Today I went into the crawl space, and again, when I'm near a certain
section of the gas pipe I smell gas. So I'm pretty sure there is a leak. The
pipes are metal rigid pipe, with a little bit of rust.
I'm thinking DIY repair, but the pipes are rigid and screwed together. In
order to remove one section of pipe, I'd have to turn it which would loosen
it on one end and tighten it on the other end. Are they designed to be
loosen this way, or would I strip the thread on the tighter end? If I can
losen the pipe, then I think adding a piece of pipe tape to the thread and
screwing it back may do the trick, except that the other end may now start
to leak after being overtightened and then loosen again.
If I get a contractor to fix this, what are they most likely to do to fix
this?
The house is 20 years old and the gas pipes probably are as well.
That's totally unacceptable; I'd report that to the utility company. At
least here they're responsible to at least determine unequivocally the
presence/absence of leaks although it's you nickel to repair anything on
your side of the meter.
> Today I went into the crawl space, and again, when I'm near a certain
> section of the gas pipe I smell gas. So I'm pretty sure there is a leak.
> The pipes are metal rigid pipe, with a little bit of rust.
This is too potentially dangerous a situation to leave unattended...
> I'm thinking DIY repair, but the pipes are rigid and screwed together.
> In order to remove one section of pipe, I'd have to turn it which would
> loosen it on one end and tighten it on the other end. Are they designed
> to be loosen this way, or would I strip the thread on the tighter end?
No, and no but you'll never get a joint apart that way, either.
> If I can losen the pipe, then I think adding a piece of pipe tape to the
> thread and screwing it back may do the trick, except that the other end
> may now start to leak after being overtightened and then loosen again.
Indeed....
> If I get a contractor to fix this, what are they most likely to do to
> fix this?
First, have to determine where, _precisely_ the leak is--do you even
know for certain it is the joint itself and not a pinhole failure?
Depends on how far it is back to a union and where the leak is
identified to be and what the root cause is. If they determine it is
the joint itself and it's a long way to a union likely they'll cut the
pipe and insert a union. If it's not too far away they'll take it back
to that point and reassemble and/or replace depending on the conditions
they find.
--
Before you do anything else, take soapy water and find the leak
if there is one, it may be in a place that isn't hard to fix.
check all the fittings and pipe as well, it is unlikely the leak
is in the pipe but not impossible. The pipes actually look good
for 20 years. The first place to look for a suspected leak
would be where the pipe comes through the foundation, corrosion
will be worse there than anywhere else.
basilisk
You crawl under there with a spray bottle of soapy water and spray the
joints and look for leaks. If you can't find the leak (if there is a
leak) you cap all the ends disconnect from the meeter and do a pressure
test and once again with more air pressure on the lines, you crawl under
the house with the spray bottle of soapy water. If it's leaking at a
joint then you have to decide if you want to start unscrewing the pipes
or cut one out and put in a union. It's a lot fun. Make sure the
pipes are hung properly so they don't sag or put stress on the joints.
Beware, if the gas company does find a leak they are apt to leave
with your gas meter in the back of their truck.
Well, the first thing thing that comes to mind is that living in a
house with a suspected gas leak for "several years" is, well, stupid,
but apparently you survived long enough to post your question.
If it were me, I would have *insisted* that the utility company do a
proper check with a sniffer to determine if there was a leak or not.
If I were you, I would *insist* upon that before I touched a pipe or
called a contractor.
The next question is this: Is there a shutoff to this section of pipe
or does it come directly from the meter? If there is no shutoff, and
your gas meter is anything like mine, you're going to need to get the
utility company involved anyway. Unless you plan to fix the pipe
"live" (a very stupid idea) once you shut the gas off at the meter,
you'll need to call your utility company to have them turn it back on.
At least, I do. The meter locks itself out and the utility company has
the tools to turn it back on.
Finally, in most cases, you'll need to go to find a union to remove
any section of pipe. All junctions are going to be threaded the same
way, so you can't just unscrew one end have the other end unscrew
also. Another option is to cut the section and insert a union.
In any case, you really should get the utility company out there, if
for no other reason than to get some decent service for all the money
you've given them over the years.
If it's on the house side of the meter, where I live it's the homeowner's
responsibility.
