Hayden-
For me, I see many of these difficulties stemming from the ambiguities of the label under which we are working to build 'the best buildings in the world'. For the most part, this open-ness has been utilized as a strength.
As Bronwyn states, there are 40,000+ Passive House structures in the world. Are 100% of these heated with the equivalent of a hair dryer? Clearly not. As only about 10% of them are even 'Certified' by some agency, how many are even designed/constructed to one of the handful of Passive House metrics?
Looking at those 40,000, how many are in jurisdictions which don't utilize the parameters of the Passivhaus Institute aka the Passive House Institute? I'd posit that there are a good percentage, yet they are included in the message that this is a successful building movement (which it is, thankfully).
I find it disingenuous to say that the PHIUS+ Standard is not a Passive House Standard when there are many and changing definitions, even from your chosen authority. Yes, the parameters and defining metrics have been designated at differing touch-points, but they’re all built around this core idea: utilizing passive measures to reduce space conditioning needs by up to 90% and then using this terrifically effective strategy as a part of reducing total building energy needs by game changing levels.
The ship of accepting a more open definition of ‘Passive House’ sailed from the European docks years ago. As I stated in an earlier post, ask the Belgians, Swedes, Norwegians, Finns, Swiss, and the Italians. Tossing out platitudes about how PHIUS is undermining the idea of Passive House and the numbers as defined by the entrusted German Scientists (I almost feel like they are being held up as the sacred Founding Fathers) is by design divisive. This resonates more as a protectionist move than an analysis of how to address energy consumption and build this movement as a whole.
To be clear, the basis of the recent Standard Adaptation is founded in both science and building practice and it is intended to move ‘the best buildings in the world’ further forward.
--
You received this message because you are subscribed to the Google Groups "Passive House Northwest" group.
To unsubscribe from this group and stop receiving emails from it, send an email to PassiveHouseN...@googlegroups.com.
For more options, visit https://groups.google.com/d/optout.
Adam,
Thank you for your agnosticism. You are a wise man and I respect you. Hundreds have asked PHIUS to use its competitor's name. Keeping space between the Passive House and PHIUS allows for choice and fair competition. I think this benefits all of us.
Is it unreasonable to expect PHIUS to succeed on its own merits and distinguish its programs with a different name?
Yours,
Hayden
Passive House = heating your house with a hair dryer
PHIUS+ = powering your house with PV
Passive House = heating your house with a hair dryer
PHIUS+ = powering your house with PV
Passive House = heating your house with a hair dryer
PHIUS+ = powering your house with PV
André Harrmann | Dipl.-Ing.(FH), MHP, CPHD, LEED AP
Green Building Consultant | Harrmann Consulting
Director | Canadian Passive House Institute West (CanPHI-West)
Director | North American Passive House Network (NAPHN)
Project Manager | University of British Columbia (UBC)
web: 15kwh10w.com
...
Hi Ryan,
PHIUS+ is not my forte, but no one else has jumped in, so I'll take a shot. I'm sure the crowd brain will correct me where I'm off.
My understanding is that you can't do the comparison that you are attempting without correcting for the differences in floor area metrics (TFA and iCFA), and internal-heat-gain assumptions.
In order to compare Passive House's TFA with PHIUS's iCFA, you have to add in interior partitions and doorways, stairs, a percentage of basements and store rooms, etc.
In the case of the Prospect Street Passive House, I found that, the conversion from TFA to iCFA was 150%. As Dan has point out, this number will vary from project to project. For a house with no stairs and no basement, the numbers would be closer. But, taking the Prospect St. House as an example, you would assume 2,000 s.f. for the Passive House version, and 3,000 s.f. for the PHIUS+ version. Alternatively, you could leave them both at 2,000 s.f., and make the correction in the PHIUS+ heating demand number: 5.1 x 1.5 = 7.65. In your example this bumps the PHIUS+ AHD to 15,300. Again, this is using Prospect St. as an example - other projects would be different.
An additional correction would be needed because PHIUS+ assumes a higher internal-heat-gain number that is typically more accurate for the U.S. Accuracy is good; however, for the purposes of your comparison, it adds free heat to the PHIUS+ scenario that is not present in the Passive House scenario. In order to compare the two standards, you need to add the same amount of free heat to the Passive House. This would reduce its AHD. I don't know what the PHIUS+ IHG numbers are, so I can't do this part for you, but the equation would be: Passive House AHD - (PHIUS+ IHG x iCFA) - (PH IHG x TFA). Or, at least I think so, but I'm getting tired. At any rate, you get the point.
-Hayden
From: Passive...@googlegroups.com [mailto:Passive...@googlegroups.com] On Behalf Of Ryan Abendroth
Sent: Friday, May 1, 2015 4:56 PM
To: Passive...@googlegroups.com
Subject: Re: What does PHIUS want?
Longtime lurker here.. well maybe I have posted a few times.
Bronwyn Barry, CPHD
--
You received this message because you are subscribed to the Google Groups "Passive House Northwest" group.
