On 7/12/2013 11:31 PM,
gfre...@aol.com wrote:
> Not true at all for a single 14-2 NM.
> A single conductor or cable can fill 53% of a raceway but when you get
> to two, that drops to 31%
>
> Ok to make the math easier this is metric
> Using Southwire RX
>
> width...........area
> 14-2 9mm ...63.6 mm2
> 12-2 10mm..78.5 mm2
> 14-3 7mm....38.5 mm2
> 12-3 8mm....50.24 mm2
> 10-3 9mm....63.6 mm2
>
> From Table 4
> Trade size..one wire 53%...2 wires 31%....3 or more 40%
> 1/2"EMT....104 mm2 ...........61mm2............78mm2
> 3/4"EMT....102 mm2 ...........106mm2...........137mm2
> 1" EMT......295 mm2 ...........172mm2...........222 mm2
>
> Two 14-2 RX would need a 1" EMT to be legal.
>
1" PVC might be easier to handle and install but I don't know about the
capacity. It's been a while since I installed any and I often used
calipers to compare the inside of different types of conduit when
planning a job. Scrap pieces of conduit and wire come in handy when you
want to do a practical measure of what you're installing especially when
it's signal or network cables that may not appear in any tables. Any of
the phone system or computer network installations I've done have 3/4"
EMT run to every phone or network outlet inside any wall but the wires
are not carrying any significant power. It makes it easier to install
the wires, besides, I'm lazy. ^_^