[combining 2 posts]
[and I saw your 2 recent posts - haven't looked at links yet]
>> But I agree it is a stupid idea (allowed by the NEC).
> I am curious what the answer was in the ROP.
I have looked at ROP/ROC on occasion because you can sometimes see what
the logic was. Expect that is why "curious".
(I did not discover either of these anomalies.)
(I have seen at least one proposal from you.)
Your objection (20A on 15A ckt) is certainly not surprising.
Have I mentioned that it is a stupid idea?
==============================
>>
>> (The proposal was at least 10 years ago.)
> I looked at the 2010 (for the 11 code) and I didn't see it. I will
look at some others
Damn. You made me look for my notes. I finally found them.
====================================
For 20A single on 15A ckt:
==================================
For the 2008 NEC there was a proposal to change 210.12-B-1 (single
receptacle) to require the receptacle be equal to the branch circuit
rating. The argument was specifically about a 20A singe receptacle on a
15A circuit.
The code panel rejected the change. Their statement [with my comments] was:
"The recommendation would be overly restrictive in the case of some
larger receptacle applications that do not directly correspond to the
standard ratings of overcurrent protective devices." [It is not
difficult to allow this and limit a 20A receptacle on a 15A circuit.]
"The panel notes that a 20-ampere receptacle installed on a 15-ampere
branch circuit is protected within it’s rating." [The panel apparently
does not care that you can plug in readily available devices that are
over the circuit rating.]
So the code panel apparently has no problem with a 20A single receptacle
on a 15A circuit. But IMHO this can be tagged under 406.3-A, and it
appears to me that the code panel for 406 does not agree.
============================
2008 NEC ROP
----------------------
2-8 Log #822 NEC-P02 Final Action: Reject
(210.21(B)(1))
Submitter: Jeffrey A. Fecteau, City of Peoria, Arizona
Recommendation: Revise text to read as follows:
Single Receptacle on an Individual Branch Circuit. A single receptacle
installed on an individual branch circuit shall have an ampere rating
not less than equal to that of the branch circuit.
Substantiation: As currently written, it is currently being interpreted
to allow a 20 ampere single receptacle to be installed on a 15 ampere
individual branch circuit. 20 ampere single receptacle is not less than
that of the branch circuit.
This would allow a 20 ampere rated piece of equipment to be connected to
a 15 ampere circuit.
See supporting material for response to a question posed to Code
Question of the day, hosted by NEIS, and answered by Ed Holt (Electrical
Inspector - Architect of the Capitol - Instructor - The College of
Southern Maryland)
Note: Supporting material is available for review at NFPA Headquarters.
Panel Meeting Action: Reject
Panel Statement: The recommendation would be overly restrictive in the
case of some larger receptacle applications that do not directly
correspond to the standard ratings of overcurrent protective devices.
The panel notes that a 20-ampere receptacle installed on a 15-ampere
branch cirrcuit is protected within it’s rating.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
=================================
[I have not looked this up today]
A while back I ran across 406.3-A which, IMHO, prohibits almost all 20A
single receptacles on a 15A circuit:
15/20A receptacles "shall be installed only on circuits of the voltage
class and current for which they are rated." This applies only to
"grounding-type" receptacles, so you presumably could put an ungrounded
20A single receptacle as the only receptacle on a 15A circuit (and only
in those cases where you can use an ungrounded receptacle). Oddness
remains, but is greatly limited.
(210.21 (B)(2) and (B)(3). of course allows a 15A receptacle on a 20A
circuit.)
I would expect a rule for receptacles to be in the article on
receptacles, 406.
There remains a hole - you can install a single (not a duplex) 20A
non-grounding receptacle on a 15A circuit that has no ground if it is
the only receptacle on the circuit. Rather limited application. And you
would have to find a single 20A receptacle without a ground.