Thanks,
Ron Brown
Heat detectors are not used for recall because their response is too slow. They
are generally used in sprinklered shafts to initiate a shunt trip and disconnect
electrical power before the sprinkler head opens.
Hope this helps,
Mark LoCoco
Qubic Technology
I recommend that you use Rate Compensated or Fixed temp heat detectors in the
parking garage, above car's and such. Smoke detectors in the elevator lobby
and top of shaft. By using aux contacts on the fire alarm zone and mother
board will supply you with general recall and alt floor recall. You do not
want to use smoke detectors in the open parking area ( Due to the combustion
of car engines). Smoke detectors are used for life safety ( Office
buildings, dorm rooms, hospitals etc.) heat detectors are used for property
protection. Hope this helps
Mathieu
In article <7fis09$jej$1...@list.umaryland.edu>,
rbr...@fm.umaryland.edu (R Brown) wrote:
>
> Anyone have an opinion on the use of smoke detectors in close proximity to
> parking spaces above or below grade for use in elevator recall? Would a
> particular type of smoke or heat detector be better? I realize it is up to the
> AHJ, but was wondering how serious are the problems with false alarms and if
> ionization or photoelectric detectors would be more prone to false alarms.
>
> Thanks,
>
> Ron Brown
>