I've been in a home for one year now, that was built 8 years ago. The
garage has a brick gable, with a window in the middle, above it. It
appear that the lentil that the building company put in is not strong
enough to support all of that weight and is starting to sag in the
middle which has caused the brick above it to start separating (one
large verticle crack from the window and growing larger as it moves
down to the lentil. My QUESTION is, what is the best and cheapest
repair for this. I've had a range of recommended fixes from taking
all of the bricks out and replacing the lentil, to putting in
lagger(?) bolts and tuck points(?). Is the latter option just a short
term fix? Does anyone have any suggestions? Thanks, Daniel

longshot

unread,
May 1, 2007, 8:54:47 AM5/1/07
to
I love lentil beans


MarkL

unread,
May 1, 2007, 9:15:07 AM5/1/07
to
It's lintel, not lentil. I worked for a general contractor way back
when, we did a few jobs where we changed the overhead door on
commercial buildings and had to take the brickwork out to modify the
opening (generally to make it taller). Assuming this is brick veneer
and not structural brick, I would remove the brick back far enough to
put in a new lintel, then replace the brick. Make sure you save as
much of the brick as possible so it will match when you put it back
up. You probably want to get a civil engineer or architect to do the
calculation for a replacement, especially if you're in a hurricane or
earthquake area. There can be considerations other than the weight it
supports, so don't let another contractor make a poor choice. You can
probably tear everything out yourself and set the lintel if you're
ambitious, but laying brick takes a fair bit of skill, probably not a
DIY project. You should probably also think about shoring up the
middle of the existing lintel until you can get this repaired. It
could cause quite a bit more damage (and maybe injury) if it fails
before you get it fixed. You could buy a basement support column and
put it in the middle of the span, that should stabilize it for awhile
and still allow you to use the garage.

dpb

unread,
May 1, 2007, 9:19:19 AM5/1/07
to
On May 1, 7:39 am, Daniel Fenner <dbfen...@gmail.com> wrote:


Can't tell w/o seeing but almost certainly you'll have to get to it to
either add structure or replace it for a permanent fix. If it is
steel and accessible from below and you have clearance over the garage
door, I suppose it would be theoretically possible to add some
additional strength there but you still need a structural guy to come
look and determine what is the root cause and the needed fix.

As a note, "best" and "cheapest" are almost always dichotomous notions
and I suspect that is the case here...

Goedjn

unread,
May 1, 2007, 12:04:22 PM5/1/07
to
On 1 May 2007 05:39:23 -0700, Daniel Fenner <dbfe...@gmail.com>
wrote:

Onions are not a good choice for structural materials.
Is the structure double-wythe brick, or a brick facade
over a wood frame? Are you sure the crack is because
the lintel isn't adequate, and not because the whole
foundation is moving, or because the roof
is spreading the tops of the bearing walls?
The fact that the crack started at the window makes me
a little suspicious. If it was sagging, I'd expect the
crack to start at the top of the door and work it's
way up. Does a straightedgee show sagging?

How much headroom do you have
in the doorway? Is the room above the garage finished space,
or can you get at the structure from the inside?
How much ugly are you willing to put up with?

If you can spare the headroom, the SIMPLEST fix
would be to jack the middle of the door back into
place, and weld a big chunk of angle iron to the
underside of the existing lintel to
reinforce it. I'd seriously consider
running cable and a turnbuckle under the window
across the whole width of the garage, while you're
at it.


Art

unread,
May 1, 2007, 2:20:38 PM5/1/07
to
Most brick veneers houses are poorly done. Visit www.bia.org to read the
tech reports to learn how brick veneer should be installed. The lintel
could be too thin or not long enuf. Also the masonry is supposed to be
fastened to the wood house studs every couple feet. Since most builders put
opaque paper on top of the sheathing before bricking it up, how could the
masons possibly know where the studs are unless they are marked on the paper
(never done). On top of that, many masons leave out flashing around doors
and windows and leave weepholes plugged. I had all of these defects in my
new home and had to hire a mason for big bucks to fix them all. That is why
I will never again buy a brick veneer house.


