On 11/15/2012 6:02 PM, (PeteCresswell) wrote:
> I tried this in misc.rural, and got a recommendation to try it
> here.
> -------------------------------------------------------------
> Been quite awhile since I started wondering what it was with the
> "Building Wiring Fault" lights on my UPS'.
>
> In doing some homework prior to getting a generator transfer
> switch installed, it became apparent that houses need tb
> "Grounded" - and the typical ground is one or more copper rods
> pounded into the ground and then attached to a (neutral?) wire in
> the breaker panel.
I assume this is the US, and there is an electrical code that is
substantially the same as the National Electrical Code.
There are several major elements to the building "ground" system.
One is a bond between the neutral and service panel enclosure. The
enclosure is the basic system "ground". The bond may be a visible strap.
It can be a screw that just looks like a mounting screw for the neutral
bar. This bonding is critical for tripping breakers when there is a
short from, for instance, the hot wire in a drill to the metal drill
case that is connected to the ground pin at a grounded receptacle.
Another element is one or more earthing electrodes. They are not for
tripping breakers. They keep the building "ground" at approximately
earth potential, and keep the hot and neutral wires at a reasonable
potential with respect to earth.
The third element is grounding conductors that go with the branch
circuit and connect to the ground terminal on receptacles. The grounding
conductor can be a bare or green wire, or it can be the metal of the
wiring system.
I would understand "building wiring fault" to mean that there is no
branch circuit grounding conductor or there is no neutral-ground bond at
the panel. The UPS has no way of telling if the building "ground" is
earthed.
>
> This house is a split-level, crawl space but no basement, built
> in the fifties and I am unable to find anything that even looks
> like a ground.
>
> One reason for no ground might be what the house is built on: a
> shale ridge. The builder scooped a notch out of a hillside,
> sold the topsoil, and built this house on the notch. Go down
> about 4", and you hit shale that is so solid that you need an air
> hammer or a breaker bar and lots of time to get through - as in 3
> days with a breaker bar and a tin cup to make 2 4" wide 28" deep
> holes for a boat rack I put in last year.
>
> Realistically, we've been in this house for 30+ years and never
> lost an appliance to electrical surge... but still... there's got
> tb good reasons for grounding.
>
> That being said, I'm exploring after-the-fact methods.
>
> The obvious is the copper pipe that water comes in on: buried
> several feet deep and running a good 30' to the main under the
> street. Seems like this was SOP until some time in recent
> history when it was deemed inadequate.
In the 50s the water pipe would have been entirely adequate as an
earthing electrode. A metal water service pipe and metal municipal water
system is still the best earthing electrode you will find at a house.
Relatively recently a "supplemental" electrode has been required because
the metal water service pipe can be replace by plastic in the future.
The the N-G bonded service bar should have been connected to your water
pipe (#6 wire is usually used for 100A services), and a bonding wire
should have been connected across the water meter. The code now wants
the wire from the panel to connect within 5 feet of where the water pipe
enters the house. This will be your best earthing electrode.
>
> The second thing that comes up is a "Ufer" ground wherein the
> ground wire is tied to rebar in the house's foundation. I can
> find a lot of articles on the techniques of doing this in new
> construction, but nothing about retrofits.
This is the next best earthing electrode, but is only practical to add
before the foundation is poured.
>
> The third approach seems tb lateral: long trenches in the yard
> with the grounding medium layed in the trench. Seems
> impractical to me bc the standard calls for 30" deep...
>
> Has anybody been here: retrofitting a ground system to a house
> built on shale or rock?
Ground rods can be driven at an angle or even installed flat. Ground
rods are about the worst electrode.
Ask the electrical inspector what they would recommend.