From the UL White book:
"Circuit breakers marked "SWD" and rated 347 V or less are suitable for
switching fluorescent lighting loads on a regular basis at their rated
voltage.
"Circuit breakers marked "HID" have been investigated for switching
high-intensity discharge lighting loads on a regular basis at their
rated voltage.
"Circuit breakers rated 50 A or less and 125/250 V or less are
investigated for use with tungsten-filament lamp loads.
"Circuit breakers are tested under overload conditions at six times the
rating to cover motor circuit applications and are suitable for use as
motor circuit disconnects per Section 430.109 of the NEC.
"Circuit breakers investigated for use with heating, air conditioning
and refrigeration equipment comprising multi-motor or combination loads
are marked "HACR TYPE," in conjunction with the Listing Mark. Such
circuit breakers are suitable for use with heating, air conditioning and
refrigerating equipment marked for use with HACR type circuit breakers."
end quote
Both incandescent lamps and motors have an inrush/start current of about
6x normal current. Breakers are intended to not trip powering on
incandescents.
Contacts can be damaged by arcing when the breaker is opened repeatedly.
The old fluorescent ballasts were inductive and caused arcing - hence
SWD rating. (I don't think the electronic ballasts arc much on opening.)
My guess is HID ballasts are even more inductive and arc more on
opening. I don't remember ever seeing a "HID" rating.
I have no idea how "HACR" breakers are different.
A garden variety 20A SquareD breaker I looked at is marked "SWD" and "HACR".
--
bud--