Hi Wayne,
Although I don’t have any information on the facility, I would imagine that a special study would have to be conducted for this site to determine the requirements. These requirements will probably go above and beyond AS1170.4.
I’m more in the non-structural seismic field but I don’t think Australia conduct enough special studies for these types of facilities. It usually gets handballed down to contractors who have no idea what special study means.
Regards
Tinus Smith
Engineering Manager
CPEng (Aus/NZ) RPEQ IntPE(Aus/NZ)
![]()
Gripple Australia
To view this discussion on the web visit https://groups.google.com/d/msgid/aeesorg/CA178D9D-FD03-44C2-9ED5-0BCC3F702210%40gmail.com.
Notwithstanding the specific requirements of such a plant (Kevin's comments), attached a couple of general publications on seismic design of industrial plants that may be of some assistance.
Cheers
Simon Matthews
Hello Wayne,
I’ve not worked on structures outside of the BCA (NCC Volume 1) although I have a few thoughts on the matter:
This facility would most likely be considered IL4 unless and someone wished to argue that a major failure would be confined within the boundary or not any population/neighbours (ie remote)
Source of Importance Levels and return periods for Australian structures:
I agree with Tinus: a Special Study should be completed, and I would anticipate the SA DIT would have a strong influence upon this in whatever capacity they have within government.
A great deal of the Australian Standards fall far short of clearly stating the requirement to meet the requirements of AS1170.4, especially the HV and fire suppression system standards.
My personal experience with the VIC WorkSafe Hazardous Materials division, responsible for Safety Case facilities… there’s a major assumption that Earthquake requirements fall far outside of their responsibility and that all facility designers and constructors are aware of their obligations. They had never heard of a special study also when I attempted to engage with them.
I would expect AS1170.4 to be mandated, with only international requirements of greater level to be able to supersede it.
Regards,
Jordan