How much does a chimney weigh?

379 views
Skip to first unread message

Jim Elbrecht

unread,
Jan 24, 2008, 11:42:47 AM1/24/08
to
20x20 inches, 25 feet tall.
Originally 8" liner with red brick.
Lined with 6" stainless set in place with a mortar of vermiculite.

And then- once I know how much it weighs- if I was to brace it with a
support set at a 25degree angle, how strong a support do I need? Steel
or wood?

Really long story- shortened; It has sat on a 8 foot high pillar of
clay about 3x3 in my basement for 20 years. I want to remove the
clay one side at a time and pour a 4x4 footing and a 2foot column. The
'temporary' bracing that was put in when the job was done will have to
be removed to dig the footing.

To dig the first 1/2 I won't need to disturb 2 sides of the base- and
I know it is tied to a slab that will be undisturbed. The support
will be an extra safety- hopefully not needed.

thanks-
Jim

ransley

unread,
Jan 24, 2008, 12:18:35 PM1/24/08
to

If you remove half the clay what is to stop it from falling straight
down as you try to place the support. My chimney is like that and
decided the dirt stays on a basement renovation, I dought you could do
it without at least major damage as it could shift downward. Is that a
4" x4" footing, thats not enough. If you removed brick through it and
got a big steel beam on jacks on big footers it might work. It sounds
risky anyway you do it.

Jim Elbrecht

unread,
Jan 24, 2008, 12:28:13 PM1/24/08
to
ransley <Mark_R...@yahoo.com> wrote:

>On Jan 24, 10:42 am, Jim Elbrecht <elbre...@email.com> wrote:

>> 'temporary' bracing that was put in when the job was done will have to
>> be removed to dig the footing.  
>>
>> To dig the first 1/2 I won't need to disturb 2 sides of the base- and
>> I know it is tied to a slab that will be undisturbed.    The support
>> will be an extra safety- hopefully not needed.

-snip-


>If you remove half the clay what is to stop it from falling straight
>down as you try to place the support.

Brace first, dig second. I *think* that 1/2 the clay will hold
it--- but I want to provide a brace that will take the whole load in
the case of major catastrophe.

>My chimney is like that and
>decided the dirt stays on a basement renovation, I dought you could do
>it without at least major damage as it could shift downward. Is that a
>4" x4" footing, thats not enough.

The footing that will eventually be under the new concrete column will
be 4 feet square and 12" thick reinforced concrete. It will be
poured in two pours and tied together with re-rod.

> If you removed brick through it and
>got a big steel beam on jacks on big footers it might work. It sounds
>risky anyway you do it.

I don't doubt the risk. As long as I can keep it off my head, the
house is repairable. But I'm pretty cautious- that's why I'm trying
to get a real-world feel for how big the bracing has to be to do any
good.

Jim

dpb

unread,
Jan 24, 2008, 1:29:24 PM1/24/08
to
Jim Elbrecht wrote:
> 20x20 inches, 25 feet tall.
> Originally 8" liner with red brick.
> Lined with 6" stainless set in place with a mortar of vermiculite.
>
> And then- once I know how much it weighs- if I was to brace it with a
> support set at a 25degree angle, how strong a support do I need? Steel
> or wood?
>
Brick/mortar -- 120-150 lb/cu-ft
SS -- 490

Need more dimension, geometry to figure out the actual (for instance,
was the first liner removed or is the liner inside it), but you know
that. Estimate volume, then weight is straightforward.

This would be good place for an engineer's help imo...

--

Mike Dobony

unread,
Jan 24, 2008, 1:43:13 PM1/24/08
to


This sounds like a job for a foundation repair professional.

Joe

unread,
Jan 24, 2008, 3:35:28 PM1/24/08
to
On Jan 24, 10:42 am, Jim Elbrecht <elbre...@email.com> wrote:

Joe

unread,
Jan 24, 2008, 3:52:56 PM1/24/08
to
On Jan 24, 10:42 am, Jim Elbrecht <elbre...@email.com> wrote:

Pretty scary IMO. We had that situation in our palace and since the
chimney was nothing sacred, it was simply removed brick by brick from
the top and replaced by a nice tidy Metalbestos assembly. Part of the
chimney,in addition, was a house support, so that was left intact
under the first floor.and in the basement. Eventually it was also
removed, a big footing and lally column installed. Holding up the
house for the final removal was no big, deal, just a couple of post
jacks, 6 x 6 shoring, some steel plates from the scrap yard and a 20
ton el cheapo hydraulic jack did the job. Using a level on the floor
joists was a fringe benefit as some of the upstairs doors then decided
to fit properly. Old houses are such fun.

Joe

HeyBub

unread,
Jan 24, 2008, 5:07:53 PM1/24/08
to

Common red brick weighs 120lbs/cu ft. You've got 20"(1.7 ft) x 20" x 25' =
1.7x1.7x25 = 71 cu ft of chimney. That, times 120, is about 8500 lbs.

'Course that's for a stack of red bricks. Given that the stack's hollow, the
total might be a bit less.


hal...@aol.com

unread,
Jan 24, 2008, 5:34:02 PM1/24/08
to
> total might be a bit less.- Hide quoted text -
>
> - Show quoted text -

remove chimney starting at roof, replace furnace and hot water tank
with direct vent unit, gain some interior floor space and remove a
roof maintence item

Don Young

unread,
Jan 24, 2008, 9:52:48 PM1/24/08
to

"Jim Elbrecht" <elbr...@email.com> wrote in message
news:d5fhp3d6mmvboudja...@4ax.com...
In addition to the other suggestions, if you decide to do this yourself I
would suggest that instead of removing half of the support you remove only
one fourth at a time. It seems to me that removing half of the support would
be fairly likely to cause failure of the structure and/or the support
itself.

Don Young


ransley

unread,
Jan 24, 2008, 10:45:28 PM1/24/08
to
On Jan 24, 8:52 pm, "Don Young" <no...@nonesuch.com> wrote:
> "Jim Elbrecht" <elbre...@email.com> wrote in message
> Don Young- Hide quoted text -

>
> - Show quoted text -

Does your insurance cover you as a HO screw up or does it need a
contract of a real hack-pro, You might be suprised after it causes
50,000.00 in damage as to who pays. ITS YOU

Message has been deleted

Jim Elbrecht

unread,
Jan 25, 2008, 2:15:05 PM1/25/08
to
"HeyBub" <hey...@gmail.com> wrote:

-snip-


>Common red brick weighs 120lbs/cu ft. You've got 20"(1.7 ft) x 20" x 25' =
>1.7x1.7x25 = 71 cu ft of chimney. That, times 120, is about 8500 lbs.
>
>'Course that's for a stack of red bricks. Given that the stack's hollow, the
>total might be a bit less.

Thanks- I figured someone would have the numbers in their head-- I'm
feeling a lot better about my lolly column rated at 18000pounds.
Jim

HeyBub

unread,
Jan 25, 2008, 2:25:13 PM1/25/08
to

Actually, I didn't. I Googled "Density+red+brick" and got:

http://www.simetric.co.uk/si_materials.htm

among others.