After doing a little online research, I suspect it might be a bad
thermocouple, which is a relatively easy fix. But I thought I'd run
this by the good, knowledgeable people of this newsgroup first.
Is there anything else I should look at?
-Frank
--
Here's some of my work:
http://www.franksknives.com/
That model may actually be: 80U-19A
Typically, a bad T/C will keep the pilot from lighting (though not always).
Any failure in the 24V control to the gas valve will keep the
Main burner from igniting. An AC voltmeter will help tracking
the cause.
For example:
Your Day/Night should have a Fan/Limit switch like this:
http://tinyurl.com/5m3ws5
Failure of the Limit contact to close will keep the gas valve
from opening.
Jim
> Frank Warner wrote:
> > I've got an older "Day and Night" natural gas furnace in my home, model
> > #800-19a. Setting the mercury thermostat turns the blower on, the
> > standing pilot is lit, but the burners do not ignite.
> >
> > After doing a little online research, I suspect it might be a bad
> > thermocouple, which is a relatively easy fix. But I thought I'd run
> > this by the good, knowledgeable people of this newsgroup first.
> >
> > Is there anything else I should look at?
> >
> > -Frank
> >
> I would suspect a flame safety device. This could be a thermocouple or
> some sort of optical flame sensor.
> HTH
> EJ in NJ
>
I'm not sure my furnace has a flame sensor other than the thermocouple.
I'm at work so I can't check this, but will take another look when I
get home tonight.
Thanks for the tip.
Thanks, Jim. My furnace does indeed have a Fan/Limit switch identical
to the one you linked. I'll check this part as you recommended.
>I've got an older "Day and Night" natural gas furnace in my home, model
>#800-19a. Setting the mercury thermostat turns the blower on, the
>standing pilot is lit, but the burners do not ignite.
>
>After doing a little online research, I suspect it might be a bad
>thermocouple, which is a relatively easy fix. But I thought I'd run
>this by the good, knowledgeable people of this newsgroup first.
>
>Is there anything else I should look at?
>
>-Frank
Definitely NOT the thermocouple if the standing pilot is lit. The
thermocouple is the protection to turn off the gas to the pilot if it
goes out.
> I've got an older "Day and Night" natural gas furnace in my home, model
> #800-19a. Setting the mercury thermostat turns the blower on, the
> standing pilot is lit, but the burners do not ignite.
>
> After doing a little online research, I suspect it might be a bad
> thermocouple, which is a relatively easy fix. But I thought I'd run
> this by the good, knowledgeable people of this newsgroup first.
>
> Is there anything else I should look at?
>
> -Frank
Un-freaking-believable!!!
It was bugs! BUGS!
I took the thermocouple out hoping to polish it down a little. The
pilot assembly came out with it. As I checked the parts, little pieces
of insects started falling out of the pilot nozzle. Then bigger pieces.
Then a whole housefly. Mummified. Probably in there since the furnace
was fired up last in February or something. It seems they had flown up
there, perhaps attracted by the rotten egg smell, during the long
dormant season here on the Central California Coast, and died,
partially plugging the pilot.
I cleaned out all the parts, put everything back together, and the
burners fired right up!
I still can't believe this. Been in this house twenty years and never
had anything like that happen before.
Lurkers with similar symptoms take note.
LOL
Just when you think you've seen and heard it all...
good job.
Jim
That's not a bug, it's a feature. Been hanging around M$ windows to
long...
I've cleaned out entire ant colonies from HVAC
equipment. Insects are one of the first things
I look for when HVAC systems quit working. I've
also removed the dessicated carcases of mice from
control circuits because some silly human failed
to pop a plug into a 1/2" conduit knock out. Mice
will crawl right through those 1/2" holes and get
electrocuted which will often short out the power.
Hole plugs are readily available and the phone
companies and other utilities use insecticide strips
inside control boxes to prevent insect infestation.
I don't know where I could get the same kind of
insecticide strips, I'll have to search.
BTW, those are some incredible knives Frank. I wish
I had that sort of artistic skill.
TDD
Don Young
They are not rare systems.
I've still got four older Bryant furnaces in my rental apartments that
don't have a safety pilot system.
They have a bimetallic switch heated by the pilot. If the pilot flame
goes out, the switch opens and shuts down the main gas valve. However,
the pilot gas keeps flowing. One of these furnaces had the pilot blow
out over a summer seaon. the tenant never noticed the gas smell.
Probably most went up the chimney.
Recently, a local gas company tech told me he still see lots of them.
They are pretty common in my area and are not considered unsafe.
Doug
>Don Young wrote:
WAY before, if in fact it ever was allowed.
There were apparently bimetallic thermo pilots at one time too - but
even that has been nixxed for a long time.
Help!!! I am having a similar problem with an old hanging furnace. I
woke this morning with the blower fann running but no heat! I had to
throw the curcuit to get the fan to stop. I have cleaned the
thermocouple, it was slightly corroded, but i cant seem to get the
pilot to ignite. Does electricity need to be on to have this ignite?
Please help!!! Plus i might not even be in the right spot . Any info
would be most helpful!!
REPLACE the thermocouple if you can't light the pilot..
If the thermocouple goes to the gas valve a bad thermocouple will kill
the pilot. Some real old systems had the thermocouple go to a
solenoid/relay which interrupted the thermostat circuit to the main
burner gas valve. There was a pushbutton to reset the solenoid. If the
thermocouple goes to the gas valve Tony's suggestions sound good.
>>> Definitely NOT the thermocouple if the standing pilot is lit. The
>>> thermocouple is the protection to turn off the gas to the pilot if it
>>> goes out.
>> Hi,
>> Right, if thermoouple is bad pilot won't stay lit. Thermocouple's
>> function is supplying small amount of gas to keep the pilot lit.
>> When it is calling for heat, measure across gas valve terminal to see
>> 24V AC. If you do, gently tap it to see what happens. Either you're not
>> getting power to valve or the valve is sticking.
>
> Help!!! I am having a similar problem with an old hanging furnace. I
> woke this morning with the blower fann running but no heat! I had to
> throw the curcuit to get the fan to stop. I have cleaned the
> thermocouple, it was slightly corroded, but i cant seem to get the
> pilot to ignite. Does electricity need to be on to have this ignite?
> Please help!!! Plus i might not even be in the right spot . Any info
> would be most helpful!!
Have you lit the pilot before (do you know how it is supposed to be lit)?
The valves with thermocouple I have seen you turn a knob on the gas
valve to a "pilot" position, push down on the knob and light the pilot
while holding the knob down. The pilot should light with a bad
thermocouple and no power. You need to hold the knob down until the
thermocouple gets hot. If you waited long enough and the pilot goes out
when you release the knob the thermocouple is probably bad. If the pilot
lights turn the knob back to the original position.
--
bud--