I'm interested in when it is allowed (NEC) and advisable to make a
connection in an electrical box of a wire to a screw terminal by
looping the wire around and then using the free end for another
connection. Here's what I think I know:
1) It is NOT allowed to do this with the hot or neutral conductors and
the screw terminals on a device. Use pigtails.
2) It is allowed to do this with the EGC and the grounding screw of a
metal box or strap. This is a good idea, because it makes a
neater, tighter installation.
So I think this only leaves the case of the EGC and the ground screw
on a device. Is looping allowed here? Is it a good idea?
Thanks,
Wayne
P.S. FWIW I'm just contemplating my three gang switch box and how to
handle the 8 grounds (5 cables and 3 screw terminals). One option
would be loop a ground around each of the 3 devices, and use a wire
nut on the 5 ground wires. Another is to use 3 pigtails; joining the
8 ground wires would require splitting them into two groups and using
two wire nuts with a jumper between them.
My electrician seems to love looping the hot wire from one switch to
another in a 2-gang box.
Is this fully against code or just not advisable?
Could someone please explain to me then what is "illegal"
about the "looping" that the OP is talking about?
> Could someone please explain to me then what is "illegal" about the
> "looping" that the OP is talking about?
Maybe it isn't, maybe it is just considered a questionable practice by
some (including some inspectors?).
Wayne (the OP)
1) It is not advisable to do this with an insulated conductor,
although I'm not too clear on the reasoning. One thing that is clear
to me is that if this is done, the requisite 6" of conductor should be
left before the first looped connection.
2) It is advisable to do this with the EGC and the grounding screw of
a metal box or strap, because it makes a neater, tighter installation.
So that still leaves me with the question of whether it is a good idea
to do this with the EGC and the ground screw on a device.
Specifically, for a light switch, I'm considering looping the EGC of
the cable with the outbound switched hot around the ground screw of
the switch that serves it. What's the downside?
Thanks, Wayne
I have switches like this, a single hot comes in, and it daisey
chained from one switch to another without ever being cut. It is the
ONLY time I have found a terminal screw used in my house. Everything
else is BACK STABBED. :(
later,
tom
Could be a 2002 110.3(b) violation. I just checked the instructions
on a box of NM-B and found it says to make connections at the end.
With some inspectors(I've heard of), that's is more than enough to
fail an inspection
hth,
tom
Could you elaborate on what that section covers? Does it deal
specifically with NM cable?
With conduit installations it's commonplace when running wires from box
to box to simply leave a loop in each box and cut off some insulation
from the loop and hook it around the screw terminal.
>The Real Tom wrote:
>>
>> Could be a 2002 110.3(b) violation. I just checked the instructions
>> on a box of NM-B and found it says to make connections at the end.
>
>Could you elaborate on what that section covers? Does it deal
>specifically with NM cable?
>
Any NEC quotes are summaries, please read the code for yourself:
No, it's a general instruction: "Installation and Use of Equipment".
You need to follow the manufacturer's instruction. If the manufacture
says to only connect at the ends of insulated conductors, then you
need to do so.
>With conduit installations it's commonplace when running wires from box
>to box to simply leave a loop in each box and cut off some insulation
>from the loop and hook it around the screw terminal.
Can't say it's too common. Simple since other people I run into, and
how I was taught, you cut, pigtail, and wirenut. If you are using a
greenie, then just cut, and wirenut. Now with the free end goes to
the ground screw.
The knawing of insulation in the middle of the wire run seemed to look
lazy/unprofessional, so I'm guessing an inspector can hit you as a
2002 NEC 110.12 violation. :(
Remeber i'm still learning, so I listen to what hapens to other
electricians and take note.
later,
tom
>
>later,
>
>tom
Maybe naive question, but does "back stabbed" imply some particular
kind of wiring (defect?), and if so, what is that?
Thanks,
David
>
> Maybe naive question, but does "back stabbed" imply some particular
> kind of wiring (defect?), and if so, what is that?
Many residential grade (cheap) wiring devices have holes where a 14
gauge solid wire can be "stabbed" in and a spring clamp will hold it in
place. It's a labor saving feature that can result in intermittent
connections.
"back stabbing" is what I call when you strip the wire and push
through the tiny holes in the back of a device(switch, receptacle,
etc) that only uses spring pressure to hold onto the wire. So all you
do is stab it into the hole.
This is different from what I call 'back wiring' where you insert the
wire into the back, under a pressure plate and tighten a screw.
hth,
tom
>
>Thanks,
>
>David
technical term for arcing and flickering of lights, applances, etc....
thx,
tom
> "back stabbing" is what I call when you strip the wire and push
> through the tiny holes in the back of a device(switch, receptacle,
> etc) that only uses spring pressure to hold onto the wire. So all you
> do is stab it into the hole.
Scary things those.
> This is different from what I call 'back wiring' where you insert the
> wire into the back, under a pressure plate and tighten a screw.
Backwiring was described to me as the act of bending the ground
wire back over the cable sheath, and using the box clamp to "make
the ground" connection.
Ick.
--
Chris Lewis, Una confibula non set est
It's not just anyone who gets a Starship Cruiser class named after them.
Intermittents created by back stab connections do not
adversely affect lights. But they can be catastrophic to
computer data. Notice the difference. Back stabbing is just
fine from the perspective of human safety. But a disaster for
data safety. Perspective.
David Combs wrote:
> In article <hlqb3159jsslsm77q...@4ax.com>,
> The Real Tom <Tom @ www.WorkAtHomePlans.com> wrote:
>> I have switches like this, a single hot comes in, and it daisey
>> chained from one switch to another without ever being cut. It is the
>> ONLY time I have found a terminal screw used in my house. Everything
>> else is BACK STABBED. :(
>