On 3/16/2013 3:30 PM, DerbyDad03 wrote:
> Without going into all the details about no free breakers, location of
> junction boxes, finished ceilings, etc., I'm looking for a "yes it's code"
> or "no it's not code" answer to this question:
>
> There's a junction box with a 14/2 without ground coming directly from the
> panel. Leaving this box is a 14/2 without ground and a 14/2 with ground.
> The ground wire is attached to the junction box but of course it isn't
> actually grounded.
>
> Can you run a single insulated ground wire from the panel to the junction
> box to provide a ground for the 14/2 with ground that leaves the box.
...
While others have answered as originally asked here, "yes". There are
exceptions in several places to allow the equipment grounding conductor
for the grounding-type receptacle that has been added to a circuit where
no equipment grounding conductor is available to be run separate from
the other circuit conductors and to run by itself without a cable or
raceway.
W/o the whole Code the various subsections that allow the conductor to
be run separately from the circuit conductors go to 300-3(a) and (b)
exception, then to 250-57(b) exception No. 3. To follow the Code on why
this conductor can be run by itself without a cable or raceway go to
250-92(c)(2) and the exception.
The Code is realistic in approaching existing work understanding there
sometimes just isn't a practical way "to get there from here".
What I didn't notice anybody else mentioning was that there's another
alternative as well. And that is one from
250-50(a)and(b) Exception --
"For replacement of nongrounding-type receptacles with grounding-type
receptacles and for branch-circuit extensions only in existing
installations that do not have an equipment grounding conductor in the
branch-circuit, the grounding conductor of a grounding-type receptacle
outlet shall be permitted to be grounded to any accessible point on the
grounding electrode system as described in 250-81."
It doesn't _necessarily_ have to go back to the panel iow.
I don't have recent copy at hand and didn't work at trying to find
online--the above is from a ca '96 NEC release. I don't believe any of
this has been changed altho as always, if it is really necessary to
follow Code it's the local jurisdiction that is going to control so a
phone call to City Hall is probably the ticket.
As for the Edison circuit there's not enough info give to fully
understand what was done (at least in the parts of the thread I've read)
so I'll not try to address it directly.
The following link, however, does had a pretty complete list of the
points NEC makes that you can use on the actual configuration to check
against...
<
http://inspectapedia.com/electric/multiwir.htm#code>
Scrolling around on that page will lead you to other useful areas as well...
--