Does the killowatt have a problem reading accurately with UPS units?
>> Does the killowatt have a problem reading accurately with UPS units?
>I just checked a KAW P4400 with two stepped square wave inverters and a 60W
>incandescent lamp. It shows 111V 55W and 129V 59W. I see odd readings on the
>input of a UPS too, but they have always been higher than expected.
Have you had a chance to check the power draw
of that "60 watt" lamp when it's plugged directly
into the outlet (that is, no UPS inline)?
>
I would say that's on account _you're_not_ using a Kill-o-Watt meter,
like the OP is. I, like you, ass-u-me d he was talking about a Kill A
Watt(tm) meter.
As I mentioned in a reply to another poster in this thread, I have
experience with UK version of the Kill A Watt(tm) meter and there's no way
it would behave in the manner described by the OP with regard to what is
obviously a cheap meter trying to pass itself off as a Kill A Watt(tm)
meter.
--
Regards JB Good
In that case, I rather suspect that your meter has a fault. An obvious
test would be to use it to measure resistive loads such as incandescent
tungsten filament lamps, electric kettles, electric toasters, electric
soldering irons and so on.
These are loads that have a measurable resistance which will allow you to
estimate their actual power consumption by way of a sanity check (in
addition to the rating plate or label).
Bear in mind that most electric heating elements have a modest positive
temperature coefficient of resistance so will read a little lower than
expected when cold. The exception to this is the humble tungsten filament
lamp where the postive coefficient is not so modest (multiply the cold
resistance reading by a factor of 10 if want a ball park figure estimate
of its resistance at working temperature).
--
Regards JB Good
JB - even the lill-a-watt may be able to be fooled by a "digital"
power supply putting "dirty power" back out the line. I'm going to
have my UPM replaced and see if the new one has the same issue.
>
> "Johny B Good" <inv...@ntlworld.com> wrote in message
> news:op.v137d1elkd9x7s@fred...
>> On Tue, 20 Sep 2011 13:31:15 +0100, Jim Wilkins <murat...@gmail.com>
>> wrote:
>> ...I see odd readings on
>>> the
>>> input of a UPS too, but they have always been higher than expected.
>>>
>>
>> When you say higher than expected, do you mean, for example in the case
>> of an APC SmartUPS 700, higher than the expected 20W maintenance load
>> (fully charged battery, or, indeed, no battery at all)[1] plus the load,
>> say 100W, giving a reading higher than the expected sum total figure of
>> 120W?
>>
>> Regards JB Good
>
> The UPS in question is a Tripplite 1050 I bought second-hand with
> apparently
> bad batteries, which recovered nearly their full capacity after a few
> test
> cycles.
>
> I thought its initial power demand was ~60W but noticed a brief peak of
> 100W
> after posting that. I had seen ~130W with a laptop plugged in and
> booting.
> Now it makes sense.
One would hope that the 100W represents a battery re-charging demand (and
ditto for the 60W reading). One might reasonably expect a 1KVA (700W) UPS
to have a maintenance demand when the battery pack is fully charged no
higher than 30W (on a par with the SmartUPS 700's 20W maintenance
consumption compared to the VA level of protection in each case).
Actually, with a modern design of UPS one might reasonably expect a
maintenance consumption of 5W or less.
I've also got an ancient UPSonic UPS600 which I retired about 12 months
ago on discovering that its maintenance consumption had risen from its
normal 17W up to the 35W mark indicating that it had fried its second set
of batteries (2 banks of 3 by 12v 7AH dryfits) after about a 3 or 4 year
period of service.
I'd had enough by then. It still functions but it just isn't as kind to
its batteries as it could be and has no automated battery condition test
option to give you a clue as to the impending demise of the batteries. In
any case, even the normal 17W maintenance consumption was looking like a
luxury I could well do without, especially as it was supplying a second
level of UPS protection from the protected mains sockets powered by my
SmartUPS 2000 (a 2KVA 1500W unit) that I keep in the basement.
The point I'm making here is that you might want to allow that TrippLite
plenty of time to fully charge its battery and test its consumption with
nothing powered from its outlets. Since the battery pack (3 x 6V 10AH
dryfits) can be hot swapped, you can disconnect them and check whether the
maintenance consumption changes. if the battery pack is in good condition
and has fully charged, you won't see any difference (when I did this test
on the SmartUPS 700 I couldn't detect any change, and I was using an
analogue meter which can show the tiniest of changes that would be totally
lost on a digital meter).
Any noticeable drop in consumption when disconnecting the battery should
be taken as a warning of impending battery failure. To be certain that the
battery is as charged up as it can be, reconnect the battery and repeat
the test a few hours later (preferably 4 or more). If you still see the
same drop on disconnection, you can be pretty certain the battery is past
its best.
