So I was wondering what exactly would happen if a residential electric
service (3 wire 240/120 with neutral) lost just the electric company neutral
connection but had a good ground to the neutral bar in the main panel?
Would current flow to the ground connection?
If the load was not balanced between the two hots (only every other breaker
in use at the time [extreme situation]), could the ground wire potentially
carry say the full amperage of one of the hots?
Or in other words, should the ground wire in the main electric panel be
sized to carry the full load of one leg of the service should this situation
happen?
I don't believe I've ever seen an open neutral on a service, where the
ground was able to carry the load, although if it did carry the load, noone
would notice, and I wouldn't get involved. Typically you have lighting and
appliance imbalances, which tip off the property owner to the problem
>
Two 120V circuits turn into a single 240V series circuit, that's what happens.
This is very, very, bad, as it tends to let the magic smoke out of everything
on those circuits.
>
>Would current flow to the ground connection?
Nope.
>
>If the load was not balanced between the two hots (only every other breaker
>in use at the time [extreme situation]), could the ground wire potentially
>carry say the full amperage of one of the hots?
Not unless there's a ground fault.
>
>Or in other words, should the ground wire in the main electric panel be
>sized to carry the full load of one leg of the service should this situation
>happen?
No.
The neutral conductor is the return path for the current back to the
transformer. If the transformer as well as the home had a good grounding
system and soil conditions were right, current would flow through the earth
to the transformer.
If there was not an ideal grounding system in place you could possibly have
220 volts going to circuits that shared a neutral conductor.
The electrical code does not require that your grounding electrode conductor
be the same size as your neutral conductor, which incidentally is normally
smaller than your hot conductors.
Well any one circuit could have normal voltage or have anything
between 0 and 240 volts. I used to work for a photo studio that was
in it's second location. The first one burned up due to this little
problem. The second one also suffered from it on the first floor.
The basement (processing and finishing area where I spent most of my
time, was OK.
Under this conditions you can turn on one light and others may
become brighter or dimmer or some of each. You really don't want this
to happen.
Note. Having a good ground will not help, unless that ground is
also having problems.
Well anyway, that's my long and drawn out story of an open neutral. I
forgot to mention, I took all the documents from the open neutral service
down to the KCPL office in downtown KC, Missouri and collected a check for
one TV and 2 VCRs. They were fried.
steve barker
"Bill" <billnoma...@yahoo.com> wrote in message
news:6cijfmF...@mid.individual.net...
>really slow. After screwing around with it, I decided the drill was
>dying and went to get another one from the back room. That room is
>dark so I flipped on the lights. They were real dim. That's when I
>realized there might be an electrical problem. I took that drill to
>the house and it worked fine. I went back to the garage and plugged
>it into another outlet. As soon as I turned it on, those dim lights
>in the back room got real bright, and a few seconds later they went
>out (they were CFL bulbs). thats when something smelled hot, and I
>found smoke around one of those CFL bulbs. I shot off the switch to
>those lights and got my test meter. I got odd votages all over the
>garage. I flipped on a light on another breaker and it flashed and
>burned out immediately. At that same time the radio in there which
>always comes on when I turn on the lights, got real loud, then quit.
>I flipped on my 240V welder and it worked fine. At the same time I
>noticed the outdoor flood light came on. With the welder on, I
>flipped on soem more lights and they all worked normally. When I shut
>off the welder some lights got real dim, others real bright.
>
If flipping stuff on causes other stuff to blow. I would quit
flipping stuff on. :)
In a three wire (bi-phase) service, must current entering on one hot
wire leaves on the other. Only current that flows in a neutral is due to
imbalance in the load.
A safety ground is not as conductive as the neutral. But it should be
conductive enough so that current does not use other paths. For example,
in one house, the earth ground was completely missing. A neutral wire
broke inside the street transformer. So current took a return path via the
gas meter. When insulators finally broke down, the house exploded.