"Daniel Fenner" <dbfe...@gmail.com> wrote in message
news:1178023163.1...@y80g2000hsf.googlegroups.com...

mm

unread,
May 1, 2007, 6:19:01 PM5/1/07
to
On Tue, 01 May 2007 12:54:47 GMT, "longshot" <long...@aol.com> wrote:

>I love lentil beans
>
Me too.

I wouldn't know what lintel meant if it weren't for my Block City. My
best friend had Brick Town.

I guess they have both been replaced by Leggos.

Daniel Fenner

unread,
May 2, 2007, 7:42:13 AM5/2/07
to
> > term fix? Does anyone have any suggestions? Thanks, Daniel- Hide quoted text -
>
> - Show quoted text -

Thanks for the info Mark. I put up a supporting post yesterday and am
waiting for a couple more estimates before I have the work done.

Daniel Fenner

unread,
May 2, 2007, 7:49:44 AM5/2/07
to
On May 1, 11:04 am, Goedjn <p...@mail.uri.edu> wrote:
> On 1 May 2007 05:39:23 -0700, Daniel Fenner <dbfen...@gmail.com>

Thanks for your reply. The crack actually started at the headers, I
just wasn't clear in my explanation. And yes, the beam does show
obvious sagging. You mentioned the roof possibly spreading the tops
of the bearing walls. Can you explain to me in more detail? I've got
a structural engineer coming out today to look at the problem and I'll
be curious to see if he mentions that.

Daniel Fenner

unread,
May 2, 2007, 7:55:48 AM5/2/07
to
On May 1, 1:20 pm, "Art" <begunaNOSPAMPLE...@mindspring.com> wrote:
> Most brick veneers houses are poorly done. Visitwww.bia.orgto read the

> tech reports to learn how brick veneer should be installed. The lintel
> could be too thin or not long enuf. Also the masonry is supposed to be
> fastened to the wood house studs every couple feet. Since most builders put
> opaque paper on top of the sheathing before bricking it up, how could the
> masons possibly know where the studs are unless they are marked on the paper
> (never done). On top of that, many masons leave out flashing around doors
> and windows and leave weepholes plugged. I had all of these defects in my
> new home and had to hire a mason for big bucks to fix them all. That is why
> I will never again buy a brick veneer house.
>
> "Daniel Fenner" <dbfen...@gmail.com> wrote in message

>
> news:1178023163.1...@y80g2000hsf.googlegroups.com...
>
>
>
> > I've been in a home for one year now, that was built 8 years ago. The
> > garage has a brick gable, with a window in the middle, above it. It
> > appear that the lentil that the building company put in is not strong
> > enough to support all of that weight and is starting to sag in the
> > middle which has caused the brick above it to start separating (one
> > large verticle crack from the window and growing larger as it moves
> > down to the lentil. My QUESTION is, what is the best and cheapest
> > repair for this. I've had a range of recommended fixes from taking
> > all of the bricks out and replacing the lentil, to putting in
> > lagger(?) bolts and tuck points(?). Is the latter option just a short
> > term fix? Does anyone have any suggestions? Thanks, Daniel- Hide quoted text -
>
> - Show quoted text -

You made an interesting point that the masonry "is supposed" to be
fastened every couple of feet. If I find out this is not the case, is
the home builder somehow liable for this problem? The house is only 8
years old and it's my understanding that under Oklahoma state law,
home builders are required to have a 10 year warranty on their homes
(looking into the details of this). Any thoughts? I'm hoping for an
inexpensive fixso that I don't have to go the legal route.

Goedjn

unread,
May 2, 2007, 11:17:51 AM5/2/07
to
On 2 May 2007 04:49:44 -0700, Daniel Fenner <dbfe...@gmail.com>
wrote:

>On May 1, 11:04 am, Goedjn <p...@mail.uri.edu> wrote:

It was just an alternative explanation for the cracking
if the problem wasn't a sagging lintel. Since you have
an obviously sagging lintel, spreading is probably a non
issue.

