Anyway. How it that possible? Is there a bad connection up the line of
outlets that would cause it to read 50 volts instead of the normal 115
or 120?
*Is it a switch or a receptacle that has low voltage? Is something not
working properly or did you just go around checking voltages?
I can think of several possiblities. If you can follow the
wire and see what it is connected to (intentionally or not
intentionally) you likely will find the problem. Be sure to check out
grounds. This could be related to a bad ground.
Insufficient info.
50 volts with something plugged in or not plugged in etc.? Switch on
or off?
50 volts in reference to what? Ground? Live to neutral?
If the workmanship of replacing the outlets and switches was as vague
as the enquiry ........ !!!!
sligoNoSPAM...@hotmail.com needs to be more specific.
Back stabbed outlets again?????
Why were you checking?? as the previous poster asked, what happens
when you plug in a light or something else????
yes, 50V could easily be phantom voltage and the recep is really
completely dead
nate
"in2dadark" <in2d...@yahoo.com> wrote in message
news:0976fa1d-76ea-461f...@r24g2000yqd.googlegroups.com...
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"in2dadark" <in2d...@yahoo.com> wrote in message
news:0976fa1d-76ea-461f...@r24g2000yqd.googlegroups.com...
The socket does not work at all when I plug something into it. It did
in the past after I switched out all the old ones. I put in another
new socket thining that one may have gone bad somehow. But the 2nd new
one doesn't work and th all the wires are on correctly. There is no
jump at this box, just 3 wires, black, white and bare.
Ha.. I did the whole house. I know how to replace a receptical...
Nothing works at this outlet and it doens't have a switch. I guess
I'll look up the line.
I agree. One would think if you get 'any' reading it would either be
full on or nothing..I triple checked it and the meter setting.
look at other receps on the same circuit, might have a bad connection at
the one previous to it on the circuit
nate
--
replace "roosters" with "cox" to reply.
http://members.cox.net/njnagel
*Yes go to the receptacle that feeds this receptacle and check the
connections.
You can replace a receptical, but you have a hard time
spelling receptacle.
http://www.google.com/#hl=en&source=hp&q=dictionary+receptical+&aq=f&aqi=&oq=&fp=b36c7832dbb01be6
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"in2dadark" <in2d...@yahoo.com> wrote in message
news:075028bf-c351-4ccf...@r5g2000yqb.googlegroups.com...
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"Nate Nagel" <njn...@roosters.net>
wrote in message news:hgs19...@news6.newsguy.com...
Oh.. Ok.. Now I know what you mean by 'backstab'... I didn't even buy
the ones that have that. Those were more I think. RECEPTaCLe..there..
YOu should go through all the grammatical errors on this forum as
well. It'll give you something to live for and a reason to feel
supirior...
Good. Backstabs SUCK. Although I feel obligated to point out that
"spec grade" receps from the real supply house near me (Dominion
Electric) are $15/10 - probably about what you would pay for consumer
grade at the Big Box. (no backstabs on spec grade stuff either) I use
the Good Stuff exclusively once I found that Dominion was open on Saturdays.
I am quite annoyed that one of the Decora light switches that I
installed only a couple years ago is already going flaky - and it's not
even in a high use location. Soon as I find a double toggle vintage
.040" pressed brass switchplate, it's gone for a spec grade toggle. The
cheap stuff is... cheap.
Which reminds me, I need some utility knife blades. (there's a logical
line of thought that led up to that... need to run some auxiliary
grounds before I can use the metal switch plates, which means that I
need to break the paint around my baseboards so I can pry them off)
> YOu should go through all the grammatical errors on this forum as
> well. It'll give you something to live for and a reason to feel
> supirior...
^^^^^^^^
I'm just going to assume that that was intentional humor and not
failtastic irony.
"Dr. Livingstone, the troll, I presume?"
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"Nate Nagel" <njn...@roosters.net>
wrote in message news:hgu0m...@news7.newsguy.com...
...
>
>yes, 50V could easily be phantom voltage and the recep is really
>completely dead
>
>nate
Remember the OP mentioned he had a ANALOG meter.
There's no such thing as "phantom voltage," anyway; there are, however,
bad measurement practices and poorly designed test instruments.
No matter what kind of meter if there is doubt put a load on the
circuit then measure the voltage. In this case just plug something
in. I'll bet the voltage reads zero then.