The 80% rule and how it is applied to circuits.

272 views
Skip to first unread message

gfre...@aol.com

unread,
Jan 10, 2017, 11:23:00 PM1/10/17
to
There seems to be a lot of confusion, urban legend and simply false
information floating around.
OK let's start in article 210.19(A)(1)
"General. Branch-circuit conductors shall have an ampacity not less
than the maximum load to be served. Where a branch circuit supplies
continuous loads or any combination of continuous and noncontinuous
loads, the minimum branch-circuit conductor size, before the
application of any adjustment or correction factors, shall have an
allowable ampacity not less than the noncontinuous load plus 125
percent of the continuous load."

Ampacity is defined in article 100 as "The current, in amperes, that a
conductor can carry continuously under the conditions of use without
exceeding its temperature rating".

Notice this says "conductors". Overcurrent protection (breakers or
fuses) are not mentioned.

Now lets go look at the common conductors used on circuits used for
general lighting, 12ga and 14ga.
If I look an article 315, I see a 14ga conductor is 20a and a 12 ga
conductor is 25a (in the 60c column, the strictest category).
OK so where does the 20a and 15a standard come from?
That is in 240.4(D) where they tell you what breakers size you should
use on "small conductors". With a few exceptions mostly where motors
or welders are involved, you have that limit we know and love.
Since the installer has no control over what a user will plug in, they
build that 80% safety factor into the maximum breaker allowed.

I have never seen that mythical "80% breaker" but I would be willing
to look at a catalog that lists one. I am not sure why that would even
exist since the NEC.

There are a lot of other rules about specific circumstances, motor
loads, ambient temperatures etc but generally they will apply in
industrial applications. Where the homeowner will usually see that is
the conductors going to their A/C compressor. Uninformed home
inspectors will write up a perfectly legal installation because the
breaker does not seem to match the wire they used and they do not
understand the label on the unit. They will be wildly wrong if they
also try to apply "the 80% rule" to the breaker when the real rule is
as much 250%.

Light your torches and flame away ;-)

trader_4

unread,
Jan 11, 2017, 9:54:39 AM1/11/17
to
It appears that the typical breakers we buy every day are the 80% rated
ones. I think I figured this out as I posted yesterday in the other
thread. I think I just confirmed it with this:

http://static.schneider-electric.us/docs/Circuit%20Protection/0600DB0101.pdf

They explain that the rule you cited applies for our everyday breakers
which are rated for use subject to the 80%/125% rule for continuous loads.
However if you have a 100% rated breaker and panel, then you don't have
to apply the rule. In that case, with a 100% rated breaker and panel
you could have a 20 amp continuous load on a 20 amp breaker.

In the above link, they quote the following exception to the 125/80% rule:


“Exception: Where the assembly, including the overcurrent devices protecting the
branch circuit(s), is listed for operation at 100 percent of its rating, the ampere
rating of the overcurrent device shall be permitted to be not less than the sum of
the continuous load plus the non-continuous load.”


So, apparently there are these 100% rated breakers, but they are not what
we typically use everyday and they probably are not common or we'd see
them, see them marked that way, etc. But whether the breaker is 80%
or 100%, it will still only open at over 100%, ie a 20A breaker of either
type will carry a full 20A. It's a rating, listing, rule application thing.
That is my conclusion, anyway.


gfre...@aol.com

unread,
Jan 11, 2017, 11:38:25 AM1/11/17
to
As I stated in the other note when they say 100% they mean it will
handle rated current at 60c instead of the 40c that regular breakers
are rated at.
You notice all the references to enclosure size and ambient
temperatures.
The 80% rule does not apply to breakers, It applies to the conductors
and the breaker does not change that with the exception that in large
conductors, the terminal rating may be the limiting factor. THHN and
most modern conductors are actually rated 90c but there are few
devices with 90c terminals. You can still use the 90c column to derate
the conductor.
When you read the examples you also notice they all talk about the
"round up" rule which seldom applies to residential circuits and never
applies to small conductors in general lighting circuits.

trader_4

unread,
Jan 12, 2017, 10:06:22 AM1/12/17
to
Then why does Schneider say this:

“Exception No. 1: If the assembly, including the overcurrent devices protecting the
feeder(s), is listed for operation at 100 percent of its rating, the allowable ampacity
of the feeder conductors shall be permitted to be not less than the sum of the
continuous load plus the non-continuous load.”

In short, these article says that a standard-rated circuit (circuit breaker and wire)
can carry 80% of the circuit breaker and conductor current rating. In contrast, 100%
rated circuits can carry 100% of the circuit breaker and conductor current rating."



