Thanks for the advice. I may end up doing something similar, but I'm
not sure that using the sprinkler design area would be accurate for in-
racks as I suspect that the roof design requirements for in-racks may
not be based on actual tests but may use "parallelism" or judgement to
arrive at roof design criteria. It would be helpful if one could get
the test data that were used in deriving the in-rack sprinkler
requirements. Fire damage pattern may be helpful.
I have read most of Ingason's research articles but none were for in-
rack sprinkler protection. They are useful to define the fire growth
rate for an unsprinklered fire and correspond to the measurements made
by McGratten for the plastics commodity (Ingason Group 2 if I remember
correctly). One could use Ingason's data for in-rack sprinkler
activation but that will give only the activation and fire size for
the 1st sprinkler. It won't be helpful in estimating the max. HRR. The
FM tech. reports will be most helpful but unfortunately these are not
available in the public domain!
One approach I'm considering is to estimate the limiting fire size for
roof only protection (i.e. max allowable commodity height and max.
clearance between top of commodity and roof sprinkler) by estimating
sprinkler activation time and keeping the HRR rtae constant
thereafter. One can then presumably reason that the fire size will be
smaller for protection with in-rack sprinklers as they would be QR and
have an activation temp. of 68 deg C versus the roof sprinklers with
141 deg C activation temperature. But, I think a smaller fire size
could possibly be more onerous in terms of smoke spread as the smoke
will probably be colder without a too significant reduction in volume
as the height of rise is more dominant that fire size.
On May 18, 8:20 pm, JWilliamson <
williamson.justin.w...@gmail.com>
wrote:
> > height if in-rack sprinklers are installed.- Hide quoted text -
>
> - Show quoted text -