> james wrote:
>
>> I smell a small natural gas leak in my crawl space. I think it's
>> been that way for several years.
I would definitely fix such a leak. However, it is not an imminent
emergency if the crawl space is ventilated. Natural gas only becomes
explosive when the concentration in air is above 4-5% (and below
15-17%), and a small leak in a ventilated crawl space will never build
up that much.
>> Instead, he looked at the gas meter for a few minutes and decided
>> that there is no leak, and left.
This can be an acceptable method to check for a leak but it takes
longer than a few minutes. It requires that all gas appliances be
off. If any of them use a standing pilot, you have to close the shut
off valve to that appliance and relight the pilot when finished.
Then you use a piece of tape and align one edge of the tape exactly
along the pointer dial on the least significant dial (the one that
turns fastest). Come back in a couple hours and see if the pointer
has moved. If it hasn't, you don't have a leak.
> Depends on how far it is back to a union and where the leak is
> identified to be and what the root cause is. If they determine it
> is the joint itself and it's a long way to a union likely they'll
> cut the pipe and insert a union.
Just an FYI, the plumbing codes I am familiar with only allow unions
at accessible locations, such as the gas meter and at an appliance.
So in a crawl space the proper connection to use is a left/right
coupling, which is a nipple/coupling combination which is left-hand
threaded. That way you can rotate the coupling in one direction and
simultaneously tighten (or loosen) both ends.
Cheers, Wayne
now that doesnt sound too bad but natural gas is at most a couple PSI.
But the required pressure test is 75 pounds. This high pressure finds
leaks that never leaked before it literally creates leaks.
Around here with rusty pipes the plumber will mosty likely want to
replace ALL the gas lines. Cant say I blame them just one tiny bit of
rust allows a leak at 75 pounds and they must start all over, at their
expense......
I would go find the leak with soapy water before proceeding.......
Once you know where it is it might be repairable, if the lines are
rusty you will need them replaced
Well, we don't know much (as in anything) about that here, do we? And,
if it's been leaking for years, there's no telling for sure that it
won't worsen quickly, either, depending on what the root cause might be.
You can make any judgment you wish about the severity of the situation;
I'm not about to make light of any such incident from afar...
--
> But the required pressure test is 75 pounds. This high pressure finds
> leaks that never leaked before it literally creates leaks.
They required the test at 15 psi here in Seattle.
Yep, thats what they do. Wife called the gas company about smelling
gas in the garage. She didnt want to wake me up at 10AM given Im a
shift worker. No hot water for 10 days, $400 dollar plumber bill to
tighten the flare coupling on the water heater.
Jimmie
> Beware, if the gas company does find a leak they are apt to leave
> with your gas meter in the back of their truck.
Thats the way they work here in LA as well... and they make a big stink
over re-inspection before reinstallation of the meter.
Oh, and of course, all at your expense, and on their 'schedule'.
Erik
No they won't. They'll turn off the gas until the owner certifies the leak
has been fixed.
YOU have to find the leak. Or pay someone to do it. Couple of points:
1. It may not BE a leak. While Mercaptan has a distinctive smell, the odor
may be coming from something else entirely. Did one of the previous owners
of the house disappear under mysterious circumstances?
2. Use some cardboard or similar to block off as much air-flow as possible
thereby increasing the concnetration of gas under the house. Does the
intensity of the oder increase?
3. When you do find the leak, remember natural gas pressure is measured in
OUNCES/sq in (about four ounces). It doesn't take much to stop such
pressure: Heck, a Band-Aid would do it.
> Previously I had called the utility company to check.
>The guy refused to go into the crawl space. Instead, he looked at the gas
>meter for a few minutes and decided that there is no leak, and left.
Call the local fire marshall and ask him for a residential inspection.
He can use this as a training exercise for new recruits.
He should really know how the local utilities operate and function.
*
_Fire Marshall Bill in National Fire Safety Week Jim Carrey_
Gas is low pressure so epoxy should fix it depending on the leak, use
soapy water to find it.
Use soapy water to find it. fixing a loose connection mid-stream
requires a pipe union - the difficult part is removing the original
pipe without causing a spark. A cut-off wheel is NOT the answer - a
hacksaw can cause a spark, but if you flow water over the cut it is
extremely unlikely. Spin out both ends, buy 2 peices half the length
and a pipe inion, or rethread the cut ends if you have the equipment
available. Use teflon pipe dope on the joints - NOT TEFLON TAPE..
