For my welder and plasma cutter this would be a good but not necessary
thing. Currently none of my woodworking tools are 3 phase, but that could
change.
My questions are this...
1) Generally, what is the cost difference in kw/hr 3 vs.. single
2) Are woodworking power tools performance improved with 3 phase?
3) Would you do it if you could?
Thanks,
Brian
-----= Posted via Newsfeeds.Com, Uncensored Usenet News =-----
http://www.newsfeeds.com - The #1 Newsgroup Service in the World!
Check out our new Unlimited Server. No Download or Time Limits!
-----== Over 80,000 Newsgroups - 19 Different Servers! ==-----
> 1) Generally, what is the cost difference in kw/hr 3 vs.. single
None, you are charged by the watt.
> 2) Are woodworking power tools performance improved with 3 phase?
No, but it allows you to use smaller breakers and gauge of wire due to the
smaller amp draw.
> 3) Would you do it if you could?
Yes.
You then have any and all power options available to you. I go to many
auctions and I see three phase equipment go for peanuts where the same thing
in single phase goes for five times as much, because most home/small shop
people don't have 3 phase power, and big shop people don't go to auctions
looking for bargains.
I saw a 24" 10 hp, big ass, cast iron, minty fresh, planer go for $800
dollars because it was three phase and there were only hobbyists at the
auction.
If it costs less than $2000 for three phase power, you can get the back in
no time by buying used equipment.
Thanks,
David.
Every neighbourhood has one, in mine, I'm him.
Remove the "splinter" from my email address to email me.
Newbies, please read this newsgroups FAQ.
rec.ww FAQ http://www.robson.org/woodfaq/
Archives http://groups.google.com/advanced_group_search
Crowbar FAQ http://www.shavings.net/CrowBarFAQ.HTM
1) A transformer is required to convert 3 phase to single phase except 208
3phase WITH a neutral wire.
2) A special converter such as a roto-phase unit is required to convert
single phase to 3 phase.
If the service is 208VAC 3 phase WITH A NEUTRAL (Neutral is required), then
there is nothing to be concerned with. You get the best of both worlds. Any
leg of the 208 to neutral will give you your normal 110VAC power, however
220 is not available. If the 3 phase power is something like 480V then you
will need a step down transformer for all of your single phase needs. There
are a lot of factors to consider and there is no "best" answer to your
question. Below are a couple of websites that you can look at to do some
research. As far as performance is concerned, YES the 3 phase will provide a
more constant power source and therefore provide higher torque and smoother
operation over standard single phase tools. 3 Phase motors do not require
starter capacitors or brushes so they tend to live longer and run quieter.
If you only have single phase power available you can still convert to 3
phase with special equipment. Generally speaking, it is cheaper to convert 3
phase to 1 phase. Some of the links below are for converters.
If you are serious get an electrician handbook such as
http://www.amazon.com/exec/obidos/ASIN/0020364253/qid=1010291283/sr=2-2/ref=
sr_2_9_2/002-1344961-2804844 so you can get a better idea of what your
connection options are.
http://www.howstuffworks.com/power.htm
http://www.isomatic.co.uk/3phConverter.htm
http://www.phaseconverter.com/remanufacturedconverters.html
Good luck
None.
>
> 2) Are woodworking power tools performance improved with 3 phase?
3 phase induction motors are inherently simpler than single phase so they
tend to last longer. Bearings are the first to go rather than it being a
race between the bearing and the windings.
>
> 3) Would you do it if you could?
You bet!
>
> Thanks,
> Brian
Tom Jackson
Engineered Conversions of Woods into Sawdust
No doubt 3 phase motors run cooler and cost less. However, you might
want to consider a converter before getting commercial if your
electric utilities are similar.
Larry
--
ra...@lmr.com
"Brian N. Blazer" <br...@brianblazer.com> wrote (with possible
editing):
--
Ross Canant
http://www.myoldtools.com
"Tom Kendrick" <tken...@stealthaccess.net> wrote in message
news:aWA4PPUSGLtzeK=NFCFpX...@4ax.com...
> Some questions to guide you -
> Will the service be "demand" or metered as is done for a
> residence? Demand makes you pay for the highest use during a billing
> cycle.
> Single phase breaker boxes are very common, however 3-phase
> breaker boxes are more expensive and are not usually stocked. They are
> manufactured when ordered.
> Should you need/want to relocate later, you could become
> "locked into" 3-phase and reduce your alternatives for new sites if
> your equipment could not function on single phase power.
> Consult an electrician about his rates and equipment costs as
> though you will hire him to wire it for you. The difference may be
> significant.
> Tom
>You have lots of good answers here - I'll just add that you should
>check with your electric utility before making a decision. For
>example, up here in northern NH, Public Service (the electric utility)
>will only provide 3 phase at commercial rates which are very high and
>require a demand meter which easily makes them higher. The co-op (New
>Hampshire Electric Co-op) is similar and the cost from both utilities
>to provide 3 phase is staggering.
>
>No doubt 3 phase motors run cooler and cost less. However, you might
>want to consider a converter before getting commercial if your
>electric utilities are similar.
