Are these bulbs interchangable, or with T8 bulbs only go into specific
fixtures?
I intend on opening up the fixtures to check the ballasts next time I'm up
in the ceiling, but I'd like to know.
"Calab" <mys...@csd.ca> wrote in message
news:TtJoj.33766$4w.26391@pd7urf2no...
"Calab" <mys...@csd.ca> wrote in message
news:TtJoj.33766$4w.26391@pd7urf2no...
A universal ballast can usually be used for one or two bulbs and can work
with 120volts to 277volts. But they are not universal for T12 and T8.
Completely incorrect answer: Here are the specs from a Keystone ballast:
KTEB-240-1-TP /C (Electronic Fluorescent, 120V)
2x CFQ26W/G24q , CFTR32W/GX24q , F25T8 , F30T12 , F32T8 , F34T12 ,
F40T12 , F40T12 (25W)
>
>
"SBH" <Mea...@bluebottle.com> wrote in message
news:eeednaqn7YpfSzja...@wideopenwest.com...
Check out the fine print too. It's at:
http://www.keystoneballast.com/techdocs%5CKTEB-240-1-TP.pdf
If you just want the tubes to light up, fine. If you want them to operate
at manufacturer-rated values, then look further.
The ballast operates standard 4-foot F40T12 lamps at 75% of rated output,
but standard F32T8 lamps at 5% more than the rated value.
TKM