Homeowner knowledge is quite simple to avert such failures. If
incandescent bulbs change intensity when major appliance power cycle, then
get the problem eliminates. In most cases, that light intensity change is
a minor problem. In some cases, it indicates a threat to human life. At
no time should lights change intensity due to appliance power cycling.
Never ignore the symptom because in rare cases it could be a major human
safety threat such as failed neutral.
> responding to
> http://www.homeownershub.com/maintenance/What-happens-when-electric-neutral-cut-disconnected-315303-.htm
> westom wrote:
> Bill wrote:
>> So I was wondering what exactly would happen if a residential electric
>> service (3 wire 240/120 with neutral) lost just the electric company
>> neutral connection but had a good ground to the neutral bar in the
>> main panel?
> -------------------------------------
> Obviously an earth ground is not as conductive as a neutral wire. But it
> does not have to be in most cases.
>
> In a three wire (bi-phase) service, must current entering on one hot
> wire leaves on the other. Only current that flows in a neutral is due to
> imbalance in the load.
>
> A safety ground is not as conductive as the neutral. But it should be
> conductive enough so that current does not use other paths. For example,
> in one house, the earth ground was completely missing. A neutral wire
> broke inside the street transformer. So current took a return path via the
> gas meter. When insulators finally broke down, the house exploded.
How did it find that path? There has to be a connection somewhere that
should NOT be there. If the neutral is broken the current does NOT
automatically go to the earth ground unless there is an improper connection
as these are supposed to be isolated. In a stove the 240 elements will
continue to function as long as there are no controls that require 120 as
these will all be shut down. That is, a computer controlled stove will
cease to function, but an old fashioned stove with simple controls will
still cook and heat as they use only the opposing hot legs. The neutral is
only used where 120 is required.
>
> Homeowner knowledge is quite simple to avert such failures. If
> incandescent bulbs change intensity when major appliance power cycle, then
> get the problem eliminates. In most cases, that light intensity change is
> a minor problem. In some cases, it indicates a threat to human life. At
> no time should lights change intensity due to appliance power cycling.
> Never ignore the symptom because in rare cases it could be a major human
> safety threat such as failed neutral.
There is often a slight momentary dimming at the moment of startup of a
refrigerator compressor or central air compressor.
I would guess that what he means is that:
A - there was no proper earth ground to the panel and
B - the gas meter was bonded to the ground system of the house which
is connected to the neutral at the main panel.
> In a stove the 240 elements will
> continue to function as long as there are no controls that require 120 as
> these will all be shut down. That is, a computer controlled stove will
> cease to function, but an old fashioned stove with simple controls will
> still cook and heat as they use only the opposing hot legs. The neutral is
> only used where 120 is required.
>
>
>
> > Homeowner knowledge is quite simple to avert such failures. If
> > incandescent bulbs change intensity when major appliance power cycle, then
> > get the problem eliminates. In most cases, that light intensity change is
> > a minor problem. In some cases, it indicates a threat to human life. At
> > no time should lights change intensity due to appliance power cycling.
> > Never ignore the symptom because in rare cases it could be a major human
> > safety threat such as failed neutral.
>
> There is often a slight momentary dimming at the moment of startup of a
> refrigerator compressor or central air compressor.- Hide quoted text -
>
Exactly what I was thinking too. I've seen new construction in $1 mil
homes
where a similar motor load will cause lights to dim momentarily at the
end of
long runs. For example, turning on a shop vac. I've seen that
happen in
many homes. If the standard was no noticeable
change in intensity ever, you'd probably need to rewire most of the
homes
in the US.
ITYM "lights on a different circuit than the appliance." I can't
remember living anywhere where a light on the same circuit as a
microwave for instance wouldn't dim even on a 12AWG, 20A ckt.
nate
Neutral and earth are bonded together @ main panel. So they are not
isolated.
nate
But the earth rod and the transformer ground are not going to carry
enough current to stabilize the load. Loss of neutral between the
house and the service will result in the potential between the two
hots and neutral varying depending on the total load on each side. So
it will be divided just like it is now but not always equally. And
this will affect just about everything in the house as even many 240v
appliances use 120 for some things.
