
I wish more manufacturers would make furnaces with fan/limits and 24v
relays. Why the need for all this fancy electronics?
Brian
> The air flow switch was certainly a good start, since it probably had never been changed.
Huh? I think I meant the air flapper. My mistake.
Brian
Respectfully, Bob
If I said board I'm referring to the Lennox Blk Ignition Module. Unless
you've hand some hands on you're going to be working on it blind. I did
the 1st one I ever saw... I've got a pretty good understanding with my
Lennox distributors counter guy... Good old Charlie loves to explain
things and if you've got an ear he'll teach you everything you need to
know!
--
MDamron,AllTemp Heating & Cooling
Wishing All Our Friends In Alt.Hvac A Happy And Joyful Holiday Season!
http:/www.alltemphvac.net/Greetings.html
: Unfortunately your furnace is a pig to work on. Non Lennox dealers
: don't have the knowledge to trouble shoot them. Do yourself a long
: term favor and junk it. Parts are unique and expensive for this
Excuse me? You are telling someone to JUNK a six-year-old furnace? Easy
for YOU to say.
: furnace plus it's far and few between to where you will find that
: certain tech that can troubleshoot and repair this furnace the first
: time out.
: Output.
: I'm sure you will get all kinds of things that "may" be wrong from
: this group but chances are none of them will be right. Its pretty
: hard to fix something from here. I've seen posts where everything
: under the sun is wrong and it turns out to be that the stat was off
: LOL. Usually HO posts wanting a diagnosis over the net seldom gets
: any *real* help but they are good for starting pissing contests. Now
: if you want more input ask which furnace is better. Good luck.
: Electricity.
: Mike
: UA local 370
: Mike
: UA local 370
: On Fri, 3 Dec 1999 15:30:04 -0500, "Laird Allshouse" <lai...@penn.com>
: wrote:
: >I have a Lennox Pulse 21 furnace (model G21Q4/5-100-3) which has an
: >intermittant problem. Frequently, when it starts up, it will only run for a
: >few moments, then shut down for about 30 seconds, then attempt to start
: >again. It may cycle this way for up to three times. At some times the
: >furnace will just "burp" and immediately shut down. In every case the
: >furnace finally does come on for good and run until the thermostat shuts it
: >down.
: >
: >This problem started last year, and the furnace is now six years old.
: >
: >So far the repairman, in two trips, has replaced the "flapper," checked the
: >gas pressure and cleaned the filter. He has also checked the thermostat
: >anticipation setting, which is .6.
: >
: >I have tried setting the thermostat way up, thinking that when it first
: >comes on, it might somehow vibrate off when the furnace comes on. No luck
: >with that either.
: >
: >The exterior exhaust and air intake are not in any way blocked, and there is
: >nothing around these pipe which would cause the exhaust fumes to be drawn
: >back into the intake.
: >
: >There is one other symptom which may or may not be associated with the
: >problem. The pulsing of the furnace is uneven whereas, as I recall, it
: >sounded with a steady hum when the furnace was first installed.
: >
: >I would appreciate any ideas on this one before I call the repairman again.
: >
: >Laird
: >
: Mike
: UA Local 370
: reply to <ft...@usol.com>
--
Commenting about the Lennox Pulse, G21...
> Parts are unique and expensive for this
>furnace (the Pulse)
Hi Mike,
My first chance to call Lennox and provide some fact to your
statement: I have checked previously about what non-Lennox dealers
pay for Lennox parts, and it is only slightly more than dealers. I
have only the prices for dealers...
- The ignition module (same one used on all Pulse furnaces), includes
conversion kit, cost less than $95. (there of 26 of them at my
distributer)
- The inducer assembly (same one used on all Pulse furnaces) is less
than $20 (even I find that hard to believe, but that's what they tell
me, includes motor, blower wheel, housing, etc.) (12 of these at my
distributer)
- The sensor (again, same one used on all Pulse furnaces) is less than
$15.
I don't have to tell you what a 24v relay and fan/limit cost. From
what I see, the prices are quite reasonable. Actually, looks to me
like the Pulse parts may be about THE LEAST EXPENSIVE OF ANY OTHER 90%
FURNACE??? As I have stated, the Pulse may be intimidating at first,
but is a very simple and reliable design. Don't confuse it with the
Triathlons and Amana Glycol furnaces of the past. The original
poster's Pulse was built after 1988 (after the solder episode).
I don't like to get into pricing, but at least it provides some
substance to counter unsubstantiated claims.
Brian
How do you like your Robertshaw Electronic Ignition Tester?
