> > On Tue, 21 Aug 2012 16:17:35 -0700 (PDT),
recyclebin...@gmail.com
>
> > wrote:
>
> > >> so the one side of the a-coil is laying in the pan??
>
> > >No only the foot of the A is. I did say �the letter A turned exactly 90 degrees� NOT 135 degrees.
>
> > If you want help, you're going to have to talk nicer to these people.
>
> > Two of your four posts so far have a measure of sarcasm. Above, it's
>
> > not necessary to prove you said it right the first time, nor to go
>
> > into numeric detail when you try to do so.
>
> > Does the AC function as expected? Or do you think there is a problem
>
> > related to the air coming to the A from the top versus the bottom.
>
> > I'll admit that that is not the same as bloging in one end of a straw
>
> > versus blowing in the other end, but in general I don't see why it
>
> > should matter.
>
> > Even if someone with experience here said, " I think it's better if
>
> > the air comes in through the bottom of the A", I don't think that's
>
> > enough to warrant charging a customer to turn the evaporator around,
>
> > even if it were easy, and even you think it will be hard.
>
> > Look at their webpages, and if that doesn't answer your questoin, call
>
> > the manufacturer of the A-frame and ask a tech if it matters which way
>
> > t he air goes.
>
> > Is the AC newsgroup still around?
>
> The problem was that the evaporator was freezing over. It may have been because most of the registers were closed. It remains to be seen if it was due to that or some other reason.
Good grief. Of course if you close off most of the
registers there is a good chance you're going to
freeze the coils. Surely that will do more to reduce
the airflow than the air flowing through the coil
backwards. Also, if it were the coil orientation, how
long has it been installed? If the coil has been there
for a substantial time and this problem is new, it
would suggest that it's not the coil orientation.
The units I've seen, I have never seen a coil
installed that way though. Very likely it was installed
wrong. Did you google for the install manual?
I will be waiting to hear from my client. It seems to me however that
in its present configuration the top leg of the A blows the condensate
on to the bottom leg and would cause a restriction in the air flow and
to eventually cause it to freeze over.
I would think it would take a hell of a lot of condensate
for the condensate to significantly reduce the airflow.
Likely more than the unit could produce. It's not like
water is coming out at 1 GPM.