Variation is minimized so that neutral currents do not use other paths
(ie water heater, furnace) to obtain earth via gas pipes. So that higher
voltages do not exist and did not compromise gas line gaskets.
Among many functions of earth ground is to reduce voltages due to a
neutral failure. Had that homeowner reacted properly when lights were
changing intensity (when 120 volt appliances were power cycling). Or had
that homeowner inspected his earth grounds, then his house would not have
exploded.
True. (although I've never seen a "transformer ground" - are houses
now getting four wire service entrances?) My point was, though, that
they are bonded together, so if the ground connection is completely
lost, that unbalanced neutral current will try to find any path it can
to ground, which will likely be either a water or gas line (or both)
nate
Transformers are usually grounded. Houses still have 3 wires. 2 hots
and a grounded neutral.
And exactly where was this home that exploded anyway?
--
The best argument against democracy is a five-minute conversation
with the average voter. (Winston Churchill)
Larry Wasserman - Baltimore Maryland - lwasserm(a)sdf. lonestar. org
The REAL indicator of a failed/failing neutral is lights that "flare"
when a load cuts in, because the heavy load (frdge starting, etc)
causes a low resistance on the one leg, causing voltage to go up on
the other leg.
Typical response from homeownershub to a thread that is almost 3 years old.
> jamesgangnc wrote:
>> But the earth rod and the transformer ground are not going to carry
>> enough current to stabilize the load. Loss of neutral between the
>> house and the service will result in the potential between the two
>> hots and neutral varying depending on the total load on each side.
> -------------------------------------
>
> Variation is minimized so that neutral currents do not use other paths
> (ie water heater, furnace) to obtain earth via gas pipes. So that higher
> voltages do not exist and did not compromise gas line gaskets.
>
> Among many functions of earth ground is to reduce voltages due to a
> neutral failure.
Cite a source that agrees It is not an intended function of earthing
because it is not reliable.
As usual from homeownershub, this question was answered almost 3 years ago.
Among the answers - from gfretwell:
"Back in the olden days when all the homes were connected together by a
solid metal piping system, nothing would happen. Now days you would
end up with an unbalanced service. One side of the panel would have
high voltage and the other would be proportionately low. Dirt is a
terrible conductor and your ground rod is pretty useless as a neutral."
*If* you have a typical metal municipal water supply system the neutral
current can run to adjacent houses and back through their neutrals,
using the N-G bonds at all the houses.
(Unfortunately that wouldn't work for westom because he says that a
metal water pipe can't be used as an earthing electrode.)
There is probably about a post a year here of bright/dim lamps caused by
a bad service neutral.
--
bud--
Which we usually refer to as "neutral" and absolutely DOES carry
enough current to stabilize the load... that's its intended
function. I'm confused at what you are trying to say?
nate
I was replying to the poster that said he had never seen a transformer
ground and asked if houses have 4 wires now. Did I say the service
entrance neutral did not carry a load? No, I didn't.
I was that poster, and yes you did.
"But the earth rod and the transformer ground are not going to carry
enough current to stabilize the load. "
then you said, in response to my post
"Transformers are usually grounded. Houses still have 3 wires. 2
hots and a grounded neutral."
I didn't start off to bust your balls, but now I feel obligated to
because at this point I haven't a clue whether you know what you're
talking about or not.
In short, if you are using "transformer ground" and "neutral"
interchangeably, then you did make an incorrect statement.
nate
Seems to me this is fine but would "a neutral that is grounded" work better?
>>
>>> Which we usually refer to as "neutral" and absolutely DOES carry
>>> enough current to stabilize the load... that's its intended
>>> function. I'm confused at what you are trying to say?
