thanks,
dp
What is the pressure at the main? What is your elevation w/respect to
the main? What is the water "demand" in your house, ie, the fixture
count.
A 1" line, even without bends and fittings, will create a loss of
pressure due to the friction of the water passing thru the pipe.
For instance, using a Williams & Hazen formula for schedule 80 pipe,
a 1" pipe 1500 ft long would create a pressure loss of 35 # @ 8 GPM
flow. This is schedule 80 pipe -- what will you be using?
Go larger, mush larger -- you only pay once, but enjoy the benifits as
long as you live in the house!!
lyle
--
ltu...@primenet.com (Lyle Tuttle)
"Do what's right. Do it right. Do it right now."
For normal household requirements, 6GPM will handle the everyday things.
However, if you ever plan on using the water for fire protection, or if
you ever anticipate putting in a sprinkler system, you'll really need
30+ GPM. For those applications, even a 1.5" pipe is marginal.
I would say the lions' portion of the cost is digging the trench, not in
the incremental cost between 1", 1.5", and even 2" pipe.
As far as the location of the pressure regulator, I'd put it at the
house, so that the pressure inside the house stays fairly constant.
If you put the regulator 1500' away, it will regulate pressure 1500'
away , not at your house. As your water requirements vary, the pressure
to
the house is going to vary depending upon the pressure loss in the 1500'
pipe for the flow rate at that instant.
<><><><><><><><><><><><><><><><><><><><><><><><><><><><>
HELP WITH BUILDING CODES
http://www.CodeCheck.com
mailto:red...@codecheck.com
CodeCheck.com=A9 by Redwood Kardon
<><><><><><><><><><><><><><><><><><><><><><><><><><><><>
>I'm getting ready to run a water line for city water. I have a couple
>of questions. The distance to the house from the meter is about
>1500'. I'm considering a 1" line. Is this sufficient? Also I figure
>I'll need a pressure regulator. Should the regulator be mounted at
>the meter or the house?
I think I would go 1.5" on a long run like this. If you need a
pressure regulator, it should be located where the line goes into the
house.
--
Vic Dura (vpd...@hiwaay.net) DuraHaven, Rogersville AL 35652
I have a 1.5" line running about that distance and have plenty
of volume and pressure. I suspect 1" might do, but the
difference in cost to go to 1.5" might be worth the peace of mind.
Consider putting in a check valve near the public supply end of
your line. You can get them for under $20 at a plumbing store
or large "home center". Then, if the public line needs repair
or has a leak, it won't siphon all the water out of your lines
and hot water tank. And if your house is below any part of your
line, you'll have a bit of a reserve supply.
--
W.J. Emerson
fsa0...@wvnvm.wvnet.edu