On Jan 14, 11:22 am, bud-- <
remove.budn...@isp.com> wrote:
> On 1/14/2013 9:31 AM,
trad...@optonline.net wrote:
>
>
>
>
>
> > In a current thread, gfretw told a poster that one
> > way to indentify 3 phase service is if it's connected
> > to two or three transformers. That brought back a
> > question that has stumped me for a very long time.
>
> > I know that it's possible to get 3 phase service with
> > just two transformers. Apparently that is used for cost
> > savings on lighter 3 phase loads. But what I don't
> > understand is how you can get true 3 phase with only
> > TWO transformers. Coming down the road you
> > have 3 high voltage lines. Each of those has an AC
> > waveform and each is 120deg off in phase from the
> > other. If you have three step-down transformers,
> > then you have one transformer connected to each
> > high voltage line and obviously you get 3 waveforms
> > out that have the same 120deg phase relation as
> > those on the high voltage side.
>
> > But how do you get 3 waveforms at 120deg shift
> > relative to each other with only two transformers
> > connected to only two of the 3 high voltage lines?
>
> Would be a lot easier to explain with a pencil and piece of paper.
>
> The usual delta connection has a 120/240V transformer, and then adds
> 3-phase to that. A diagram is about halfway downhttp://
en.wikipedia.org/wiki/Three-phase_electric_power
> where the transformers are connected in a triangle.
>
> L1-N-L2 is a single phase 120/240V Edison circuit. Two transformers add
> L3 - L1-L2-L3 is 3 phase 240V. The voltage from N-L3 is 208V and is
> called the "high" leg (or several other names). This is "high-leg delta".
>
> But it still works if the L1-L3 transformer is not used. It is then
> called open delta and only uses 2 transformers. This used to be
> moderately common and is still around. It is probably not used for
> anything new. It is pretty easy to identify because of 2 utility
> transformers, only one of which has a secondary neutral connection.
>
> =======================================
> For a wye connection, a Scott (or T) transformer connection can be used.
> See the diagram about halfway down labeled "Scott T transformer 3ph to 3 ph"
http://en.wikipedia.org/wiki/Scott-T_transformer
> X1-X2-X3 are 3-phase with X0 being the neutral. This gives a wye
> 3-phase. A rather common use would be 480V 3-phase connected to H1-H2-H3
> and 277/120V coming out X1-X2-X3-X0.
>
> This is used on some relatively small "dry" transformers in buildings
> with a 480V service. The advantage is you have 3 phase with only 2
> transformers. The disadvantage is you screw up the power factor on both
> transformers and have to derate them to 87% (if I remember right). (And
> if I remember right, the delta transformers above also have to be
> derated for the 3-phase power.)
>
> I don't think utilities ever use this connection.
>
> The transformers actually run at real 2-phase at 90 degrees. You can use
> a Scott connection to actually use the 2-phase.- Hide quoted text -
>
> - Show quoted text -
But the question is, when using only two transformers
tied into two of the 3 phases, what generates the missing third phase
that is 120deg away from the other two? Does a special transformer
give the phase shift? A typical
transformer that you would use in a 3 phase installation
using 3 transformers, tied to all 3 high voltage phases
gives outputs that are not phase shifted, or at least by
only a little, right?