Condensing units are 5-ton Tranes. Checking the superheat comes out as 12°,
the suction pressure is rock steady at 50 psi and the head pressure is 240 with
an outdoor ambient of 75° . It is exactly the same for both units. I am not
familiar with this type of cooling system. The Unico website offers some
assistance but not what I need to know. And the people have lost all the
paperwork that came with the evaps. Right now the units are operating on the
freezestats until temperature setpoint is reached. I believe that the evaps
are not matched correctly with the condensing units or the evaps do not have
enough ducts to move more air.
Need some help with this one.
C. Hawk Halterman
Destiny HVAC Company
>Condensing units are 5-ton Tranes. Checking the superheat comes out as 12°,
>the suction pressure is rock steady at 50 psi and the head pressure is 240 with
>an outdoor ambient of 75° . It is exactly the same for both units. I am not
>familiar with this type of cooling system. The Unico website offers some
>assistance but not what I need to know. And the people have lost all the
>paperwork that came with the evaps. Right now the units are operating on the
>freezestats until temperature setpoint is reached. I believe that the evaps
>are not matched correctly with the condensing units or the evaps do not have
>enough ducts to move more air.
I would definitely want to check the equipment sizing as you
suggest. With head that high on a low-ambient day ( assuming this is
22 ? ), and suction that low on *any* day, even though SH isn't
bad.... something real funky ! Is this TXV ? That would explain the
SH staying under control.....
>Need some help with this one.
>
>C. Hawk Halterman
>Destiny HVAC Company
Destiny, Destiny, can't avoid my Destiny !
Destiny, Destiny, can't avoid my Destiny !
{ shades of Young Frankenstein :-) }
Did anyone else find that one scene to be the irritation
equivalent of the alarm clocks on Dark Side ?
Paul ( pjm @ pobox . com ) - remove spaces to email me
>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~>~~
Please look at http://helpthecritters.com/ , my new domain for helping critters !!!
My personal WWW site is at http://www.pmilligan.net ,
featuring free HVAC, stock market, and other free software
Never color inside the lines in the coloring book.
Color instead where it pleases you to.
You can only color a page once, but there are always more pages.
On 02 Aug 2002 22:32:39 GMT, hawkm...@aol.comnojunk (Hawkmeistr)
wrote:
>Last October some friends of a friend had two Unico systems put in their 80
Yes they both are.
Apparently four different technicians have just shaken their heads and went
away saying they had to look into it further.
>You are obviously one very motivated individual. ( or very stupid :-)
Retired military...never run from a fight or a challenge.
I have seen these systems before but not to work on any of them. I thought I
would try this one as it is quite a dome scratcher. The local rep is approx.
120 miles away in another state.
>Retired military...never run from a fight or a challenge.
And may I add ( assuming you worked for the USA ! ) - retired
from the best in the world !!!!!!
>>Is this TXV ? That would explain the
>>SH staying under control.....
>
>Yes they both are.
OK, low back and high head with a TXV ( good SH )......
Your post sounds like you already know the things to look for
. I think you have a compound problem here.
hey, compound problem guys - take a shot at this one !!! :-)
My guesses :
- equipment mis-match seeing as this is a new start up
- low airflow ( can you blow some free supply air out somewhere to see
what the back does ? )
- what's the DT across the evap ?
- that high head ( R22 ?? ) bothers me a whole bunch - air in the
pipes ? Recover and evac and recharge clean ????
- let's guess the condensor is clean ( new start-up ) - is airflow
out there good ? Good free air paths in and out, no re-breathe ?
>>The owner isnt willing to have the
My guess would be not nearly enough airflow, and someone stuffed a lot
of refrigerant in it to try to compensate.
To do a proper analysis, instead of guessing, we would need the
following:
Low side:
Evap air in temp
Evap air out temp
SST (saturated suction temp)
Suction line temp near compressor
High side:
Cond air in temp
Cond air out temp
SCT (saturated condensing temp)
Liquid line temp near condenser
Gary
If your really that set on it, email me or call me and I'll get the
book out and give you some of the info
Bubba
On 02 Aug 2002 23:16:05 GMT, hawkm...@aol.comnojunk (Hawkmeistr)
wrote:
>>The owner isnt willing to have the
The product catalog is quite intensive, offering not only products, but also
design, installation, & system sizing manuals.
You may also want to consult with the Engineering Support Technician, Richard
Eason (314-481-9000)
Unico, Inc
7401 Alabama Ave
St Louis Mo 63111
>Subject: Unico High Velocity System
>From: hawkm...@aol.comnojunk (Hawkmeistr)
>Date: 8/2/2002 3:32 PM Pacific Daylight Time
>Message-id: <20020802183239...@mb-cr.aol.com>
Damn right!!
I printed the Installations Tips and the minimum amopunt of outlets per ton is
five. I didn't count all the outlets but from what I saw, there aren't 25
outlets per each unit.
Hawk
On 03 Aug 2002 17:56:04 GMT, hawkm...@aol.comnojunk (Hawkmeistr)
wrote:
Yes you did! Having read some of the information on the website it is all
coming together. I will have to count the diffusers and get the information
for the website's calculator. I did two of the rooms that I knew about and it
calculated out to two tons of cooling. With four more rooms to figure in for
the downstairs system...just not enough airflow!!
I am going to call Unico on Monday and get their spin on the problem. Thanks
to all who replied. I'm sure I can get it to work correctly.
Hawk
PS - while Gary makes a good point about someone dumping juice
in to compensate for low back, IE, look for over-charge, also keep in
mind the effect of that TXV throttling down, backing refrigerant up
into the condensor.