The proper union is usually referred to as a "ground joint union"
which has accurately machined or ground taper that does not require
pipe dope or gaskets.
They are legal if accessible, although code calls for them only at the
meter and at consuming devices.
Shut the gas off first. The gas company will weld on the pipes if the gas
is shut off.
I'd not use a cut off wheel in a crawlspace anyway, but I'd use a hacksaw or
reciprocating saw.
Teflon tape is okay, you just have to use twice as much (or yellow Teflon
tape which is twice as thick).
But pipe dope is better; it actually seals the joint rather than just
lubricating it.
for better sealing use both tape and dope
The leak might not be from his home, I had a friend with a leak that
was actually from the main line, and followed back from 1/4 a mile away
> for better sealing use both tape and dope
Nope. That isn't redundancy, that's counterproductive. The presence of
each will interfere with the effectiveness of the other.
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"Smitty Two" <prest...@earthlink.net> wrote in message
news:prestwhich-677B9...@news.eternal-september.org...
http://www.bramec.com/brands/detail.asp?cat=2036&ManuID=bramec
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"james" <nos...@nospam.com> wrote in message
news:i0iirq$q5p$1...@speranza.aioe.org...
The companies that make tape for gas lines must be going broke then, what
with all that unsold inventory.
Not according top a friend a master plumber who has 12 trucks on the
road.....
He says tape gets a occasional leak.
Dope gets a occasional leak
The combo almost never leaks:)
When your paying nyour techs by nthe hour on fixed price jobs thats
important
Teflon tape is NOT recommended for gas, because if any of it "strings"
off inside the pipe it WILL block orfices - causing untold problems.
If you really know what you are doing, you CAN install tape so that it
cannot "string off" - but you really DO need to know what you are
doing. Teflon paste works much better, is much simpler, and will not
cause a problem unless you REALLY screw things up.
I know for a fact that in SOME areas, tape on a gas pipe will cause
an inspection failure and the gas will NOT be turned on untill the
tape is removed and the pipelines cleaned out.
What planet are you from ?
Every plumber I have ever seen fix existing gas piping NEVER starts
disassembling the entire system from the meter back to where the
leak is... They sacrifice a length of pipe either where the leak is,
or
in a leak adjacent area where it is easier to work and REPLACE
the piping including the section they cut to disassemble...
Remember, gas piping can be cut and threaded to any length
needed... It just takes a skilled person to see where the easiest
point of attack to fix the problem is... It is NOT taking every
length
of pipe and fitting out starting from the meter, that is patently
ridiculous...
~~ Evan
>>
>Teflon tape is NOT recommended for gas, because if any of it "strings"
>off inside the pipe it WILL block orfices - causing untold problems.
>If you really know what you are doing, you CAN install tape so that it
>cannot "string off" - but you really DO need to know what you are
>doing. Teflon paste works much better, is much simpler, and will not
>cause a problem unless you REALLY screw things up.
Well, that may be how SOME people think of it, but CERTAINLY not ALL.
There are MANY jurisdictions where tape is COMMONLY used WITHOUT
problems. What do YOU think of THAT?
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"Thomas" <cano...@yahoo.com> wrote in message
news:03e1de31-ad05-4be3...@a1g2000vbl.googlegroups.com...
YOU might find THAT SOME teflon TAPE is suited for GAS pipes. Have a
LOOK and maybe you'll BE able to learn some.
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
<cl...@snyder.on.ca> wrote in message
news:cths26188kdhj7rip...@4ax.com...
THE techs around MY area TELL me that TEFLON paste isn't good, beCAUSE
it dries OUT and leaks, LATER.
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
<cl...@snyder.on.ca> wrote in message
news:jnhs26t840c0usa2l...@4ax.com...
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"Vinny From NYC" <vi...@qzyqzy.net> wrote in message
news:rkms26drmsr56j63v...@4ax.com...
Ineffective union influence, laissez fair regulations (if any), severe lack
of nanny-state oversight.
Why not a bit of flexible metallic hose instead of a union?
