Any ideas? "Internal control fault" sounds like the controller board, but
why would it work except when it gets cold out? What is the best way to
troubleshoot "internal control fault" error?
Thanks,
Casey
Yeah, those two resistors do look like they have been overheated.
I cleaned the ignitor and flame sensor and where they contact the mount
yesterday (with steel wool and wire brush). I thought that might have done
the trick because the heat worked all day yesterday afterwards and this
morning (which was very rare beforehand). However, it was locked out when I
got home today. :(
<gof...@gonefishin.net> wrote in message
news:7lb5r2550a5blke3m...@4ax.com...
> look in the middle of the circuit board, see the two big square white
> resistors and the two resistors immediately above them? One looks
> like its been over heating....also the mounting holes/slots in the
> ignitor assembly.....sand paper the metal around those mounting
> locations as well as their corresponding mating surfaces where they
> mount. you need a good grounding connection there...
>
> too bad when they replaced your heat exchanger they didnt also replace
> the totall rusted out inducer housing. Inside that inducer housing is
> a totally rusted inducer blower wheel. the wheel should have been
> replaced as well, as they tend to disentegrate
>
> also, check for tightness on all stake on connectors and the edge
> connector on the ckt board. those units are notorious for
> over-firing. be sure to check and set the pressure at the gas valve.
> your service tech should have de-rated the burners if its overfiring
>
> see that round black gizmo with wires coming out of it at the back of
> the inducer motor? thats the Hall-Effect sensor, a total piece of
> shit. It tells the control board the inducer motor is running and
> its ok to open the gas valve and spark the ignitor. It is a piss-poor
> design though, as the inducer motor can be spinning a totally rusted
> out inducer wheel. So when the gas ignites, you get major flame
> roll-out, which usually burns all the wiring up. Did I mention I LOVE
> CARRIER??
>
> finally, take a shop vac to the crap in the bottom of the burner
> compartment. cleanliness is next to godliness.
>
> ps- error code 8 is carrier's way of saying.....get ready to spend
> the big bucks....
Leave it powered up and scrub the back of the circuit board with oo steel
wool to get the soldered connections clean. Sounds like you have a dirty
connection.
> Leave it powered up and scrub the back of the circuit board with oo
> steel wool to get the soldered connections clean. Sounds like you
> have a dirty connection.
LOL!!
You're cruel!
--
Respectfully, Bob
Seriously, I plan to check all the connections to make sure they are secure
and everything, that should be, is well grounded. If that doesn't fix, I
have to assume the circuit board needs to be replaced.
"Oscar_Lives" <nos...@nospam.net> wrote in message
news:3hgth.317255$FQ1.248621@attbi_s71...
I had a similar problem (as have many others) and hope this information
helps. --John
Symptom:
Intermittent furnace lockout with Internal Control Fault (8 flashes),
sometimes accompanied by the "modified fan blower delay" fault (1 flash).
Problem occurs especially when the temperature falls below 32 degrees.
Exhaust Fan continues to blow after lockout. Checked rollout switches and
flame sensors, no problem.
Cause:
Excessive vibration triggering the relays on the Integrated Control Panel,
which cause the internal control fault (usually the vibration can be felt
by touch on any part of the unit)
Temporary Fix:
Dampen the vibration to the control panel using high-temp flame-resistant
padding.
Permanent Fix:
Vibration most likely due to imbalanced exhaust blower wheel (cage wheel
inside the blower that pushes flame exhaust out of the unit). Replace
blower cage wheel.
Casey wrote:
> http://www.commercialinstallations.com/Misc/heat.htm
> Thanks,
> Casey
-------------------------------------
##-----------------------------------------------##
Delivered via http://www.thestuccocompany.com/
Building Construction and Maintenance Forum
Web and RSS access to your favorite newsgroup -
alt.hvac - 28581 messages and counting!
##-----------------------------------------------##
Is this a joke? I don't know much about heating and cooling but I'm an EE
and this
is not a good idea for any circuit board. It will short out components and
most
likely damage the board. If there is high voltage on the board it could
burn or
electrocute a person. It would also not fix any bad connections on the
back of the
board.
This has to be a joke for people who know better but some non-technically
inclined
person may actually try this. Not very funny.
-------------------------------------
>responding to
>http://www.homeownershub.com/hvac/Carrier-48SS-locks-out-with-internal-control-fault-when-co-11733-.htm
>mark356 wrote:
>??? Leave it powered up and scrub the back of the circuit board with oo
>steel
>wool to get the soldered connections clean???
>
>Is this a joke? I don't know much about heating and cooling but I'm an EE
Which explains why you didn't get the joke.
--
Click here every day to feed an animal that needs you today !!!
www.theanimalrescuesite.com/
Paul ( pjm @ pobox . com ) - remove spaces to email me
'Some days, it's just not worth chewing through the restraints.'
'With sufficient thrust, pigs fly just fine.'
HVAC/R program for Palm PDA's
Free demo online at www.pmilligan.net/palm/
Free 'People finder' program now at www.pmilligan.net/finder.htm
Whenever a Liberal utters the term "Common Sense approach"....grab your
wallet, your ass, and your guns because the somnabitch is about to do
something damned nasty to all three of them.
Pray for Obama : Psalms 109:8
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"mark356" <mfiedler356_at...@foo.com> wrote in message
news:4484e$4d0398ab$45499b77$15...@news.flashnewsgroups.com...
responding to
http://www.homeownershub.com/hvac/Carrier-48SS-locks-out-with-internal-control-fault-when-co-11733-.htm
Better to brush both sides of the circuit board with hydrofluoric acid and then shine up the solder connections with a belt sander with 80 grit.