I have a 100 hp 3-phase 575-volt motor and a 480-volt supply. The motor
is poart of a hydraulic system to be shipped to Canada.
I don't have a satisfactory transformer arrangement at the moment and
don't really want to buy one.
The quesiton is, can I run the 100 hp 575 volt motor on my 480-volt
supply for testing under derated load conditions (at say 60HP)? The MCC
control transformer can easily be changed to operate the starter during
this test.
It sounds allright to me but I have never tried it.
What do y'all think.
Thanks
MJMcN.
--
gyro, 400 bandit, v-max, helix, diesel powered bmw r100-rt.
VW diesel wabbit, dodge D-350 cummins.
Fred G
mike.mcnaughton wrote in message <36C4E35...@sympatico.ca>...
1. Max load = approx 64%
2. Motor Torque drops to (460/575)squared per unit. (about 64%
3. Full load speed drops by 5-7%
4. % slip increases by 56%
Good luck. BTW 575v/480v transformers are standard products and can easily
be purchased (at least in Canada).
Steve Costello