Wiring a wireless thermostat

510 views
Skip to first unread message

Golan

unread,
Nov 17, 2007, 1:20:12 PM11/17/07
to
Good evening.

I am trying to replace and old mechanical thermostat with a new
wireless digital thermostat. At the moment the system is controlled by
Honeywell ST6400C Programmer,

The old thermostat is Honeywell T6360

http://europe.hbc.honeywell.com/products/pdf/en0r8281uk07r1204.pdf

The wiring to the old thermostat is
3=N
1=L
And one goes to the Earth

I am trying to replace the old thermostat with SALUS RT500RF

http://www.heatingcontrolsonline.co.uk/instructions/RT500%20RF%20MANUAL%203(1).pdf


The problem is that I can't understand the wiring diagram; also there
is no option to earth in the new thermostat

I tried to connect only the L and the N but the problem is even when
the thermostat suppose to stop the heating it is still keeping it on,
the light on the receiver goes off but the electrical connection is
not been disconnected

HELP .... :(

Thank you

John

unread,
Nov 17, 2007, 3:39:17 PM11/17/07
to

"Golan" <go...@etzuvim.com> wrote in message
news:9f5cbf3c-c037-4652...@v4g2000hsf.googlegroups.com...

You should have a live, Neutral, switched feed and earth (3 cores and earth)

Have you checked to see what you have at the boiler end of the circuit?


Golan

unread,
Nov 17, 2007, 3:48:23 PM11/17/07
to
On Nov 17, 8:39 pm, "John" <john.plant...@ntlworld.com> wrote:
> "Golan" <go...@etzuvim.com> wrote in message
>
> news:9f5cbf3c-c037-4652...@v4g2000hsf.googlegroups.com...
>
>
>
> > Good evening.
>
> > I am trying to replace and old mechanical thermostat with a new
> > wireless digital thermostat. At the moment the system is controlled by
> > Honeywell ST6400C Programmer,
>
> > The old thermostat is Honeywell T6360
>
> >http://europe.hbc.honeywell.com/products/pdf/en0r8281uk07r1204.pdf
>
> > The wiring to the old thermostat is
> > 3=N
> > 1=L
> > And one goes to the Earth
>
> > I am trying to replace the old thermostat with SALUS RT500RF
>
> >http://www.heatingcontrolsonline.co.uk/instructions/RT500%20RF%20MANU...

>
> > The problem is that I can't understand the wiring diagram; also there
> > is no option to earth in the new thermostat
>
> > I tried to connect only the L and the N but the problem is even when
> > the thermostat suppose to stop the heating it is still keeping it on,
> > the light on the receiver goes off but the electrical connection is
> > not been disconnected
>
> > HELP .... :(
>
> > Thank you
>
> You should have a live, Neutral, switched feed and earth (3 cores and earth)
>
> Have you checked to see what you have at the boiler end of the circuit?

I checked the wires from the thermostat to the programmer.

1 wire go to the N (CH on)
1 wire go to Live witch for some reason is connected to the wiring
center
1 earth

i have no idea where to start.

may be it is not the right thermostat for the system.

Heliotrope Smith

unread,
Nov 17, 2007, 5:15:51 PM11/17/07
to

"Golan" <go...@etzuvim.com> wrote in message
news:9f5cbf3c-c037-4652...@v4g2000hsf.googlegroups.com...
> Good evening.
>
> I am trying to replace and old mechanical thermostat with a new
> wireless digital thermostat. At the moment the system is controlled by
> Honeywell ST6400C Programmer,
>
> The old thermostat is Honeywell T6360
>
> http://europe.hbc.honeywell.com/products/pdf/en0r8281uk07r1204.pdf
>
> The wiring to the old thermostat is
> 3=N
> 1=L
> And one goes to the Earth

There is no neutral on the old stat. Just live in and switched live out plus
earth.


>
> I am trying to replace the old thermostat with SALUS RT500RF
>
>
http://www.heatingcontrolsonline.co.uk/instructions/RT500%20RF%20MANUAL%203(1).pdf
>
>
> The problem is that I can't understand the wiring diagram; also there
> is no option to earth in the new thermostat

The new wireless stat does not need an earth as there is no mains going to
it. It is powered by batteries.
Mains power is required at the reciever only.


>
> I tried to connect only the L and the N but the problem is even when
> the thermostat suppose to stop the heating it is still keeping it on,
> the light on the receiver goes off but the electrical connection is
> not been disconnected
>
> HELP .... :(
>
> Thank you

What make/model boiler are you wiring up?


