On Thu, 12 Jan 2017 14:04:59 -0800 (PST), trader_4
Here is another guy from ECN explaining this
This is perhaps one of the most misunderstood aspects of circuit
breakers.
The so called "80% rule" is actually not stated anywhere in circuit
breaker listing and labeling rules. UL489, the standard for Molded
Case Circuit Breakers, requires that all MCCBs are tested at 100%
load.
YOU must size CONDUCTORS at 125% of the continuous load you are
feeding per the NEC. You then size the breakers for protecting those
CONDUCTORS. So INDIRECTLY the breaker will never carry more than 80%
of the load that you selected the conductors for. Ergo people refer to
them as being rated for 80%, but that's just because of the way the
NEC is worded.
You cannot use a 100% rated breaker unless you have also met all of
the conditions for the CONDUCTORS that allow you to size the CONDUCTOR
at 100% of the load. One of those conditions will end up being that
the conductors are rated for 90C. In order for you to use conductors
rated and sized for 90C, all components in the circuit must also be
rated for 90C. Lugs on standard circuit breakers are NOT rated for
90C, they are rated at best, 75C. So one thing you get when you buy a
100% rated breaker is that the lugs will be 90C (usually copper, not
Al). The other thing is that panelboards are NEVER rated for 90C
conductor use. So the only way to use a 100% rated breaker is to buy
it as a separately enclosed stand-alone breaker, or as an open breaker
that YOU will build into an assembly, such as a switchboard or MCC,
that you will have listed for use with 90C rated conductors at 100%
load.
So for example where you see this done most often is that the MAIN
breaker in a switchboard or MCC is selected to be rated 100%, because
the load side of that breaker is going to bolt directly to the bus
bar, not cables, so that connection can be rated for 90C. The incoming
cables to that breaker can then be sized, selected and rated based on
100% load as well.
But if you have a breaker in a panelboard and you think you can simply
upgrade it to 100% rated to get more current out of it, you are going
to be disappointed because you will find that the 100% rated breaker
cannot be used that way.