I have a lot of ideas. My first is that it doesn't sound like you are
measuring correctly. Sure that meter is set to DC, rather than AC? Plug in
a light and see if it is as bright as you expect. With the fraction of
power you seem to be claiming, that would be a good double-check. What
problem are you trying to solve in the first place?
- Nate
Try playing with your dimmers and see if the voltage changes. You may have
two circuits connected on the same dimmer, who knows...
My two cents....
Eric.
Montreal.
"Robert Flagg" <lee...@tdl.com> wrote in message
news:bb3adb78.03050...@posting.google.com...
What you have is/are broken or disconnected wire(s).
A good Simpson voltmeter doesn't load the circuit very much and it can get
some kind of a reading just from the electric field coupling a truly HOT
conductor with a conductor that has been disconnected.
First, check your fuse/CB box to ensure your circuits are hot at that end.
Also check to see if there are any GFCIs about that have tripped. Some
folks (quite legally and properly) use a GFCI to protect and outlet when the
ground connection is lacking (although they are supposed to label the outlet
"no ground.")
Go back to the outlet, take the cover off, and repeat your measures (be
careful because you may have a HOT wire in the box) where the wired connect
to the screws. If you outlet is the cheap "poke in" type and the poke in
wiring method is used, re-wiring using screws.
Basically, you have to check your wiring one junction box at a time until
you find something wrong.
If you want to be very cautious, you can pull the MAIN fuses or MAIN CB but
leave all the branch circuits fuses in or the CB in "ON."
With a "cold" system, you can use the resistance testing function to do a
LOT of testing.
For example, if you have a good ground then the resistance at any outlet
between neutral and ground should be a fraction of one ohm.
Depending upon what is still "ON" the resistance between HOT and Neutral or
Ground should be more than one ohm but less than, say, 10 ohms.
You can do a lot of safe checking for open wires, reversed connections, and
missing grounds.
You can even do stuff like measure resistance between the ground of an
outlet that test right to the wires of your "bad" outlet.
Do you have aluminium house wire? I have seen a problem with
the corrosion between the disimilar metals. Pull all the outlets
on the circuit and test. Also get one of those testers to
see if someone switched neutral and ground or some other wiring
mistake. Maybe you are feeding in series through some applicance.
If that's the case, check the wire connections at the outlet immediately
before that one.