Golan

unread,
Nov 17, 2007, 5:59:27 PM11/17/07
to
On Nov 17, 10:15 pm, "Heliotrope Smith" <sm...@heliotrope.com> wrote:
> "Golan" <go...@etzuvim.com> wrote in message
>
> news:9f5cbf3c-c037-4652...@v4g2000hsf.googlegroups.com...
>
> > Good evening.
>
> > I am trying to replace and old mechanical thermostat with a new
> > wireless digital thermostat. At the moment the system is controlled by
> > Honeywell ST6400C Programmer,
>
> > The old thermostat is Honeywell T6360
>
> >http://europe.hbc.honeywell.com/products/pdf/en0r8281uk07r1204.pdf
>
> > The wiring to the old thermostat is
> > 3=N
> > 1=L
> > And one goes to the Earth
>
> There is no neutral on the old stat. Just live in and switched live out plus
> earth.
>
> > I am trying to replace the old thermostat with SALUS RT500RF
>
> http://www.heatingcontrolsonline.co.uk/instructions/RT500%20RF%20MANU...

>
> > The problem is that I can't understand the wiring diagram; also there
> > is no option to earth in the new thermostat
>
> The new wireless stat does not need an earth as there is no mains going to
> it. It is powered by batteries.
> Mains power is required at the reciever only.
>
>
>
> > I tried to connect only the L and the N but the problem is even when
> > the thermostat suppose to stop the heating it is still keeping it on,
> > the light on the receiver goes off but the electrical connection is
> > not been disconnected
>
> > HELP .... :(
>
> > Thank you
>
> What make/model boiler are you wiring up?

The boiler is vaillant ecomax 612
Honeywell ST6400C Programmer

i dont think ican wire a wirless thermostat in the currect
configration. is there any digital thermostat that i can buy that will
work with just a N and L wires ?


John

unread,
Nov 17, 2007, 6:33:20 PM11/17/07
to

"Golan" <go...@etzuvim.com> wrote in message
news:aa31e09b-9615-448c...@w73g2000hsf.googlegroups.com...
You are thinking wrongly - think live and switched feed. You may not have a
neutral although you have a black wire.

Imagine a simple switch - it has a live and a switched feed. This is what I
think you need. If you were connecting live to neutral you would get a
short.

( although I think you need a neutral to make it work)


Golan

unread,
Nov 17, 2007, 6:46:31 PM11/17/07
to

Can it be that the simple mechanical thermostat dose not have
neutral ?

in that case is a 2 wire digital thermostat will work ??

http://www.screwfix.com/app/sfd/cat/pro.jsp;jsessionid=KEQ3DYQRQGNNUCSTHZOSFFQ?id=39124&ts=43139

Heliotrope Smith

unread,
Nov 17, 2007, 6:58:57 PM11/17/07
to

"Golan" <go...@etzuvim.com> wrote in message
news:147dc589-9497-4d68...@n20g2000hsh.googlegroups.com...
If the existing thermostat has only two wires plus an earth going to it then
there is NO neutral . The (probably red) takes the live to the thermostat
(switch) and the (probably black) takes the live back to the boiler.

> in that case is a 2 wire digital thermostat will work ??
>
As long as the thermostat is volt free, yes.
>
http://www.screwfix.com/app/sfd/cat/pro.jsp;jsessionid=KEQ3DYQRQGNNUCSTHZOSFFQ?id=39124&ts=43139


Ed Sirett

unread,
Nov 17, 2007, 7:12:19 PM11/17/07
to


This subject comes up at least once a week (during the colder half of the
year). We need a FAQ or a wiki page on it. Some one must be able to to
write down something sensible.

Modern heating controls are double insulated and require no earthing,
having no metal casing or chassis. Sometimes there is a spare terminal to
park the unneeded earth wire on.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html

John Rumm

unread,
Nov 17, 2007, 10:20:37 PM11/17/07
to
Golan wrote:


> The old thermostat is Honeywell T6360
>
> http://europe.hbc.honeywell.com/products/pdf/en0r8281uk07r1204.pdf
>
> The wiring to the old thermostat is
> 3=N
> 1=L
> And one goes to the Earth

OK, reading between the lines here. It sounds like someone has used
ordinary two core and earth cable to hook up your old stat and has only
made use of some of its functionality. In reality I would guess you
*don't have any* neutral connected to the old stat.

The old style stats work better if there is a neutral present, however
they will still work without it.

Forget the colours of the wires: one will be a permanent live connected
to pin 1, and the output from pin 3 will be a switched live.

> I am trying to replace the old thermostat with SALUS RT500RF
>
> http://www.heatingcontrolsonline.co.uk/instructions/RT500%20RF%20MANUAL%203(1).pdf
>
>
> The problem is that I can't understand the wiring diagram; also there
> is no option to earth in the new thermostat

With the earth, cover it in earth sleeving, and fold it back on itself.
That way it is available if needed in the future. Its not needed now.

> I tried to connect only the L and the N but the problem is even when
> the thermostat suppose to stop the heating it is still keeping it on,
> the light on the receiver goes off but the electrical connection is
> not been disconnected

You probably connected your black wire to the pin identified as neutral
in the diagram thinking it is neutral.

Instead, look at the top 230V operation diagram in the manual, you want
to connect your red wire to the terminal marked L, and your black to the
one marked SL (On).

For completeness you should sleeve the black wire with red at both ends
to save further confusion. Both wire in the cable are live - one
permanent, one switched.

--
Cheers,

John.