All the answers were fine, including Larry's. I've got a friend who has a
cabient shop, and he only uses single phase. Reason: he is the only industry
along a stretch of road some 18 miles long that could use 3 phase. At one
point, he wanted to go 3 phase and picked up a bunch of used gear in
anticipation. He's now trading/selling the gear, because the local power
barons told him it was far, far too costly to run a line to just feed one small
shop (3-4 employees).
But, IIRC, the original poster wanted to know if he should lease a building
with 3 phase already in it. I would, because it gives you the option of using
single or 3 phase, and 3 phase, as many others have noted, gives access to
literally tons (sometime in one piece of gear) of equipment at prices of not
much more than a quarter a pound.
Charlie Self
Hearing about all of the auctions where 3 phase equipment goes for the
cheap, I am REALLY interested now.
Brian
"Brian N. Blazer" <br...@brianblazer.com> wrote in message
news:3c37a...@goliath.newsgroups.com...
Three phase power can be generated from single phase easily, using readily
available converters of several types. Many home shop enthusiasts (like
me) make their own rotary converters. For further info, googlize
"converter rotary OR static OR VFD" in rec.crafts.metalworking.
www.google.com/advanced_group_search
Jim
Snip
If the service is 208VAC 3 phase WITH A NEUTRAL (Neutral is required), then
there is nothing to be concerned with. You get the best of both worlds. Any
leg of the 208 to neutral will give you your normal 110VAC power, however
220 is not available.
BUT..I must politely disagree.......... you can run a 220 volt motor on 208
volts although it will not run at top efficiency it will run
"Brian N. Blazer" <br...@brianblazer.com> wrote in message news:<3c38b742$1...@goliath.newsgroups.com>...
Without even looking at the other posts I would go with 3 pahse in a heartbeat.
And all because of electrical performance. I would further extend it to the
house if possible.
For morors the controls etc to get the motor started are as simple as pie.
And no starting circuitry in the motors. Just hit them with the 3 phase and
away they go. To reverse just swap any two leads.
The down side is that the power panel will be more expensive. I would go to a
place like a demoilition store. In my town I could get everything I need for
$200.00. I am sure you can do as well on Ebay.
Bob AZ
Bob AZ
Not quite.
A 208V/3ph/4w service provides 208V/3ph, 120V/1ph, but not 220V/1ph.
It is a square root of 3 thing.
--
Lew
S/A: Challenge, The Bullet Proof Boat, (Under Construction in the Southland)
Visit: <http://home.earthlink.net/~lewhodgett> for Pictures
What I forgot to add is that over the years, sold quite a few "Buck-Boost"
transformers to solve this very problem.
As an example, very common for shopping centers to be built with 208V/3ph/4w
which provides not only the single phase but also the 3 phase for the
heating and cooling loads.
When 208V was first introduced to shopping center builders, long before
everybody got their act together and ordered the right equipment, a lot of
mechanical equipment (air conditioning, refrigeration, etc) would arrive at
the job site with 230V/3ph motors.
Rather than send the equipment back and delay the construction cycle,
buck-boost x'fmr's came to the rescue.
SFWIW.
Actually, you were right the first time. If you were to connect one lead
of a battery operated oscilloscope to phase A and the refrence lead to phase B
(for instance) you would see a near perfect sinusoidal voltage with an RMS
value of 208 volts. Connect that same oscilloscope to your 220 volt single
phase source and you would also see a near perfect sinusoid with an RMS value
of 220 volts. In the US, the line voltage is always given as the RMS voltage,
not the peak voltage.
The peak voltage is larger than than the RMS voltage (for a sinusoid) by a
factor of sqrt(2). In the case of your 220, the peak voltage is actually
220 * 1.414 = 311 volts. The peak voltage between phase A and phase B for
the 208 volt 3 phase system is 208 * 1.414 = 294 volts (a difference of 12
volts RMS and 17 volts peak). The peak to peak voltage is twice the peak
voltage. Your 220 volt line actually swings from -311 volts to +311 volts,
while the single phase of the 208 volt 3 phase system swings from -294 volts
to +294 volts.
The 120 volt phase shift is only seen when comparing any two phases in a
3 phase system. For instance, the phase A to phase B voltage is 120 degrees
out of phase with respect to the phase B to phase C voltage. Likewise, the
phase A to neutral voltage is 120 degrees out of phase to the phase B to
neutral voltage, etc.
Jack
P.S. If you are interested in what is meant by RMS, it stands for "root mean
square". The idea is that if you connected a 1 ohm resistor to a DC voltage
of say 10 volts you would dissipate 10 watts of power. Connect that same 1
ohm resistor across a sinusoidal voltage with a peak value of 10 volts and
you would dissipate less than 10 watts if you averaged the power over one
cycle. This makes sense since the absolute value of the voltage is only at
that 10 volt level for brief moments during the cycle, and is less than 10
volts for most of the cycle. It turns out that for this example, the average
power dissipated is 10/sqrt(2) = 10/1.414 = 7 watts. Hence a sinusoidal
voltage that has a peak value of 10 volts is said to be 7 volts RMS.
I hope this isn't too confusing :-)