Mike
UA local 370
On Mon, 06 Dec 1999 13:44:43 GMT, Br...@SpencerAir.com (Brian S-)
wrote:
>
>Hi Mike,
>
>My first chance to call Lennox and provide some fact to your
>statement: I have checked previously about what non-Lennox dealers
>pay for Lennox parts, and it is only slightly more than dealers. I
>have only the prices for dealers...
>
snip
Hey Brian, I checked with our local Lennox dealer today and I'll be
damned :) 18.36 for the inducer. I stand corrected.
>Hey Brian, I checked with our local Lennox dealer today and I'll be
>damned :) 18.36 for the inducer. I stand corrected.
Hi Mike,
I, too, was doubting if that was correct. Wonder what it's made of??
I have never had the need to replace one.
Brian
>ftwhd wrote:
I don't know, Its been a long time since I've seen the innards of a
Pulse I don't remember what the inducer looks like. It sure cant be
much though. Not for that price anyway.
Once again, and on a continuing basis, the furnace only runs briefly for a
couple of times until it finally settles into a full cycle.
I don't know if this helps with the diagnosis, but thought I would post it
for your information.
In the meantime, I have provided my repairman with copies of all of the
messages posted here, and I want to thank you for your suggestions.
If we get this thing solved I will advise what the fix was.
Regards,
Laird
"Brian S-" <spen...@mindspring.com> wrote in message
news:3849e15...@news.mindspring.com...
> airf...@webtv.net wrote:
> >Exactly what is an air flapper?
>
> The Pulse furnace works by injecting a small amout of gas and air into
> a chamber, then lighting it with a spark. The flappers allow the air
> and gas into the chamber, but does not allow either back out. The air
> flapper is about 3" diameter, the gas flapper is about 1" in diameter.
>
> On a call for heat the inducer runs to purge all old gas products out
> of the system (the inducer pushes air rather than pulling the fumes
> out). Then the spark plug sparks, the gas valve opens, and air is
> pushed into the "chamber". This creates an explosion. (The marketing
> people thought "pulse" sounded better, thus the name.) The "pulse"
> pressurizes the chamber closing the flappers for the gas and air. The
> explosion is pushed up a pipe. As it goes into the pipe the chamber
> is now under negative pressure, so gas and air are sucked back in.
> The spark plug runs only a few seconds to start this process going.
> After that the last explosion itself ignites the next gas and air
> mixture that is being sucked in. The inducer also shuts off and is
> not turned on again untill the end of the heat cycle when used as a
> post purge.
>
> So, while operating the Pulse uses no inducer, no spark plug, and the
>Prior to the furnace's attempt to start
>I heard what I would guess is a purging fan start up. It actually started
>for a few seconds, stopped for about 30 seconds, started again and repeated
>this cycle three times when, while it was running, the furnace started.
Hi Laird,
That's great info to have. Hopefully it will be acting up when the
svc man is there. Could be the inducer motor is getting voltage but
overheating and quiting. Could be one of the air flow switches is
opening, breaking voltage to the ignition (which in turn energizes the
inducer). Could be the ignition module itself is cutting the inducer
motor off.
Bob mentioned earilier about a possible inducer fan problem, but the
unit finally starts. He may have been right on?
Brian
Laird Allshouse wrote:
> I'm the original poster of this problem. This morning I went down and spent
> some time listening to the furnace. Prior to the furnace's attempt to start
> I heard what I would guess is a purging fan start up. It actually started
> for a few seconds, stopped for about 30 seconds, started again and repeated
> this cycle three times when, while it was running, the furnace started.
>
--
MDamron,AllTemp Heating & Cooling
Wishing All Our Friends In Alt.Hvac A Happy And Joyful Holiday Season!
http://www.alltemphvac.net/Greetings.html
"AllTemp" <All...@Pacbell.net> wrote in message
news:384EF49B...@Pacbell.net...
* Sent from RemarQ http://www.remarq.com The Internet's Discussion Network *
The fastest and easiest way to search and participate in Usenet - Free!
Respectfully, Bob
Respectfully, Bob
>"Laird Allshouse" <lai...@penn.com> wrote:
>
>>Prior to the furnace's attempt to start
>>I heard what I would guess is a purging fan start up. It actually started
>>for a few seconds, stopped for about 30 seconds, started again and repeated
>>this cycle three times when, while it was running, the furnace started.
>
>Hi Laird,
>
>That's great info to have. Hopefully it will be acting up when the
>svc man is there. Could be the inducer motor is getting voltage but
>overheating and quiting. Could be one of the air flow switches is
>opening, breaking voltage to the ignition (which in turn energizes the
>inducer). Could be the ignition module itself is cutting the inducer
>motor off.
>
>Bob mentioned earilier about a possible inducer fan problem, but the
>unit finally starts. He may have been right on?