/=================================================================\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\=================================================================/

John Rumm

unread,
Nov 17, 2007, 10:52:29 PM11/17/07
to
Ed Sirett wrote:

> This subject comes up at least once a week (during the colder half of the
> year). We need a FAQ or a wiki page on it. Some one must be able to to
> write down something sensible.

Sounds like a good plan...

Your wish is my command (well sometimes) ;-) :

http://wiki.diyfaq.org.uk/index.php?title=Thermostat_wiring

Now all we need is some content. I could shamelessly nick some diagrams
from that the PDF quoted above as a handy starting point.

Fancy adding any more relevant topics to the skeleton?

John

unread,
Nov 18, 2007, 5:17:13 AM11/18/07
to

"John Rumm" <see.my.s...@nowhere.null> wrote in message
news:13jvbod...@corp.supernews.com...

Guys - in the instructions it clearly looks as though it needs a Neutral -
as it is a wireless one it requires power. The instruction states "The unit
still requires 230v feed for volt free operation." This implies 3 wires and
earth.


John

unread,
Nov 18, 2007, 5:20:45 AM11/18/07
to

"John Rumm" <see.my.s...@nowhere.null> wrote in message
news:13jvbod...@corp.supernews.com...
> Golan wrote:
>
>
>> The old thermostat is Honeywell T6360
>>
>> http://europe.hbc.honeywell.com/products/pdf/en0r8281uk07r1204.pdf
>>
>> The wiring to the old thermostat is
>> 3=N
>> 1=L
>> And one goes to the Earth
>
>

T4360 A does not have a neutral - the connection between the stat and the
"Heating Load" (the boiler) is the switched live - it is not neutral.

Please - look at the diagrams and get your terminology right


John Rumm

unread,
Nov 18, 2007, 6:16:54 AM11/18/07
to
John wrote:

>>> The old thermostat is Honeywell T6360
>>>
>>> http://europe.hbc.honeywell.com/products/pdf/en0r8281uk07r1204.pdf
>>>
>>> The wiring to the old thermostat is
>>> 3=N
>>> 1=L
>>> And one goes to the Earth
>>
>
> T4360 A does not have a neutral - the connection between the stat and the
> "Heating Load" (the boiler) is the switched live - it is not neutral.

True, but we are talking about the T6360 which does have provision for a
neutral connection in the A and B variants. Only the 6360B seems to
actually have a use for it in that it has the heat anticipator
(according to the spec table)

> Please - look at the diagrams and get your terminology right

Indeed.

John Rumm

unread,
Nov 18, 2007, 6:25:18 AM11/18/07
to
John wrote:

> Guys - in the instructions it clearly looks as though it needs a Neutral -
> as it is a wireless one it requires power. The instruction states "The unit
> still requires 230v feed for volt free operation." This implies 3 wires and
> earth.

Yup, it quite possibly does for the receiver (the transmitter has
battery power).

This is one of the occasions where it is actually harder to wire the
wireless version than would normally be the case for a wired version!

John

unread,
Nov 18, 2007, 6:37:42 AM11/18/07
to

"John Rumm" <see.my.s...@nowhere.null> wrote in message
news:13k07lf...@corp.supernews.com...

Sorry - I got the model numbers mixed. I got a bit carried away when I saw
the diagram without the accelerator.

Perhaps there is a case for ease of wiring for the receiver to be fitted
close to the boiler - provided it is within range of the transmitter.

I believe the OP has a live and a switched feed (in black) are we agreed?
And that the model also needs a neutral.


John Rumm

unread,
Nov 18, 2007, 7:24:47 AM11/18/07
to
John wrote:

> Sorry - I got the model numbers mixed. I got a bit carried away when I saw
> the diagram without the accelerator.
>
> Perhaps there is a case for ease of wiring for the receiver to be fitted
> close to the boiler - provided it is within range of the transmitter.
>
> I believe the OP has a live and a switched feed (in black) are we agreed?
> And that the model also needs a neutral.

Yup, the original stat possibly has provision for a neutral, but it
looks like it has not been installed that way. The black wire sounds
like it is the switched live. (the original connections only make sense
for the A and B variants of the T6360).

The new stat's receiver will need a neutral (to allow the receiver to
draw power for itself). Assuming it is positioned close to the boiler
this could be connected via a length of multicore control flex, rather
than fixed wiring using 3&E. Alternatively the stat may currently be
connected to a wiring concentrator if it is being used to control the
boiler indirectly via a two or three port valve and possibly an external
"programmer".

Heliotrope Smith

unread,
Nov 18, 2007, 7:57:23 AM11/18/07
to

"Golan" <go...@etzuvim.com> wrote in message
news:9f5cbf3c-c037-4652...@v4g2000hsf.googlegroups.com...

Set up the receiver close to the wiring centre.
Remove the wire link on the receiver.
From the wiring centre find the permanent live & neutral and connect to L &
N on receiver.
Trace the old stat wires in the wiring centre, disconnect and do away with
these and connect to COM and NO.
Should now be able to set up transmitter and get things working.