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"HeyBub" <hey...@NOSPAMgmail.com> wrote in message
news:3OGdnZzyONHU4LPR...@earthlink.com...
Over time it can develop leaks if it is flexed enough. Check your local code
though. Some used to say no flex except for stoves, others now want flex
because of potential seismic movement that could break regular pipe joints.
.
If you can get away with it where you are, and you don't screw it up,
more power to you.
Can't do it here if you are getting an inspection, so I just use pipe
dope, even when I'm NOT getting an inspection. Hate to have someone
else working on it later, needing an inspection, and having it failed
and come back on me. Ain't going to happen, buddy.
Do tit once, do it right.
>I THINK that CLARE must live in a DIFFERENT part of the COUNTRY from
>you and I, and THAT Clare has a different EXPERIENCE.
> http://www.google.com/products?q=gas+teflon+tape+&hl=en&aq=f
Used to also be you could not use galvanized fitting on NG lines here
- but now you CAN.. Some inspectors still don't like it, but it is now
legal in some areas.
It's possible the yellow tape MAY pass here now too, but when my
furnace was replaced about 3 years ago, it was still not allowed - the
whole job was done with pipe dope - just like the water heater 8 or
more years ago. The guy doing the furnace inspection said if there was
ANY teflon tape visible he could not turn the gas back on - period -
end of story.
It's been a few decades but I've fit miles of pipe when I worked in
chemical plants back in the 70s. Threaded pipe up to 2" and flanged up to
12". IMHO using both tape and dope would be a waste of time. Applied
properly and installed correctly, neither will leak.
--
When the game is over, the pawn and the king are returned to the same box.
Larry Wasserman - Baltimore Maryland - lwasserm(a)sdf. lonestar.org
I've ALSO found that the LOCAL inspector may be RIGHT or WRONG, but on
some THING like teflon tape, IT IS easier to do it like the local
INSPECTOR wishes. NATURAL gas is low enough PRESSURE that either ONE
is likely to SEAL.
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
<cl...@snyder.on.ca> wrote in message
news:989t269ir9s4og6mb...@4ax.com...
On Fri, 2 Jul 2010 19:00:11 -0400, "Stormin Mormon"
Used to also be you could not use galvanized fitting on NG lines here
> I THINK that CLARE must live in a DIFFERENT part of the COUNTRY from
> you and I, and THAT Clare has a different EXPERIENCE.
> http://www.google.com/products?q=gas+teflon+tape+&hl=en&aq=f
Clare lives in Canada, Stormy. He regularly avoids mentioning that when
speaking of codes and practices.
>I like BLACK iron pipe BECAUSE it is visibly different THAN water
>pipe. So, YOU can tell by JUST looking which ARE which.
>
>I've ALSO found that the LOCAL inspector may be RIGHT or WRONG, but on
>some THING like teflon tape, IT IS easier to do it like the local
>INSPECTOR wishes. NATURAL gas is low enough PRESSURE that either ONE
>is likely to SEAL.
Up here they really like it if you paint the gas pipes yellow. IF
there is also galvanized water piping in the building.
Other than industrial/commercial sprinkler systems, galvanized water
piping is pretty much extinct around here.
Au Contraire, mes amis - I very often mention "up here in Ontario" or
other references to my location.
Waterloo Ontario - home of the RIM Blackberry, Open Text, Sandvine
Systems, MKS, and a slew of other world renouned technology companies.
> On Sat, 03 Jul 2010 10:40:54 -0700, Smitty Two
> <prest...@earthlink.net> wrote:
>
> >In article <i0lr4f$9t7$1...@news.eternal-september.org>,
> > "Stormin Mormon" <cayoung61**spamblock##@hotmail.com> wrote:
> >
> >> I THINK that CLARE must live in a DIFFERENT part of the COUNTRY from
> >> you and I, and THAT Clare has a different EXPERIENCE.
> >> http://www.google.com/products?q=gas+teflon+tape+&hl=en&aq=f
> >
> >Clare lives in Canada, Stormy. He regularly avoids mentioning that when
> >speaking of codes and practices.
> Au Contraire, mes amis - I very often mention "up here in Ontario" or
> other references to my location.
Yes, I know you mention it frequently, but often fail to mention it when
it would be most appropriate to do so: when speaking of "normal
practices" or code issues, this thread being one example.
--