The annoying thing with that tripplight unit is its use of three 6v 10AH
batteries rather than the more usual pair of 12v 7AH batteries which are
far more widely available on account of their use in home burglar alarm
control panels. The WH ratings are very similar, 180 and 168 watt hours
respectively.
This is yet another UPS manufacturer who fails to reveal the maintenance
consumption figure for its product. The only hint of this is a reference
to "Green & high efficiency features" as being "Greater than 95%
efficiency - GREEN UPS". WTF is this supposed to mean? Can it be the
conversion efficiency of battery power into line voltage power? Perhaps
this is their rather coy way to explain why it might be consuming just
over 35W when plugged into an outlet with no load attached. Best of all,
WTF _is_ "GREEN UPS" supposed to mean exactly? My guess is that it's
simply the usual marketing BS that's so often used to sugar coat an
otherwise unpalatable fact. You might, indeed, find that the UPS does take
over 30W with the battery pack disconnected, thus revealing the marketing
BS for what it is.
To highlight the importance of "This dirty little secret", at one point I
was burning 82W in maintenance consumption from a collection of 5 UPSes
that I'd acquired at radio ham rallies over the past 20 years or so. After
retiring that Upsonic UPS600 and the SmartUPS 700 (which had also been
providing a second level of protection from the protected supply) I've now
reduced this to some 45W.
I'm using an ancient Emerson 30, my very first UPS from about 20 years
ago, to protect the Cable modem wireless router powered from a normal
mains outlet. The maintenance consumption on this is only around the 7 to
8 watt mark. Strange to say, this was the only UPS that ever got used in
anger to cover a 3 or 4 hour outage shortly after its acquisition.
Even so, what it was used for was simply to power a lamp stand with one
of those (at the time) new fangled CFLs fitted in order to provide
illumination from the half landing to light up the hallway and the stairs.
It was also handy to illuminate the upstairs toilet which allowed one of
the children to complete their school homework whilst sitting on the
toilet seat.
That event happened on a radio ham club night. On returning home about 3
hours later, The mains supply was back on and it seems the UPS had managed
to keep that 15W lamp powered right through the whole outage which ISTR
was around 4 hours in total. Since this ancient unit doesn't have a black
start function it wasn't possible to switch it on and off to maximise
battery endurance, leaving me only with the one option of shedding the
load, i.e. switching the light off.
Aside from a period of sub one second dropouts a few years back when the
local substation contactor gear was in need of an overhaul, we've never
had any other outages. Here in the UK, suburban mains supplies are very
reliable (most of the UK population lives in the 'burbs) so the desire to
protect against a once per generation outage event might seem a little bit
over the top but it's my computer kit I'm protecting. The market for UPSes
is very tiny indeed in the UK. However, there's every possibility that
this may change in the not so distant future.
>
> That laptop is becoming a data logger. Yesterday I added a dual serial
> port
> PC card to run both a Dataq DI-194RS four channel A/D and a serial-output
> Radio Shack DVM. Since the meter isn't fast enough to catch inrush or
> switching supply current I got some of these to use with the 194:
> http://www.gmw.com/magnetic_sensors/asahi/current-sensors-HA.html
> and ordered these to read thermocouples:
> http://parts.digikey.com/1/parts/2004324-ic-thermocouple-a-w-comp-8msop-ad8495crmz.html
>
> The 400MHz laptop draws only ~8W with the screen off and should run for
> days
> from a truck battery.
>
Is that using the truck battery to directly power the laptop through its
charger socket?
--
Regards JB Good
I was just confirming that we were both on the same page, as it were. ;-)
>> The new EM 100 registers .21 KwH over a period of 5.1 hours - which
>> translates to almost exactly 40 watts. The line reads 113 volts on the
>> new unit, and 116 on my old one.My LAB meter reads 115.6 volts - so
>> the new meter is going back.
Woah! Hold your horses! Does your LAB meter take a series of samples,
square each value, sum them over a period of time, preferably over at
least one or more complete cycles, average the results then calculate the
square root of that average to accurately measure the RMS voltage?
Or, is it just an accurately calibrated moving coil meter with a
rectifier to produce an average voltage reading which is then calibrated
by the multiplier resistor to produce a deflection on the scale based on
the fixed relationship between average and RMS for a sine waveform?
Or, does the meter simply use the peak value of the mains voltage and use
a multiplier resistor 1.4 times larger than it would be for a constant DC
voltage to scale the peak to its corresponding rms equivalent (again, a
correction factor based on the assumption that the mains is a pure sine
waveform)?