DanG

unread,
May 2, 2007, 9:08:32 PM5/2/07
to
The number of brick ties to sheathing will have very little to do
with your problem. The lintel is just not right. The wood was
probably undersized, wrong grade, or wrong species. The lintel
iron was not strong enough to carry the load. You need to
determine if the wood portion has bowed down to verify the
diagnosis of wrong wood. The fact that the brick has bellied says
the steel lintel was undersized. The two should not have been
tied together in my opinion. One of many reasons I don't like
brick gables.

--
______________________________
Keep the whole world singing . . . .
DanG (remove the sevens)
dgri...@7cox.net

"Daniel Fenner" <dbfe...@gmail.com> wrote in message

news:1178106948.8...@o5g2000hsb.googlegroups.com...

Oren

unread,
May 3, 2007, 12:11:05 AM5/3/07
to
On Tue, 01 May 2007 12:54:47 GMT, "longshot" <long...@aol.com> wrote:

>I love lentil beans
>

I missed out on the bean count.

I like Lima beans.
--
Oren

If your not getting it from the horses mouth, You're listening to the wrong end.

Houstonbrick

unread,
Jun 11, 2016, 9:44:05 PM6/11/16
to
replying to Daniel Fenner, Houstonbrick wrote:
We see this problem often here in Houston,TX..We are a small masonry repair
contractor in Spring, TX..There are very few options available. If there is a
way to access your home warranty, you could ask them to repair. Second option
is to call someone like us. We would demolition 2 to 3 feet of garage and
replace lentil with stronger back. A stronger piece of iron the is 4 inches on
one side and the other side 5 to 6 inches. If the masonry above garage is
attached well with wall ties,there is a possibility that entire gable will
have to come down. This is not a DIY project. It's best to call a pro. In our
area it is considered an extensive repair. You can expect to pay 3200 to 7000.
There really is no easy way to do it right. The guys at www.masoncrew.net are
wonderful and you can trust them to give you a free evaluation if you send
pictures.

--
posted from
http://www.homeownershub.com/maintenance/lentil-beam-above-garage-is-bending-213768-.htm


Uncle Monster

unread,
Jun 11, 2016, 11:22:59 PM6/11/16
to
On Saturday, June 11, 2016 at 8:44:05 PM UTC-5, Houstonbrick wrote:
> replying to Daniel Fenner, Houstonbrick wrote:
> We see this problem often here in Houston,TX..We are a small masonry repair
> contractor in Spring, TX..There are very few options available. If there is a
> way to access your home warranty, you could ask them to repair. Second option
> is to call someone like us. We would demolition 2 to 3 feet of garage and
> replace lentil with stronger back. A stronger piece of iron the is 4 inches on
> one side and the other side 5 to 6 inches. If the masonry above garage is
> attached well with wall ties,there is a possibility that entire gable will
> have to come down. This is not a DIY project. It's best to call a pro. In our
> area it is considered an extensive repair. You can expect to pay 3200 to 7000.
> There really is no easy way to do it right. The guys at www.masoncrew.net are
> wonderful and you can trust them to give you a free evaluation if you send
> pictures.
> --
>

Tragically, five years ago, Dan was sitting in his running car when the garage collapsed. The car exploded and Dan was killed in the fire that destroyed both the car and garage. It was awful, Dan left behind 18 children. o_O

[8~{} Uncle Burning Monster

Percival P. Cassidy

unread,
Jun 12, 2016, 5:46:38 PM6/12/16
to
On 06/11/2016 09:44 PM, Houstonbrick wrote:
> replying to Daniel Fenner, Houstonbrick wrote:
> We see this problem often here in Houston,TX..We are a small masonry repair
> contractor in Spring, TX..There are very few options available. If there
> is a
> way to access your home warranty, you could ask them to repair. Second
> option
> is to call someone like us. We would demolition 2 to 3 feet of garage and
> replace lentil with stronger back. A stronger piece of iron the is 4
> inches on
> one side and the other side 5 to 6 inches. If the masonry above garage is
> attached well with wall ties,there is a possibility that entire gable will
> have to come down. This is not a DIY project. It's best to call a pro.
> In our
> area it is considered an extensive repair. You can expect to pay 3200 to
> 7000.
> There really is no easy way to do it right. The guys at
> www.masoncrew.net are
> wonderful and you can trust them to give you a free evaluation if you send
> pictures.


