Hello,
I am not sure did anybody have this problem but when I set up glass configuration in Window and when I insert the same configuration in Therm I get different glass thickness.
How to fix this?
Thanks in advance.
Goran

1.jpg




2.jpg


Robin Mitchell

unread,
Mar 22, 2019, 1:20:06 PM3/22/19
to THERM
Each program has the option to set the thickness values to "Nominal Thickness" 

In the THERM screenshot you can see the "(nominal)" indicator to the right of the thickness, so in this case THERM is set to use the nominal thickness for the glass layers. This can be set when importing a WINDOW glazing system into THERM

NominalGlassThickness-THERM.png

Then in WINDOW, you can also specify to use Nominal Thickness in File/Preferences/Options. Checking that box results in the glass layer 5012 having a thickness of 0.236


NominalGlassThickness-WINDOW.png



Robin

Miracle Ojo

unread,
Jun 15, 2020, 4:29:27 AM6/15/20
to THERM
I am having this problems also, can you guild me through on how to have it fixed?

Robin Mitchell

unread,
Jun 16, 2020, 11:27:06 AM6/16/20
to Miracle Ojo, THERM
It looks like you are using nominal thickness in the THERM instance, and not in the WINDOW instance.

In WINDOW, the setting for displaying in nominal thickness is set in Preferences

image.png

In THERM, you indicate whether or not to use nominal thickness when you import the glazing system

image.png

--
You can view the THERM forum online at: http://windows.lbl.gov/software/THERM/forum
---
You received this message because you are subscribed to the Google Groups "THERM" group.
To unsubscribe from this group and stop receiving emails from it, send an email to LBNL-THERM+...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/LBNL-THERM/3480f7e5-d537-4eae-bc5c-2ad1fe58cf57o%40googlegroups.com.


--
Robin Mitchell
Building Technology and Urban Systems Division
Energy Technologies Area
Lawrence Berkeley National Laboratory

Raymond Roy

unread,
Jul 27, 2023, 5:19:38 PM7/27/23
to THERM
Hello, 
I have both my Therm and Window set for Nom Glass thickness. in window the thickness reads .975" but it shows and imports as .950" in Therm.  

Please advise. 

Robin Mitchell

unread,
Jul 27, 2023, 5:50:15 PM7/27/23
to Raymond Roy, THERM
Raymond

Can you email me the THERM file and the WINDOW database, zipped up? 

You can make a small WINDOW database with just the relevant glazing systems by making a "Project Database" -- see this Knowledge Base article for details


Robin


---
You received this message because you are subscribed to the Google Groups "THERM" group.
To unsubscribe from this group and stop receiving emails from it, send an email to LBNL-THERM+...@googlegroups.com.

Zugur Rakhmanov

unread,
Jul 27, 2023, 6:13:02 PM7/27/23
to Raymond Roy, THERM
Hi,
Which of unit system do you use in Window?
I think you should use the same unit systems in both programs.