I plan to install a 100amp breaker into my existing FPE (200 amp
service) box to service a new breaker box (also 200 amp service), then
rewire the house to the new box, and because of other reasons we will
be moving the incoming service to the new box. Note: I say "we" but
in this case "we" means electricians and the electric company as far
as they need to be involved.
Anyway, if anyone is familiar with the FPE Stab-Lok load center, I'd
appreciate some advice about the 100amp breaker. I've found the
NA2100 (Type NA, 2 poles, 100 amp) breakers, but I'm not sure if this
is the one I need for this breaker box or not. My existing breakers
are type NC. Apparently the type NB breakers bolt in ("B" is for
"Bolt" obviously). I have found several of the 30amp or less breakers
as type NC, but anything over that seem to be type NA. I just want to
know if the NA2100 will work in my box...or if you need more
information to make that determination.
Thanks,
Charlie
I'm not exactly understanding why you want to feed the panel from the
existing FPE panel, if you're moving the service to the new panel, unless
this is just for a temporary setup. I wouldn't replace the FPE equipment out
of fear of fire. I would replace it simply because it's garbage. I believe
the difference between the NA and NC is that the NA, possibly because of
it's 100 amp rating stabs into four places on the buss, as opposed to just
two
I _believe_ all NA and NC are allowed in any FPE panel that takes one or
the other, but the real answer is on the sticker on the inside of your
panel -- it will list the allowable breakers it accepts.
I'm assuming this is intended simply as a temporary feed to the new
panel? Be sure you use adequately-sized cable to feed it -- don't try
to "get by" w/ something too small just because it's temporary and
short-time expected...
--
Yes, it's only temporary. Rather than replacing everything at once,
it will let me rewire the different circuits as I can, and would
ensure minimal downtime when it comes time to move the service to the
new box. The old FPE is history after that.
Thanks for the response.
-Charlie
You're correct that it's listed inside the box...I found that after
I'd sent this question to the group. It accepts NA, NC, & 2B
(whatever that is?) breakers. And yes, I've spoken with an
electrician and will be using 2 gauge 4 conductor (2 hots, 1 common, 1
ground) copper from this breaker to the new breaker box.
Thanks a bunch.
Charlie
I think it's a waste of time and those FPE breakers are more expensive than
other brands. Many service changes to single family houses are done in a
day. Unless there is some other reason to temporarily feed a new panel I
suggest that you start talking to qualified electrical contractors about
what you are trying to accomplish. If you don't want to swing over the old
circuits to the new 200 amp panel, have the electricians run a feed from the
new panel to the old panel thereby making it a sub panel.
It might be cheaper, and certainly less trouble, to deal with your fears.
There may even be a twelve-step program available.
John,
Excellent suggestion! Actually I have spoken with a couple
electricians, but they mostly just agreed that what I had planned
would work and was a good way to approach it. I guess that my idea
was the reverse of what you suggested...make the new panel a sub-
panel, rewire, then switch the service. Moving the service and then
making the old one a sub-panel I think is indeed a better approach.
It'll be much easier to find the appropriate 100amp breaker for the
new panel, and I'd certainly trust it much more than another old Stab-
Lok double-pole breaker in the FPE breaker box.
Thanks for the new approach.
Charlie
HeyBub,
I'm afraid that I have a fear of twelve-step programs.
Charlie
or install the new main panel and feed each new breaker to a feed in
the old FPE box, after stripping out all the old breakers and
hardware.
just use the old box as a pass thru.
i have thought about doing that at a home, since the wires are too
short and a garage door track obstructs the area,.
better one pass thru box than 10 or 12 junction boxes.eater smaller
less work
Well, back to plan one.
About your plan to put a 100-amp breaker in the existing box and feed a
200-Amp box from that:
I suspect pulling 100 Amps through one breaker will melt the stab-on bar.
I'd replace the existing box with a new, 200A one. You won't have to splice
wires either.
Just because it'd be a 100 amp breaker doesn't mean that 100 amps will
be drawn through it...but that's mute at this point anyway.
If I trusted the wiring AND didn't want to move the service entrance,
I would indeed do a simple breaker box replacement. The new plan as
per John's suggestion is to install the new 200Amp breaker box, have
the service moved to the new breaker box, install a 100Amp breaker in
the NEW breaker box (instead of the old one), and use that breaker to
feed the old Federal Pacific breaker box until I can rewire everything
to the new box.
As a benefit of doing this, when I remove the old FPE breaker box,
I'll replace it with a 100Amp sub panel and feed it with the same
100Amp breaker that temporarily fed the old FPE box. Because some of
my heavier wires feeding ranges, dryers, etc are already there and are
somewhat more recent wires than the rest of the house, I'll just
connect those to the 100Amp sub panel and won't have to rewire those.
The rest of the house can be rewired room by room as I get time (it's
definitely a priority!).
I'll definitely consult with an electrician(s) as for the components
to use and how to load each circuit & leg in the box, but I'll also
save a few $$$ by breaking my own back and dropping my own wires.
Thanks again everyone for their suggestions!