I am using THERM 7.8 and validating EN ISO 10077-2 Annex I.
For case I.1 (reference L²D = 0.550 W/(m·K)), I obtain:
EN ISO: 0.53784 (−2.21%) – PASS CEN Simplified: 0.53064 (−3.52%) – FAIL
NFRC: 0.52944 (−3.74%) – FAIL
The other Annex I cases I tested are within ±3%.