I am currently trying to analyze a wall with ventilated siding in WUFI and have found numerous suggested approaches, with perhaps the most involved being an iterative estimation process described here (p. 18): http://www.buildingscience.com/documents/reports/rr-0907-ventilated-wall-claddings-review-performance-modeling.Does anyone have a good sense of what is acceptable practice?
--
You received this message because you are subscribed to the Google Groups "Passive House Northwest" group.
To unsubscribe from this group and stop receiving emails from it, send an email to PassiveHouseN...@googlegroups.com.
For more options, visit https://groups.google.com/d/optout.
Here is an excerpt from my notes from a late-2012 WUFI workshop with Achilles and Andre:
To create a ventilated cavity (air has both a way in, and out), create a material layer using "Air" from "Generic Materials" Then, on the "Assembly/Monitor Positions" window, click on the "Sources, Sinks" button. Then click on the "New Air Change Source" button. See instructions for creating a leak, below. Under "Spread Area", select "Whole Layer". Under "Source Type", select "Constant". At "Air Changes [1/h]", enter the appropriate value. (Air-change rates for ventilated cavities are between 25 and 50 for most cases, and there is not much difference between those two values; see ASHRAE TRP 1091.) For a drainage plane (such as can be created by the adhesive beads used to adhere exterior insulation), 5 - 10 ACH - assuming venting flashings are provided at top and bottom.