Well, it sure as hell hasn't done that. This unit doesn't recognize a
change in the room temperature until it's changed by at least three
degrees. That means it gets very cold before the furnace kicks on. It
stays on for a long time - sometimes twenty minutes or more, then goes
off for as long as an hour. It's four degrees outside right now and
the furnace came on once in the past hour. When it does go on and off
it "thinks" that the inside temp has changed by one degree when in fact
the swing is about five degrees.
The guy who installed it agrees there is a big problem but he is having
trouble convincing Carrier.
Does anyone else have a similar problem with this new model? It's very
frustrating considering the little sucker cost about $400.
Thanks
Jane
You need to call the installer back out and have him calibrate the
thermostat. Sounds like they forgot something in the set up program...
Or..it could just be that someone else if finding out why some of us hate
Totaline...
LOL
Watchit.......
;-].
googlem...@yahoo.com wrote:
Yes it has a problem. If all is set up and operating correctly your room
temp (measured at the user interface or remote sensor, will remain
fairly constant.) Does this happen to be a zoned system?
hvacrmedic
My installer is going to have someone from Carrier come. He's
convinced there's a bug in the thermostat. All I know is we are
miserable.
googlem...@yahoo.com wrote:
> No it is only one zone.
In that case the first order of business is to recheck
connections--color coding (G,Y,W,R), tightness, etc. It's characteristic
of the terminal strip in this furnace to have screws that are difficult
to turn. This can lead to a tech or installer believing that the
connection is tight when it isn't. I have encountered this problem more
than once. It's a pin connector as well and may not be seated onto the
pins all the way. Have them check the screw connections by pulling on
the wires *individually*. Beyond that it could be a system fault, which
should be easy to diagnose since the t-stat data-logs all faults, even
runtime history, for easy retrieval. It could simply have the db set to
high in the setup menu.
hvacrmedic
Give us an update once they correct the problem.
Once you get it working properly, you will like it....
The problem is the room temp on the thermostat is wrong by about three
degrees. The temp in the room has to go down or up two or three
degrees before the thermostat sees any change in the temp and reacts.
Would the "db" have an affect on the thermostats temp sensor?
By the way - the installer came and put in a new thermostat and it did
the same thing. He also said he had two other customers with the same
problem. He thinks it's a problem with the thermostat. I think it's a
problem with the setup.
What do you think?
VS DC is variable speed direct current, you have it. Learn about it.
96% efficient no, I bet yours is only 94-94.5% efficient, just BS
marketing as I expalined
googlem...@yahoo.com wrote:
> What is the "db"?
Deadband, the temp swing, if you will, between off and on.
>
> The problem is the room temp on the thermostat is wrong by about three
> degrees. The temp in the room has to go down or up two or three
> degrees before the thermostat sees any change in the temp and reacts.
>
> Would the "db" have an affect on the thermostats temp sensor?
It might appear to, but no. If db is set too high it will cause
variations from the set point by up to the amount of db set.
>
> By the way - the installer came and put in a new thermostat and it did
> the same thing.
That should be a valuable clue.
> He also said he had two other customers with the same
> problem. He thinks it's a problem with the thermostat. I think it's a
> problem with the setup.
Unfortunately I can't see it from here.
>
> What do you think?
I can't diagnose it from here based upon the minimal info that you've
given, sorry. Contact Carrier yourself if you have to. The fact that he
has other customers with the same problem indicates that he's either
installing and/or setting up the systems incorrectly. The only settings
on the controller that would cause this would be the db, already covered.
If the temperature offset adjustment (a different setting mentioned
elsewhere in the thread) were off by a few degrees this wouldn't result
in the setpoint reading on the stat being off from the actual room temp
reading on the stat.
It really sounds as though your unit is simply malfunctioning, e.g.
misfiring, locking out, etc, and simply not getting the area around the
stat up to the setpoint temp. This could be caused by several different
installation errors involving combustion piping or indoor airflow
issues. The blower speed setting may also be set incorrectly. There
could be a restriction in the ductwork. The vent pipes may be too small
in diameter or not sloped properly. The list really does go on and on.
Best bet is to get another company out, or else get the current company
to go through the installation guide page by page checking the
instructions there against the actual install. If the manual is over
their head then that could also account for several install issues, and
unfortunately this isn't unusual in the real world.
hvacrmedic
http://www.xpedio.carrier.com/idc/groups/public/documents/techlit/uid01-1si.pdf
We have noticed some improvement by setting the fan speed to low, but
the actual room temp stills varies by two or three degrees without the
change being recognized by the thermostat. Very frustrating.
Thanks for trying to help. I really appreciate it.
Jane
googlem...@yahoo.com wrote:
Well the deadband and differential are sometimes reversed in their
definitions depending upon whoever wrote the manual. My last Carrier
stat install had deadband as the on/off swing and differential as the
difference between heat and cool settings. But this is all beside the
point. The on/off swing setting, regardless of what this is called on
your stat, is the only t-stat setting that could cause what you are
seeing,as settings go. A fault with the t-stat is a highly remote
possibility, but you may have gotten that one of those 1 out of umteen
faulty ones. But like I said, this is going to be impossible to diagnose
over the intenet because there are too many parameters on your
particular unit that require manual testing and/or checking. Good luck
resolving this, and remember that you are free to contact Carrier
yourself, they won't mind, and will even be happy to take your calls and
or e-mails.
hvacrmedic
We are thinking about getting a remote room sensor so that the
thermostat can react to the temp in the living room and not in the
dining room. Do you know if the remote sensor can be easily
deactivated so the furnace and/or air conditioner responds to the
thermostat sensor if we want it to?
Anyway, things are much better. Thanks all for your help.
Not sure if anyone brought it up or not, but:
What is the wall like where the thermostat (interface) is mounted? If the
installer left a good size hole (behind the thermostat) and you have a
"draft" coming through it, that can really have an affect (or is that
Effect?) on the operation.
Just a thought...
Good thought though.
Inside walls will get drafts too, but enough of that....;-]
You know how they sell "gaskets" to put behind faceplates for switches and
outlets in your house? That's kind of the same idea. Even a "figer-size"
hole can let enough of a draft in to mess with the thermostat. The only
thing is, if it didn't affect the old one, I don't see how it could now.