Wood is a poor insulator. Your looking at about R-1. Steel framing
would allow almost 100% insulation around the outside. A garage can
not be connected to a homes ventilation system. Most likely due to the
risk of CO poisoning.
AJ
Wood has an R value or around 1/inch. It varies by specie of wood, some
being better at around 1.25 and some being a little worse. But if you
figure an R of 1/inch you'll be in the ball park. So a 3.5" deep stud
will have an R value of around 4 give or take. This is much less than
the same thickness of fiberglass (11-13) so, yes, the studs are a better
conductor than is the insulation in between the studs.
Matt
Here's what I use when running energy calculations:
Item R/inch Mat'l Depth R U
2x4 1.25 3.50 4.38 0.23
2x6 1.25 5.50 6.88 0.15
2x8 1.25 7.25 9.06 0.11
2x10 1.25 9.25 11.56 0.09
2x12 1.25 11.25 14.06 0.07
3/4" plywood 1.25 0.75 0.94 1.07
5/8" plywood 1.25 0.63 0.78 1.28
1/2" plywood 1.25 0.50 0.63 1.60
1x subfloor-softwood1.25 0.75 0.94 1.07
1" hardwood 0.90 0.75 0.68 1.48