>>
>>> nate- Hide quoted text -
>>
>>> - Show quoted text -
>>
>> I was replying to the poster that said he had never seen a transformer
>> ground and asked if houses have 4 wires now. Did I say the service
>> entrance neutral did not carry a load? No, I didn't.
>
> I was that poster, and yes you did.
>
> "But the earth rod and the transformer ground are not going to carry
> enough current to stabilize the load. "
>
> then you said, in response to my post
>
> "Transformers are usually grounded. Houses still have 3 wires. 2
> hots and a grounded neutral."
>
> I didn't start off to bust your balls, but now I feel obligated to
> because at this point I haven't a clue whether you know what you're
> talking about or not.
>
> In short, if you are using "transformer ground" and "neutral"
> interchangeably, then you did make an incorrect statement.
>
> nate
I thought james was clear and correct.
--
bud--
I didn't. I made 2 statements. In response to your 2 sentences.
First you said you had not seen transformer grounds. Then later you
asked if houses had 3 or 4 wire service.
1. Yes, transformers are usually grounded.
2. Houses have 3 service wires.
I didn't say there was a relationship between those 2 statements. I
didn't say anything about the grounds being able to carry the load. I
didn't comment on what happens if the neutral service line is broken.
You're reading a lot of things into two simple statements. All I did
was tell you that transformers are typically grounded and that houses
have 3 service wires. Quit trying to read things into a post that are
not there. I didn't try to say anything else. You've jumped to half
a dozen other assumptions from my simple comments. If I'd wanted to
say something else I would have said it.
Still not seeing how your initial statement was correct. You stated
that the xformer ground would not carry the unbalanced neutral
current. Isn't that exactly what it is designed to do? I'm not aware
that it is common practice to provide a neutral in transmission lines,
only distribution ones.
nate
Not what I heard him say - but even what I heard didn't make a whole
lot of sense.
>On Apr 1, 2:04 pm, jamesgangnc <jamesgan...@gmail.com> wrote:
It's my understanding the distribution, usually 3 phase, feeds 3
transformers - but be that true or not, each transformer gets 2 power
wires to the primary, and the center tapped secondary has 3 wires, L1,
N, and L2.
Inmany areas it is common practice to run one bare and 2 oinsulated
wires from transformer to service stack when using overhead wire. The
bare wire is sometimes a steel cable and it supports the other 2
(live) wires, and is grounded at the pole and at the service panel.
This is obviously not the only way to do it, but it is fairly common.
Look at inspectopedia.com/electric/Electrical_Ground_Required.htm for
all you ever wanted to know about grounding, bonding, and neutral
conductors.
The "bare" is probably ACSR cable. Aluminum Conductor- Steel Reinforced.
The center strand or strands will be steel for strength and the outer
strands are the aluminum conductor. You may actually see the strands
separated with the steel wire/s attached to a support and the aluminum
strands crimped to an entrance cable neutral.
http://www.sural.com/products/bare/acsr.htm
TDD
<stuff snipped>
<ITYM "lights on a different circuit than the appliance." I can't
remember living anywhere where a light on the same circuit as a
microwave for instance wouldn't dim even on a 12AWG, 20A ckt.>
Thanks for pointing that out. When I added new circuits to the kitchen, I
was sorely disappointed that light on that circuit still dimmed when the
microwave started up. I thought something must be wrong somewhere but
rechecking everything to the point of overloading the circuit with two space
heaters to see if it indeed carried 20A and popped at 25A and it did, so I
forgot about it. Nice to know that it's just what happens. I suppose when
the microwave starts dimming lights on unrelated circuits that you have to
worry . . .
--
Bobby G.
Now you're arguing about my earlier post. If you cut the neutral
coming into your entrance panel and leave the house ground rod(s)
connected, the ground rod(s) will not handle the load originally
carried by the neutral. Ground resistance is too high. Go pound a
ground rod into your yard somewhere and measure the current when you
connect a hot to it.