Since that EM100 is already gathering such voltage signed sampling data
to be multiplied by the corresponding current signed sampling data to
calculate both positive and negative power values to be averaged then
summed to produce a net power flow reading, it seems highly likely that
this data and processing power is not going to go to waste.
There's every chance, within the limits of sampling error, that the meter
is giving a more accurate RMS voltage reading than a simple moving coil
meter ever could since the mains waveform (at least in the UK) is quite
noticeably flat topped (if you have you ever looked at the mains waveform
on an oscilloscope, you'll know exactly what I mean).
>>
>> It also indicates 0.69 amps, which at 113 volts would be 78 watts.
No, that just means it's 78VA which may or may not be 78 watts. In this
case, the real power figure is likely to be a lot less though not to the
same extreme you might see with a line interactive switching UPS such as
the SmartUPS 2000 that I've just been testing 3 digital meters and my
analogue Metrawatt power meter on[1].
>>
>> It is now on the "old" EM 100, which is more accurate voltage-wize,
>> according to my meter. It registers 0.72 amps at 116 volts - which
>> would be 83.5 watts. We will see what the KwH reading over time says.
>
>
> Well, they both agree with 40 watts, when the KWH is divided by time.
That does seem the more likely figure in view of the fact that the UPS is
float charging a battery with a steady inverter load on it. Incidently, it
would be useful to know what the UPS's model number is or it's basic
specifications.
[1] I've just spent about an hour in my basement collecting as much
measuring data on the four states of operation of the SmartUPS 2000. These
were rear panel switch in the off position (all functions disabled), rear
panel switch in the on position (charging only enabled, protected power
turned off, then activated from the front panel, enabling protected power
function without load then ditto with a 150W lamp load. I'll only detail a
couple of readings here and now which are relevant to yours (I'll post the
details in a later posting since it is now 4:48 AM BST as I type.
When I was testing the charging only mode (after allowing some 15 minutes
to let the battery return to its fully charged state) the 2000MU-UK (UK
version of the KAW P4400) I was getting a 26.5W and a 136VA reading
(averaged - there was a +/- variation of up to a watt/voltamp either way).
I would have recorded a PF figure but I forgot, however I did record a PF
value of 0.21 on the next stage of the test where I was getting readings
of 29.4W and 136.5VA. Assuming the 40 watt figure is correct that 78VA
figure you calculated implies a PF of just over 50%.
----------------
"Martin Riddle" wrote in message news:j5l8b2$knh$1...@dont-email.me...
Consider stocking up on your standard inverter test load. They may
become scarce in the future.
I know exactly what you mean. About 20 years ago, whilst still employed
by BT, I came across a Strowger PABX that had been decommisioned a few
years before and spotted the 24 225AH cells that had formed the 48v
battery before they'd all been disconnected and left to die.
I selected the best dozen out the bunch (based on appearance alone - the
cell cases were transparent to allow visual inspection of the plates) and
ferried them home (two trips). They'd been left for so long they were all
totally flat and I had to connect each one in turn via a 12v headlamp bulb
(acting as a current limiter/conductivity indicator) to a 12v charger in
order to kickstart each one (the electrolyte was so depleted of H2So4 it
was almost pure water with very low conductivity) before they could be
assembled into a pair of 12v strings that I could then apply the several
charge / discharge cycles needed to revive them. I reckon I had managed to
restore them back to 80% capacity by the time I'd finished the revival
process.
This provided my basement radio shack with a 12v 400AH battery backed
supply for the next 8 or 9 years by which time I'd lost interest in the
hobby and the cells were starting to show signs of old age by their
increased and uneven water consumption.
Realising that all I was doing was burning electricity to electrolyse
water into its constituents, I disconnected them all so I could determine
if I still had enough cells good enough to make up a single bank. The test
was simply to let them stand for a few weeks/months and discard those that
had the most reduced cell voltage from self discharge. The remaining half
dozen "good" cells I left standing with a view to assembling them as a
single battery bank. They're still standing where I left them some ten
years on.
>
>> This is yet another UPS manufacturer who fails to reveal the
>> maintenance
>> consumption figure for its product. ...
>
> The fully charged Tripplite's idle power is about 17W. The batteries
> hold a
> charge well when unplugged for months. I won't know the DC power to
> recharge
> them until I finish the laptop data logger, -after- I fix the hydraulic
> pump
> on my tractor and do some excavating. KAW measurements include the
> charger's
> or lab supply's overhead.
>
> I left it "off" (blinking) and unplugged for a week and measured 0.36 KWH
> ($0.05) to recharge it. I'll probably add a switch to disconnect the
> batteries without removing them, and test points to measure & recharge
> the
> batteries from a lab supply. The batteries and wires are such a tight fit
> that cramming them in bent a connector tab at some point.
