HVDC line grounding system question

7 views
Skip to first unread message

Michael Moroney

unread,
Jan 3, 2021, 1:03:48 AMJan 3
to
There is a long HVDC power line from northern Quebec Canada to Ayer,
Massachusetts USA. It operates at either +/- 375 kV or +/- 450 kV
depending on source. As I understand it, it is grounded at exactly one
point, near Saint-Claude, Quebec. You can see it on this Google
satellite view: https://goo.gl/maps/bnsYcbv9Q3ewmkG49 where the power
line ROW runs diagonally on the right side, and the actual grounding
point is the weird circular shape at the upper right. Additionally,
multiple conductors (6) run from the ROW to the circle. The street
view at https://goo.gl/maps/K94ZceiRfUL2ePaU7 shows the huge towers
as well as 4 grounding leads, two at the top of the towers and two
others on wooden poles. They are on rather substantial insulators.

Does anyone know any details for this rather odd setup? Why multiple
grounding conductors, and any details of the circular structure?
Do the grounding conductors carry current during normal operation,
perhaps with the line at half power with one side out of service and
the grounding (neutral?) carrying the return current?

Dimitris Tzortzakakis

unread,
Jan 3, 2021, 7:10:26 AMJan 3
to
the ground wires on top of the poles are lightning arresters. they
normally carry no current. the other two on the wooden poles seem to
carry too high a potential to being ground wires. they probably could be
a MV feed for a nearby town. I read that in HVDC feeds there are no
fround wires and the ground current flows through, the well, ground,
from the starting point of the transmission line to the end point. and
there are cases like submerged feeds where the current has to flow
through earth (and I suppose the cable's shield, but that would be very
thick for 1200+ amperes).

Dean Hoffman

unread,
Jan 3, 2021, 12:46:54 PMJan 3
to
You might try the sci.electronics.design group. There are still some
knowledgeable people there.

gfre...@aol.com

unread,
Jan 3, 2021, 1:35:56 PMJan 3
to
On Sun, 3 Jan 2021 11:46:50 -0600, Dean Hoffman <deanh...@clod.com>
wrote:
In a DC system I don't think either conductor is grounded. It also
looks like the other line on the wood poles is another DC system since
there are only 2 conductors, both ungrounded. I suppose it could be a
delta distribution but they usually run all 3 legs on a delta unless
it is just a run down a residential street. I don't see much medium
voltage single phase derived from delta but I assume someone might do
it. It is usually wye (one hot and a neutral) in Florida

Michael Moroney

unread,
Jan 3, 2021, 4:58:10 PMJan 3
to
Dimitris Tzortzakakis <no...@nospam.com> writes:

>Στις 3/1/2021 8:03 π.μ., ο/η Michael Moroney έγραψε:
>> There is a long HVDC power line from northern Quebec Canada to Ayer,
>> Massachusetts USA. It operates at either +/- 375 kV or +/- 450 kV
>> depending on source. As I understand it, it is grounded at exactly one
>> point, near Saint-Claude, Quebec. You can see it on this Google
>> satellite view: https://goo.gl/maps/bnsYcbv9Q3ewmkG49 where the power
>> line ROW runs diagonally on the right side, and the actual grounding
>> point is the weird circular shape at the upper right. Additionally,
>> multiple conductors (6) run from the ROW to the circle. The street
>> view at https://goo.gl/maps/K94ZceiRfUL2ePaU7 shows the huge towers
>> as well as 4 grounding leads, two at the top of the towers and two
>> others on wooden poles. They are on rather substantial insulators.
>>
>> Does anyone know any details for this rather odd setup? Why multiple
>> grounding conductors, and any details of the circular structure?
>> Do the grounding conductors carry current during normal operation,
>> perhaps with the line at half power with one side out of service and
>> the grounding (neutral?) carrying the return current?
>>
>the ground wires on top of the poles are lightning arresters. they
>normally carry no current.

I don't think they are lightning arrestors. Near the south end, this
line has an insulated conductor and a pair of (uninsulated) lightning
arrestor lines. https://goo.gl/maps/LGNiEYMcC7rrtjMQA

> the other two on the wooden poles seem to
>carry too high a potential to being ground wires. they probably could be
>a MV feed for a nearby town.


I followed these lines to the circular ground point using Google Satellite
View zoomed in. They are two of the 6 conductors which go there.
Two others are the two conductors on top of the pylons. It appears the
other two are also the two conductors on top of the pylons but from the
ones continuing past the point where the lines go to the circle.

They are not the feed for a town. I have never seen a delta distribution
system using the ground as a conductor in the US (although this is
Canada)