Hello. Both the interior and exterior boundary conditions are set to Auto Enclosure. Therm cannot calculate the value when both are set this way. When Auto Enclosure is used on the inside the outside radiation needs to be set to Blackbody or simplified.
6.0 Btu/h/ft2/F is the standard outdoor film coefficient should be set to simplified.
1.46 Btu/h/ft2/F is the standard indoor film coefficient for walls should be set to simplified.
In the file indoor boundary is set to vinyl/wood and is probably close for a wall but really meant for window frames.