> run wire between the studs under the sheet rock from a knock out of the
> subpanel up to the joist and down the wall under the rock where the
> charger will be, even though in some places it is acceptable to bore
> holes no more than a specific side in the studs to pass wire
> horizontally, I would wouldn't recommend it. If you do decide on
> this, use rigid with feed through stud supports that can be mounted.
>
> THe charger should have knock outs on the back panel inside for the
> power entrance. Most people in this case use a rung of romix. You
> simply surface mount the charger with the entrance poking through inside.
>
> I always thought a charger was an appliance and should have a
> rubber cord with cap to a surface or recessed receptacle.
> Jamie
The 100A circuit needed by the charger (the actual charger is in the vehicle
-- this is really just a connector to the structure's 240 ac mains) requires
3 awg copper wire (4 awg ground). Some kind of conduit required, probably
1.25 inch. Romex not an option.
Under the 'rock is difficult: water heater & furnace are between the panel
and the charge station proposed location. Enough clearance over the 'rock but
going "sub" requires much frustration, if possible.
What's a "feed through stud support"? (Googling this gets hits relating to
threaded electrical stud, not a 2x4...)
Still think that surface mount except for the last 18 inches then going "sub"
is the best option.
These cars are 85 KWh capacities. Think "SLA charger times 10."
Thanks.