Seems clear to me. The exception in NEC and Schneider are saying
that with a 100% rated breaker,
the circuit can use that breaker and you don't have to derate the
ampacity for continuous loads. Eg if you have a 20A, 80% breaker,
then that circuit is limited to a 16A continuous load. If you
have a 20A, 100% breaker, then it's OK to have up to 20A continuous
load. Isn't that what NEC and Schneider are saying?

gfre...@aol.com

unread,
Jan 12, 2017, 11:30:14 AM1/12/17
to
On Thu, 12 Jan 2017 07:06:16 -0800 (PST), trader_4
You also notice they say "feeder"?
I already showed you in that article that they say a "standard"
breaker can carry 100% of it's rating.
This still has to do with the terminals on the breaker which is
usually the limiting factor when you are using 90c conductors.
Find me a trip curve that shows a standard breaker tripping at less
than it's rating on that site.

trader_4

unread,
Jan 12, 2017, 1:56:09 PM1/12/17
to
No, I don't see where they say that in what I've quoted.


> I already showed you in that article that they say a "standard"
> breaker can carry 100% of it's rating.
> This still has to do with the terminals on the breaker which is
> usually the limiting factor when you are using 90c conductors.
> Find me a trip curve that shows a standard breaker tripping at less
> than it's rating on that site.

You keep going back to something that I'm not arguing. I've said
quite clearly that I agree that both an 80% breaker and a 100% breaker
will carry the full, 100%, current. According to Schnieder and what
I see elsewhere, the difference is that the 80% breaker has to have
the 125/80% de-rating rule applied for continuous loads, while the
100% breaker does not.

gfre...@aol.com

unread,
Jan 12, 2017, 2:19:24 PM1/12/17
to
On Thu, 12 Jan 2017 10:56:04 -0800 (PST), trader_4
Again, they are talking about feeders, not branch circuits and we are
talking about industrial sized breakers so it is really just an OT
curiosity here in Home Repair.

You win OK?

dpb

unread,
Jan 12, 2017, 2:39:06 PM1/12/17
to
On 01/12/2017 12:56 PM, trader_4 wrote:
> On Thursday, January 12, 2017 at 11:30:14 AM UTC-5, gfre...@aol.com wrote:
>> On Thu, 12 Jan 2017 07:06:16 -0800 (PST), trader_4
>> <tra...@optonline.net> wrote:
...

>>> Then why does Schneider say this:
>>>
>>> “Exception No. 1: If the assembly, including the overcurrent devices protecting the
>>> feeder(s), is listed for operation at 100 percent of its rating, the allowable ampacity
>>> of the feeder conductors shall be permitted to be not less than the sum of the
>>> continuous load plus the non-continuous load.”
...

>> You also notice they say "feeder"?
>
> No, I don't see where they say that in what I've quoted.
...

It's in the above...

"...the allowable ampacity of the FEEDER CONDUCTORS (emphasis added)
shall be permitted ..."

trader_4

unread,
Jan 12, 2017, 3:00:22 PM1/12/17
to
No, they are not talking about feeders. Schneider reference NEC 210.20
which covers *branch circuits*. 210.20 (a) says that you have to apply
the 125/80% rule to continuous loads.

210.20 (a)
Where a branch circuit supplies continuous loads or any combination of
continuous loads and non-continuous loads, the rating of the overcurrent
device shall not be less than the non-continuous load, plus 125% of the
continuous load.

Exception: Where the assembly, including the overcurrent device
protecting the branch circuit, is listed for operation at 100% of
it's rating, the ampere rating of the overcurrent device shall be
permitted to be not less than the sum of the continuous load plus
the non-continuous load.

I read that to mean that if you have a normal, 80% breaker, then per code,
the breaker is limited to a continuous load of 80% of what's stamped on
the handle. . But if you have a 100% rated breaker and panel, then it's
code compliant to the full value stamped on the handle. You raise a
good point as to what size these 100% breakers come in, IDK and they may
not even exist for residential size circuits.

We are in agreement that a 20A breaker you buy at HD, while it's not
the special 100% rated type, will carry the full 20A circuit load.
I said that at the beginning, when the other poster was saying that
a 20A breaker will normally trip at 16A.
It just has the 80% limitation applied with regard to being code for
continuous loads.

trader_4

unread,
Jan 12, 2017, 3:03:28 PM1/12/17
to
That is a totally different section of NEC code they are talking about.
Yes, they have a section where they talk about feeders, but they
also have a section where they specifically talk about 210.20 A
which is about *branch circuits*. THAT is the part I'm talking about
and referencing.

dpb

unread,
Jan 12, 2017, 3:33:41 PM1/12/17
to
On 01/12/2017 2:03 PM, trader_4 wrote:
...

> That is a totally different section of NEC code they are talking about.
> Yes, they have a section where they talk about feeders, but they
> also have a section where they specifically talk about 210.20 A
> which is about *branch circuits*. THAT is the part I'm talking about
> and referencing.