I'd be inclined not to attempt that sort of modification, there are too
many issues, not the least of which is finding and fitting a 50 or 60 amp
switch. Allowing the UPS to maintain its own battery pack is usually the
best option and if you want to save electricity because you don't need the
protection for the foreseeable future, the best option is to _still_ let
the UPS keep its battery pack maintained but on a part time basis, say a 4
or 5 hour charging session once every week/fortnight/month, whatever seems
best.
>
>>
>> I'm using an ancient Emerson 30, my very first UPS from about 20 years
>> ago, to protect the Cable modem wireless router powered from a normal
>> mains outlet. The maintenance consumption on this is only around the 7
>> to
>> 8 watt mark. Strange to say, this was the only UPS that ever got used in
>> anger to cover a 3 or 4 hour outage shortly after its acquisition.
>> ....
>
>> Aside from a period of sub one second dropouts a few years back when
>> the
>> local substation contactor gear was in need of an overhaul, we've never
>> had any other outages. Here in the UK, suburban mains supplies are very
>> reliable (most of the UK population lives in the 'burbs) so the desire
>> to
>> protect against a once per generation outage event might seem a little
>> bit
>> over the top but it's my computer kit I'm protecting. The market for
>> UPSes
>> is very tiny indeed in the UK. However, there's every possibility that
>> this may change in the not so distant future.
>
> In New England power suffers from tropical hurricanes, arctic ice storms
> and
> idiotic traffic accidents. I've twice lost it for a week, both in
> midwinter.
Local suburban house voltage distribution, here in the UK, is all served
by underground cables connected to a local sub-station so is largely out
of harm's way. Even the bean counters can't compromise new developments
since we Brits simply wouldn't tolerate such eyesores in the suburban
landscape. Then there's the fact _so_ well and truly proven that the
capital expense of laying a new underground distribution system more than
justifies the savings on the maintenance cost to the extent that it makes
no sense whatsoever to do otherwise except in remote rural areas of the
country.
>
>> Is that using the truck battery to directly power the laptop through its
>> charger socket?
>> Regards JB Good
>
> There isn't much difference between a 12V auto/air adapter which inverts
> to
> 18V or a small 120V inverter plus the mains power supply. I haven't
> measured
> it precisely because the computer's draw isn't steady, and I don't own a
> DC
> current probe for the scope. The only number that matters is run time,
> which
> is too sensitive to hard drive activity and processor + fan speed to
> characterize accurately. There's no point testing it with the computer
> inactive because I wouldn't waste battery power that way during a
> blackout.
>
Yes, the issue is really to do with the number of voltage level
conversions between the utility supply and motherboard voltages. There are
enough such conversion stages without adding yet another two in the form
of a UPS. With laptops, it's rather galling that their battery chargers
are viewed by the money grubbing makers as their version of the Printer
manufacturer's replacement inkjet tank/cartridge profiteering scam.
I'm pretty certain that some (if not all) of the early laptops were
designed to be charged from cigar lighter socket voltage (ranging from
10.8v right up to 15v) since the switching power conversion process used
was quite capable of working over that range, including up to the 16v
limit used by the first mains chargers.
No doubt these chargers were set to the upper limiting voltage rather
than the more useful 12 or 13.8 volts in order to reduce the amount of
current flowing through the plug/socket contacts (an engineering decision)
as well as restricting their utility to solely that of laptop charger
(endorsed by the marketing division).
It only needed one of the competing manufacturers to start a "Voltage
War"(tm) as a means of keeping a monopoly on the supply of replacement
chargers unique to their brand at grossly over-inflated prices by adding
"voltage agnostic[1] spoiler" circuitry to the laptop's power management
module. The requirement for a specific voltage from the charger ( be it
16, 18, 18.5, 19, 19.5, 20, 22 or 24 volts to within +/- half a volt) is
an entirely spurious requirement enforced by that additional circuitry.
The point here is that if the laptop manufacturers had stuck with the
original voltage agnostic power module circuit(anywhere from a 10.8v
minimum to whatever the input capacitor(s) chosen voltage rating was,
typically 16 or 25 volts) you'd have been able to power your laptop
directly from that 12v battery.
[1] agnostic is kind of apt in this case since the manufacturers had "The
Church of 16 volts", "The Latter Day Saints of 22 volts" and so on to
choose from as well as a plethora of connector types and sizes to spice
things up even further.
--
Regards JB Good
That's not a problem for me. That single 150W lamp I used in my meter
test is one of three that I've taken out of the box of 25 I acquired as a
free gift a couple of decades back. ;-)
--
Regards JB Good