Sounds like there is a vent that is partialy closed, or fully closed.
Double check if all the vents are opened.
Usually, I get that sound if I close one of the vents in a room that
is suplied by the main trunk line.
Mikepier wrote:
> On Oct 12, 12:11=A0pm, kjirstingraham_at_yahoo_dot_...@foo.com (twinmom)
> wrote:
>> Our house is 5 years old and we have a trane furnace (80%
>> efficiency) tha=
> t
>> is the same age. =A0When the blower turns on (whether a/c, heat or
>> just
>> fan), you can hear a faint high pitched whine coming from each of
>> the air
>> vents (not the return vents) in the house. =A0It starts the second
>> the
>> blower turns on and stops as soon as the blower turns off. =A0The
>> closer =
> the
>> vent is to the furnace, the louder the noise, e.g. our kitchen air
>> vent i=
> s
>> just above the furnace and it is loudest there. =A0We've had the
>> furnace
>> installer out several times and they say everything is normal.
>> =A0But the
>> noise is constant and annoying. =A0The high pitched noise goes
>> away when =
> the
>> furnace panels/doors are removed - particularly, the solid metal
>> panel
>> that covers access to the fan. =A0The installer cut a new return
>> vent in =
> the
>> metal duct that drops down next to the furnace unit in the
>> basement
>> (thinking we just needed to slow down the air flow in the system),
>> but
>> that did not correct the noise. =A0So he left the panels off the
>> furance =
> and
>> duct taped an air filter over the opening. I don't think the
>> company
>> really has any other solution. =A0Any thoughts on how we can get
>> rid of t=
> he
>> noise and get the panels back on our furnace? =A0Is it safe to
>> leave the
>> panels off and/or will it cause damage to the furnace? =A0I'm
>> pretty hook=
> ed
>> on this temorary fix given that it alleviates the noise, but we
>> can't
>> leave it like that forever.
>>
>> -------------------------------------
>> Twin Mom
> Sounds like there is a vent that is partialy closed, or fully closed.
> Double check if all the vents are opened.
> Usually, I get that sound if I close one of the vents in a room that
> is suplied by the main trunk line.
All of the vents are open. We've also gone around the house and checked
each of the return grills to make sure the sound wasn't coming from a
vibrating fin. No luck. This is definitely a noise coming from the unit
itself that emanates through the ducting and out of each of our air vents.
-------------------------------------
Twin Mom
What about the other panels?
Always had the noise for 5 years?
Air passage or bearings are the likely culprit.
Depending on frequency, your repairman might not even hear it.
I suppose the load on the blower due to pressure differentials could
cause a bearing to squeal.
Electronics can squeal, but that doesn't seem to fit your problem.
Or maybe some harmonic vibration from a panel, which might be cured by
gasketing material.
The load question might be answered by blocking return vents.
That could duplicate what leaving the panels on creates in terms of
air pressure, though you weren't clear on whether the panels have an
effect on that.
On my furnaces most access panels have no effect on air flow.
Probably not related, but I thought I had a blower bearing going bad
when I had a repairman replace my furnace motherboard.
Wasn't real high pitched, more of a rumbling.
Didn't even mention it to the repairman until he heard it and made an
adjustment with a wrench.
Then I noticed it was gone, and he told me what he did.
Different furnace than yours though.
You might get a different repair man in, or tinker with the panels.
For locating sound sources get a mechanics stethoscope.
They're cheap, and might get you close to the source.
I love this kind of problem, at least when somebody else has it, so
keep us posted.
--Vic
Do you have a drop-in filter right next to the blower?
I used to get a high-pitch whistle around the filter slot, which could
be heard in other rooms.
I keep a wedge of wood shoved in the filter slot (on the intake side)
which pushes the filter away from the return trunk and towards the
furnace. Stops the whistle completely.
It seems to me you need to either increase the size of the entire
return (which is what the stopgap solution effectively does), and/or
perhaps muffle that area by stuffing some loose insulation in there
followed by an air filter to make sure it stays in place.
I think the cross-section of the return should be in the same ballpark
as the total of the cross-sections of all the ducts away from the
furnace (although there's significant leeway).
The Stucco site is not a help forum, it's an
*advertising* forum that invades real forums
(like "alt.home.repair", part of "usenet")
parasitically in order to generate free
advertising for itself, which continually
advances its search engine placement, thereby
increasing its own revenue through its click-
through advertising commissions.
So the first thing you should do is write them
an email and tell them to quit spamming.
Then try to find your way here through proper
channels. Please do a google search on "Usenet"
and post the regular way.
--
Christopher A. Young
Learn more about Jesus
www.lds.org
.
"twinmom" <kjirstingraham_...@foo.com> wrote in message
news:5d3fa$4cb48897$45499b77
When we replaced the furnace in my daughter's condo, and relocated
it, the installer recommended the intake plenum (duct) be 15-30%
larger than the outlet. I think we ended up about 20% larger. This was
a Lennox 84? %.
My Tempstar was installed to the original ducting, which appears to be
equal sized, but the total outlet and inlet sizes could still be
different. It whisles when I have the filter out for cleaning
sometimes - but quiets right down when the filter is installed.
Do you think it is an "air whistle" or could the blower motor need
oil???
Sounds like there is something in that return ducting that is causing
it. A stray piece of something sticking into the air flow. Or a
small leak. Taking the cover off and puting a filter over that
opening means that almost all the return air is going directly into
the air handler. A stethscope might help you pin it down closer but
I'm thinking you are going to have to open up that return system. How
much of the return system is hard duct verses flex pipe? I'd look in
the hard duct first. Get some metal tape and start sealing seams from
the inside.
Here's my experience. Yours is probably different, so take it for what
it's worth. I had a furnace blower go bad there the spot welds, holding
the blades in place on the blower wheel, had all loosened up. It
started as a quiet sizzling noise, but got louder and louder as the
days/weeks went by. I was able to quiet it down by reducing the speed
... it was a plain 4 speed motor, not variable speed, like many newer
units. Anyway, I replace the blower wheel. The new wheel ran quiet.
And, once I got the old one out, if I would hold one end with my feet,
and twist the other with my hands, you could definitely hear small
squeaking noises coming from the weld areas. As I said, probably not
the same, but maybe?
I had the same issue with the eductor fan on my Tempstar. Dealer who
installed it had gone T.U. - local dealer had no parts in stock and
I'd have to pay for the parts and labour up front (over $300 IIRC) and
the POSSIBLY get up to $200 back.
I took the fan out and brazed the blower weheel web to the hub. It's
been quiet ever since (about 6? years now)