Whatever.

gfre...@aol.com

unread,
Jan 12, 2017, 4:49:54 PM1/12/17
to
The part you are missing is 210.20 refers to the breaker and the
enclosure assembly, not the conductors and the breaker is sized to the
conductor it protects.

trader_4

unread,
Jan 12, 2017, 5:05:03 PM1/12/17
to
I know it applies to the breaker and the enclosure. I never said
anything about sizing the conductors. Do you disagree that it says
that if you have a regular breaker on a branch circuit, then the
breaker has to be sized
to 125% of the continuous load, while if you have a 100% rated breaker,
then the breaker is sized to 100% of the continuous load, allowing
a smaller breaker?

gfre...@aol.com

unread,
Jan 12, 2017, 7:19:05 PM1/12/17
to
On Thu, 12 Jan 2017 14:04:59 -0800 (PST), trader_4
I would more properly say the conductors are sized to the load and the
breaker is sized to protect the conductor.
That is the way the NEC is laid out.

gfre...@aol.com

unread,
Jan 14, 2017, 9:20:08 PM1/14/17
to
On Thu, 12 Jan 2017 14:04:59 -0800 (PST), trader_4
Here is another guy from ECN explaining this


This is perhaps one of the most misunderstood aspects of circuit
breakers.

The so called "80% rule" is actually not stated anywhere in circuit
breaker listing and labeling rules. UL489, the standard for Molded
Case Circuit Breakers, requires that all MCCBs are tested at 100%
load.

YOU must size CONDUCTORS at 125% of the continuous load you are
feeding per the NEC. You then size the breakers for protecting those
CONDUCTORS. So INDIRECTLY the breaker will never carry more than 80%
of the load that you selected the conductors for. Ergo people refer to
them as being rated for 80%, but that's just because of the way the
NEC is worded.

You cannot use a 100% rated breaker unless you have also met all of
the conditions for the CONDUCTORS that allow you to size the CONDUCTOR
at 100% of the load. One of those conditions will end up being that
the conductors are rated for 90C. In order for you to use conductors
rated and sized for 90C, all components in the circuit must also be
rated for 90C. Lugs on standard circuit breakers are NOT rated for
90C, they are rated at best, 75C. So one thing you get when you buy a
100% rated breaker is that the lugs will be 90C (usually copper, not
Al). The other thing is that panelboards are NEVER rated for 90C
conductor use. So the only way to use a 100% rated breaker is to buy
it as a separately enclosed stand-alone breaker, or as an open breaker
that YOU will build into an assembly, such as a switchboard or MCC,
that you will have listed for use with 90C rated conductors at 100%
load.

So for example where you see this done most often is that the MAIN
breaker in a switchboard or MCC is selected to be rated 100%, because
the load side of that breaker is going to bolt directly to the bus
bar, not cables, so that connection can be rated for 90C. The incoming
cables to that breaker can then be sized, selected and rated based on
100% load as well.

But if you have a breaker in a panelboard and you think you can simply
upgrade it to 100% rated to get more current out of it, you are going
to be disappointed because you will find that the 100% rated breaker
cannot be used that way.



Dean Hoffman

unread,
Jan 14, 2017, 9:51:49 PM1/14/17
to
On 1/14/17 8:19 PM, gfre...@aol.com wrote:

>
> You cannot use a 100% rated breaker unless you have also met all of
> the conditions for the CONDUCTORS that allow you to size the CONDUCTOR
> at 100% of the load. One of those conditions will end up being that
> the conductors are rated for 90C. In order for you to use conductors
> rated and sized for 90C, all components in the circuit must also be
> rated for 90C. Lugs on standard circuit breakers are NOT rated for
> 90C, they are rated at best, 75C. So one thing you get when you buy a
> 100% rated breaker is that the lugs will be 90C (usually copper, not
> Al). The other thing is that panelboards are NEVER rated for 90C
> conductor use. So the only way to use a 100% rated breaker is to buy
> it as a separately enclosed stand-alone breaker, or as an open breaker
> that YOU will build into an assembly, such as a switchboard or MCC,
> that you will have listed for use with 90C rated conductors at 100%
> load.

Isn't there a provision requiring engineering supervision if
one builds more than
two components into a panel?

gfre...@aol.com

unread,
Jan 14, 2017, 11:11:59 PM1/14/17
to
-

If you are not using a listed assembly it is up to the AHJ what they
will live with. There are a number of things in the NEC where they
specify engineering supervision tho.

trader_4

unread,
Jan 16, 2017, 1:44:54 PM1/16/17
to
Didn't see this until today. I agree with what's there, and see your
point, that in addition to the circuit breaker and the enclosure having
to be 100% rated, the conductors would have to be too. So, in a practical
sense, with residential circuits, you probably never see these 100% special
breakers, because they don't exist for the typical residential size panel.
The ones we use every day are the 80% ones. Which, again,
doesn't mean that they will open at anything over 80% of the load on the
handle, which is what the other poster claimed. It only means that the 125%
rule has to be applied for continuous loads when using that breaker.
And as you point out, the conductors have to be sized for the continuous
load too.

gfre...@aol.com

unread,
Jan 16, 2017, 2:55:52 PM1/16/17
to
On Mon, 16 Jan 2017 10:44:49 -0800 (PST), trader_4
You actually size the conductor to the load and then size the breaker
to protect the conductor.
Since 240.4(D) ends up being the limitation for breakers on "small
conductors" virtually all of them only have 60c rated lugs so the 80
vs 100% breaker thing is totally unrelated to anything you will ever
see in a home. They never have 90c rated lugs (not even the main).

This is an example of the typical breakers you will see in residential
panels.
http://gfretwell.com/electrical/breakers.jpg