replying to millinghill , Brett wrote:
Hello Theodore,
I am a licensed electrician in Massachusetts, Rhode Island and New
Hampshire.
Typically it is easier to run your wire overhead and come down to each
electrical box.
If you are using solid foam insulation, cut out a piece 1 inch wide from
above, to the box.
Turn that piece sideways and cut away enough foam to allow room for your
non metallic sheathed cable (Romex).
Run your wire down to the box and back up and over to the next box.
National electric code requires a Romex staple over the wire typically
within 8 inches from where it leaves the box, on the same stud that the
box is mounted upon.
Replace the foam over the wire.
Now you can install gypsum board wall or the plastic interlocking panels
used in basements.
Code requires arc fault protection for receptacles.
If you have more than 3 receptacles an arc fault circuit breaker is more
cost effective.
Code requires ground fault protection on receptacles in an unfinished
basement.
A combination arc fault/ ground fault circuit breaker can be installed to
cover your entire basement.
Electric code is written by the national fire protection agency.
It is a minimum standard for electrical installations to prevent fires or
deaths.
the suggested circuit breakers will comply with the code if sized
correctly to the size of the wire you are using.
American wire gauge # 12 for a 20 amp circuit breaker.
I know this may have been too much information, but now you have enough to
do a correct and safe installation.
--