>
>Brian
Sure sounds like an inexpensive repair to me :). The *purge blower*
(instead of inducer) motor needs replaced. Verified by whether or not
there is voltage to the motor when it quits during the initial startup
phase. If its quits working and has voltage, replace the purge motor.
If no voltage is present then, the motor is probably fine.
> We are captives of small-town and very rural servicing companies. I talked
> to the repairman about how long he had been working for the company. He
> said six years. He said most guys work for a few years and then go off on
> their own. The result is that few really get in-depth experience and tech
> know-how on these things.
>
> I do not have an annual service agreement so, after 6 years, I now have
> about $450 in the maintenance of the furnace, including the cost of the
> module. That figures out to about $75 a year, same as the annual service
> cost.
>
> Next time this happens I'll get one of the $90 module from you guys and fix
> it myself.
>
> "AllTemp" <All...@Pacbell.net> wrote in message
> news:3851A9F1...@Pacbell.net...
> > The control module was replaced this morning, gee. Listen didn't they
> test the
> > module the 1st trip there ? Oh ya almost forgot ! A service tech doesn't
> need
> > all those expensive high tech gadgets. Isn't that what someone one
> replied to
> > my post ?
> >
> > A simple procedure of checking the module in the appliance could have been
> done
> > using any number of electronice module testers on the market. I use the
> > Robershaw- Un-Line #900-575, I believe the Lennox part number for the
> wiring
> > harness for the etest procedure is 33J6201 . Had this been done to rule
> out
> > the control module all this delay could have been avoided. I earlier said
> I
> > would have lost confidence in this service company long ago ! Did they
> discount
> > your repair ? After all it looks like it was structly a training course
> held at
> > your inconvenience on your Pulse, lol !
> >
> > But I'm glad to hear you have it repaired.
> >
> > Laird Allshouse wrote:
> >
> > > The control module was replaced this morning, apparently fixing the
> problem.
> > > I say apparently because the problem was intermittant. I'll monitor it
> for
> > > a
> > > couple of days before I'll be satisfied that it is actually fixed.
> > >
> > > BTW, I had complained about the furnace running "rough." It now seems
> to
> > > run
> > > smoother.
> > >
> > > Thanks to all who made recommendations.
> > >
> > > Laird
> > >
> > > "Laird Allshouse" <lai...@penn.com> wrote in message
> > > news:QBz34.91$Ww1....@newsfeed.slurp.net...
> > > > I'm the original poster of this problem. This morning I went down and
> > > spent
> > > > some time listening to the furnace. Prior to the furnace's attempt to
> > > start
> > > > I heard what I would guess is a purging fan start up. It actually
> started
> > > > for a few seconds, stopped for about 30 seconds, started again and
> > > repeated
> > > > this cycle three times when, while it was running, the furnace
> started.
> > > >
A simple procedure of checking the module in the appliance could have been done
using any number of electronice module testers on the market. I use the
Robershaw- Un-Line #900-575, I believe the Lennox part number for the wiring
harness for the etest procedure is 33J6201 . Had this been done to rule out
the control module all this delay could have been avoided. I earlier said I
would have lost confidence in this service company long ago ! Did they discount
your repair ? After all it looks like it was structly a training course held at
your inconvenience on your Pulse, lol !
But I'm glad to hear you have it repaired.
Laird Allshouse wrote:
--
<ftwhd> wrote in message news:i3435s43drqv7vkal...@4ax.com...
> I'm glad you got it fixed. I'm curious how much was the bill?
> Mike
> UA local 370
> <reply to ft...@usol.com>
I do not have an annual service agreement so, after 6 years, I now have
about $450 in the maintenance of the furnace, including the cost of the
module. That figures out to about $75 a year, same as the annual service
cost.
Next time this happens I'll get one of the $90 module from you guys and fix
it myself.
"AllTemp" <All...@Pacbell.net> wrote in message
news:3851A9F1...@Pacbell.net...
> The control module was replaced this morning, gee. Listen didn't they
test the
> module the 1st trip there ? Oh ya almost forgot ! A service tech doesn't
need
> all those expensive high tech gadgets. Isn't that what someone one
replied to
> my post ?
>
> A simple procedure of checking the module in the appliance could have been
done
> using any number of electronice module testers on the market. I use the
> Robershaw- Un-Line #900-575, I believe the Lennox part number for the
wiring
> harness for the etest procedure is 33J6201 . Had this been done to rule
out
> the control module all this delay could have been avoided. I earlier said
I
> would have lost confidence in this service company long ago ! Did they
discount
> your repair ? After all it looks like it was structly a training course
held at
> your inconvenience on your Pulse, lol !
>
> But I'm glad to hear you have it repaired.
>