So where IS the spark?
Jeff
--
Jeffry Wisnia
(W1BSV + Brass Rat '57 EE)
The speed of light is 1.8*10^12 furlongs per fortnight.
You will need to re-open the connection box in the fan and re-examin the
connections that you made. It's obvious that you have a short and it may be
readily seen by a blackened or melted connector. If nothing is obvious you
*will* have to call an electrician. Good luck.
Use a circuit tester to verify that the hot, neutral and ground were not
miswired for that fixture. Also check the switch that controls the fan.
You shouldn't get a spark at all if you wired it up then turned on the
breaker then flipped the switch. The breaker should have just tripped with
no excitement. If you are seeing an arc inside the fan, maybe it is
defective. Temporarily hook up a normal lamp to check power.
You may also have mixed up the lamp and motor wires.
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
<angel...@yahoo.com> wrote in message
news:8df2002e-bd21-4d18...@l17g2000pri.googlegroups.com...
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"C & E" <chizz...@yahoo.com> wrote in message
news:4824b7aa$0$11170$470e...@news.pa.net...
breaker off. disconnect the fan. breaker on. if breaker stays on, then
the new fan fan is the problem. buy a ($25) digital multimeter and
troubleshoot the fan.
see also:
http://www.faqs.org/faqs/electrical-wiring/part1/
http://www.wikihow.com/Use-a-Multimeter
Your findings are not supported by reality. He was
skilled enough to replace several ceiling fans and
smart enough to ask about the lone problem he
encountered before proceeding,
> --
> Christopher A. Young
> Learn more about Jesus
> www.lds.org
Learn more about civility