Well, other than going by any published specs on the computer's PSU, if
there some with inrush surge listed, you'll need to get a newer ammeter
and line splitter to test the inrush.
With a motor starting up which looks like a short consisting of lots of
wire, there is a large inrush load. I don't see a computer PSU having
much of an inrush over its maximum rated capacity, and then divided by
whatever is its efficiency; i.e., for your Cooler Master M850 PSU, with
its 90% efficiency (initial rating, not after several years as
efficiency wanes), its 850W capacity would draw 850W/0.9 = 944W, or
about 8A to 9A. On a 15A circuit, that's 54% of the circuit capacity.
As the article mentions a 15A breaker actually handles a 12A load, so
turning on the computer consumes 68% of the circuit capacity.
That's assuming your PSU's output is max'ed out. You could get a
kill-a-watt meter to see what is the actual load by your computer. The
meter won't show inrush current, just the sustained power load.
Switching power supplies usually incorporate inrush current, like using
a resistor (passive) or multiple resistors, switching device, and
control circuit (active). The resistor affect the RC charging curve of
the capacitors to flatten the inrush curve. Instead of a simple
resistor for passive limitation, a negative temperature coefficient
(NTC) resistor, or thermistor is used that has high resistance when
cold, and low resistance when warmed. Inrush current will be low
through the thermistor in series with the power line (after the diode
bridge), and gone by the time the thermistor warms up with the current
passing through it. The inrush is throttled at the start, not as high,
but takes longer to charge the capacitors. A switch can be used in
parallel to zero out (bypass) the thermistor when resistor gets low as
it warms. Active inrush control can consist of resistors, triacs,
thyristors, transistors, and a switching device, and there are way too
many designs to get into here.
The point is current regulation can easily control inrush current. This
is for switchmode PSUs used by computers. They don't use linear PSUs
with huge transformers that look like a short of a very long length of
wire. Whether or not inrush is regulated depends on the quality of
design. I've seen 300W PSUs that have a an inrush rating of <45A, but
that was for a 70% non-activePFC, and inrush is measured peak to peak,
not peak to baseline. That's huge on a 15A circuit, but is very
momentarily, like 3 cycles or 0.05 seconds (check the hold-up time which
is likely around 0.016 seconds), so the breaker doesn't warm up enough
to make it snap open yet I've heard about huge setups with huge PSUs
that tripped a breaker. Maybe that depends on the type of breaker, like
a standard breaker relying on heat to trip versus AFCI breakers designed
to detect arcs in a circuit (which high inrush could emulate). AFCI
(Arc Fault Circuit Interrupter) breakers use electronics to monitor the
line to detect multiple types of faults on the line (whether an actual
arc or something that looks like one), and are often required in new
construction per NEC (National Electrical Code); see
https://www.afcisafety.org/afci/what-is-afci/#1469600217909-520261d7-4cb5.
Due to how LED light bulbs work, that momentary overload could make them
flicker. I suspect the inrush period doesn't last longer than the
hold-up rating. Cooler Master says that PSU has >16ms (so <17ms).
There is no persistence in illumination for LEDs, nor are they designed
to sustain illumination when voltage drops even if only for an instant.
https://www.superiorlighting.com/lighting-resources/light-bulb-learning-center/led-light-bulbs/led-lamp-components-explained/
"An LED driver - regulates the current flowing through the LED, similar
to a ballast in a compact fluorescent lights.LED drivers can be internal
or external. LED Light output is proportional to its current; any slight
variation in the current can result in unacceptable changes in light
output."
("unacceptable" could be viewed as "perceptible", but a flickering LED
has a shorter life.)
For your PSU:
https://www.coolermaster.com/catalog/power-supplies/mwe-series/mwe-gold-850-v2-full-modular/#specifications
That doesn't show the inrush current for that PSU. Not really
surprising since Cooler Master doesn't manufacture anything. Same for
Corsair, Crucial, and many brands. They contract with someone else to
do the manufacture accord to their specs, and slap their name on the
product. Think of wanting to have a cabinet built to your specs, but
you give the blueprints to a carpenter.
This PSU has active PFC (Power Factor Correction). Because the PSU is
changing its frequency, it's possible that feedback into the line hits
the same used in the regulator inside the LED light bulb.
https://www.nuvation.com/resources/article/power-supply-design-basics-active-power-factor-correction
"Requires better filtering to prevent high frequency hash from getting
to the line." For the <17ms hold-up time (and probably close to the
inrush time), and because LED light bulbs are nothing more than a bridge
diode with an inline capacitor on input, and a capacitor, resistor, and
LED bulb(s) on the output, the RC time is very short, so 16ms could be
more than sufficient a drop in voltage to affect the LED bulbs. The
capacitors are noise filters, not for capacity.
Use the Kill-a-Watt meter to see what is the sustained load consumed by
your computer's PSU. No, don't test when idle. Obviously the computer
is not idle when you do a cold boot. Keep the hardware as busy as
possible, like running Prime95, during which you measure the power or
amps consumed by the PSU. A Kill-A-Watt meter won't measure inrush
current, but you'll get a better idea of what is the actual load drawn
by your PSU from the line. As worst case, multiple by 2 for the inrush
current with the PSU under full load (or whatever maximum load you can
put on the PSU during testing). It won't cost $20,000 USD to measure
inrush current, but more like $160 USD by getting a better ammeter and
line splitter. If you don't get the tools, you may never know the
inrush current your PSU puts on the line.
You mentioned using a fridge light bulb, but didn't mention whether it
was incandescent or LED. There are LED appliance light bulbs. You
might've replaced an LED with another LED. While getting more rare, you
can still find an incandescent to buy to test when powering up your
computer from cold.