Your math is correct as far as it goes. It is VERY difficult to
maintain a uniform thickness. The main way to accomplish is to
carefully and accurately grade a granular subgrade material, here it
would be "fill sand". Unless you have this type of tolerance, be very
prepared for additional yardage. There is nothing worse than running
out and waiting for delivery of a 1/2 yard to finish. Much cheaper to
send back a 1/2. A truly uniform 4" slab is much stronger than one that
varies from 4 to 6 (think about tire ruts from the concrete truck if you
are backing into your forms). How are planning to pour?
Gravel capillary break is a best practice method under a floor slab, not
under exterior pavement. It does no harm, but will add to the expense
that is not necessary. What is important is proper compaction of the
subgrade. If is gets goey when it is wet, this sounds like clay - wet
clay expands. A typical commercial spec would require removal and
replacement with a select material (red select here) or lime
stabilization of the clay that is compacted to 90-95 Proctor density.
I am fairly sure you are fine to go ahead with what you have.
Wire mesh is NOT reinforcement. It keeps cracked concrete from getting
bigger cracks. In practice, it is very difficult to keep at the proper
location. Artificial or steel fiber is considered an equivalent. Cost
depends on dosage per cubic yard.
4" concrete does not gain appreciably by using #4 bar. If the bar is
run both directions there is not sufficient depth of concrete for
minimum concrete cover. Reinforcement is usually placed in the tension
dimension of the concrete which is at the bottom 1/3 point with 2" of
concrete cover from earth forming (bottom).
Your tar joint at the existing is good practice. It is an expansion
joint. If the concrete is not trapped, there is no need for more
expansion. Tooled or sawn joints are contraction joints. These help
the concrete break in a straight line when the shrinkage forces form.
Make sure that contraction joints are T/4 - at least 1/4 of the slab
thickness. Concrete should always have contraction joints at least
every 12' both directions.
YOu need to cure the concrete at least the first 3 days. You need to
keep vehicles off the concrete at least 7 days. Make sure you use air
entrainment for any exterior concrete. I would order 3500# with air.
Let the bleed water come out before any trowel work of any type. If you
don't know concrete, see about getting an informed buddy or assistant.
--
___________________________________
Keep the whole world singing . . .
Dan G