That's what you get for building beams of lentils; you're supposed to
use lumber.

And, yes, I know this is an old post to which I am responding.

Perce

thekma...@gmail.com

unread,
Jun 12, 2016, 5:49:48 PM6/12/16
to
MarkL wrote: "It's lintel, not lentil. "

Welcome to America, where everyone is
either ADHD, dyslexic, or both!

Nil

unread,
Jun 12, 2016, 6:15:52 PM6/12/16
to
On 12 Jun 2016, "Percival P. Cassidy" <Nob...@NotMyISP.net> wrote in
alt.home.repair:

> That's what you get for building beams of lentils; you're supposed
> to use lumber.

Instead of lentils, try I-beans.

Stormin Mormon

unread,
Jun 12, 2016, 6:52:51 PM6/12/16
to
Sounds like you know your beans.


--
.
Christopher A. Young
learn more about Jesus
. www.lds.org
.
.

DerbyDad03

unread,
Jun 12, 2016, 9:48:01 PM6/12/16
to
On Sunday, June 12, 2016 at 6:15:52 PM UTC-4, Nil wrote:
> On 12 Jun 2016, "Percival P. Cassidy" <Nob...@NotMyISP.net> wrote in
> alt.home.repair:
>
> > That's what you get for building beams of lentils; you're supposed
> > to use lumber.
>
> Instead of lentils, try I-beans.
>

It's easier to see eye-beans.

re: "The garage has a...lentil that...is not strong enough..."

Beams, beams, they're good for support
The more you use, the stronger your car port
The stronger your car port, the better you feel
So use those beams that are made from steel

Neill Massello

unread,
Jun 12, 2016, 9:56:11 PM6/12/16
to
Uncle Monster <uncl...@gmail.com> wrote:

> Dan left behind 18 children.

That's a lot of sprouts.

Micky

unread,
Jun 13, 2016, 1:45:01 AM6/13/16
to
On Sun, 12 Jun 2016 14:49:44 -0700 (PDT), thekma...@gmail.com
wrote:

>MarkL wrote: "It's lintel, not lentil. "

I probably wouldn't know the word but two of them came with my Block
City when I was 7 or 8, one for a round door and one for a square-top
door.

mako...@yahoo.com

unread,
Jun 13, 2016, 9:23:02 AM6/13/16
to
Did you hear about the agnostic dyslexic insomniac?

He would lie awake at night wondering about whether or not there is a dog.

M

hah

unread,
Jun 13, 2016, 3:24:16 PM6/13/16
to
Then god licks him in the face...

bs

unread,
Apr 30, 2018, 6:14:05 PM4/30/18
to
replying to DerbyDad03, bs wrote:
Yes, this is an old post. For those reading it looking for a remedy: Most
likely, the lintel was not properly fastened on the ends. This is what causes
it to sag. Common problem, home warranty issue for sure. If in Texas, it's
10 years.

--
for full context, visit https://www.homeownershub.com/maintenance/lentil-beam-above-garage-is-bending-213768-.htm


Uncle Monster

unread,
Apr 30, 2018, 6:51:20 PM4/30/18
to
On Monday, April 30, 2018 at 5:14:05 PM UTC-5, bs wrote:
> replying to DerbyDad03, bs wrote:
> Yes, this is an old post. For those reading it looking for a remedy: Most
> likely, the lintel was not properly fastened on the ends. This is what causes
> it to sag. Common problem, home warranty issue for sure. If in Texas, it's
> 10 years.
> --
>

You're too late, DerbyDad03 was abducted by Mutant Democrats From Outerspace. It's feared they tried to convert him into a homosexual HITLERy Clinton supporter. It didn't work so they fed him to The Giant Mutant Gerbils From Outerspace. It was a tragic loss for his children and The Pinebox Derby community. O_o