To unsubscribe from this group and stop receiving emails from it, send an email to PassiveHouseN...@googlegroups.com.
For more options, visit https://groups.google.com/d/optout.
--
You received this message because you are subscribed to the Google Groups "Passive House Northwest" group.
To unsubscribe from this group and stop receiving emails from it, send an email to PassiveHouseN...@googlegroups.com.
For more options, visit https://groups.google.com/d/optout.
--
Bronwyn Barry, CPHD
Certified Passive House Consultant
Director - One Sky Homes
m: 415.819.7978
t: @passivehouseBB and @oneskyhomes
--
You received this message because you are subscribed to the Google Groups "Passive House Northwest" group.
To unsubscribe from this group and stop receiving emails from it, send an email to PassiveHouseN...@googlegroups.com.
For more options, visit https://groups.google.com/d/optout.
--
Adam Cohen
Certified Passivhaus Consultant - North America and Europe
Registered Architect MD, VT, NH & CO, LEED AP, NAHB Green Professional
Design/Builder of the First US Passivhaus Public School Building
2012 VSBN Green Designer of the Year
2013 Green Builder Green Home of the Year
EMAIL POLICY
In an effort to increase productivity, I answer email as follows:
Monday - Friday
Sign up for our components newsletter here: http://eepurl.com/2MTDn
Web site: www.structuresdb.com
Commercial Passivhaus information: http://passivscience.com/
Factory Built Passivhaus Component information: http://www.passivstructures.com/
Passivhaus information: http://www.passivehousedesign.us/
More Passivhaus info: http://www.viking-house.us/
High Performance Design: http://quantum-architects.com/
540.312.8400 (cell)
--
You received this message because you are subscribed to the Google Groups "Passive House Northwest" group.
To unsubscribe from this group and stop receiving emails from it, send an email to PassiveHouseN...@googlegroups.com.
For more options, visit https://groups.google.com/d/optout.
--
Bronwyn Barry, CPHD
Certified Passive House Consultant
Director - One Sky Homes
m: 415.819.7978
t: @passivehouseBB and @oneskyhomes
Me? I suspect the job is better left to those of you with high geek credentials. What is the goal of the study?
By the way, what is the conversion factor for PHIUS+ IHG to Passive House IHG? I confess, I don't even know what the Passive House IHG number is.
-Hayden
From: Passive...@googlegroups.com [mailto:Passive...@googlegroups.com] On Behalf Of Adam Cohen
Sent: Monday, May 4, 2015 4:20 AM
To: Passive...@googlegroups.com
Ryan,
Here is what I found for internal heat gains:
"Compared to PHPP calculations, the MEL/Lighting and internal heat gain increase incorporated here causes about a 1.5-2.0 kBtu/sf.yr reduction in modeled annual heat demand and increase in cooling demand. That is, the same building “would have” modeled with higher annual heat demand under PHPP assumptions."*
So, for this back-of-envelope comparison, this suggests we can add about 1.75 kBtu/sf to the PHIUS+ AHD. For comparison purposes, this yields a Passive-House-adjusted PHIUS+ AHD of
<(PHIUS+ Annual Heating Demand) x (TFA conversion factor)> + (delta Internal Heat Gain)
(5.1 x 1.5) + 1.75 = 9.4 kBtu/ft2yr
PHIUS Tech Committee: am I getting this right? If I'm off track, somebody please correct me.
-Hayden
*(Wright , Klingenberg, Pettit: Climate-Specific Passive Building Standards, p.31, Building America Report - 1405, March 2015)
Thanks Adam,
You are right, there are a lot of other things going on. Also, I think we get back to the long vs. high-jumpers thing. If I've understood correctly, you are excited about total-building energy use - obviously an important and honorable focus. My principal interest is: enclosure performance. To me, as well as energy use, heating demand is a proxy for the quality of the building. I think it also says a lot about a building's resilience and dependability. As a bonus (while acknowledging the contrary opinions of some on this forum) the academic literature suggests that efficiency measures may be a lot more effective than alternative generation, with respect to limiting CO2.
Of course, heating load is at least as good a measure of enclosure quality and resilience. In fact, it's an even better one. But my experience in the maritime Northwest suggests that peak heating events here are uncommon and tend to occur when people are in bed and unconcerned about the room being cooler. Also, when peak loads are an issue, with a high-performance enclosure, they can be addressed with a very small amount of auxiliary heating. This has lead me to conclude that designing for peak load, though elegant, may be unnecessary. That said, I still have hope that passive technologies will evolve, beyond Passive House, to true no-power enclosures.
-Hayden
From: Passive...@googlegroups.com [mailto:Passive...@googlegroups.com] On Behalf Of Adam Cohen
Sent: Thursday, May 7, 2015 5:23 AM
To: Passive...@googlegroups.com
Subject: Re: Response to Ryan
Hayden, it is a bit more complex then that in real life.
Since Adam is coming up with similar requirements for PHIUS+15 and Passive House in CZ4, maybe I'm missing something? For the Seattle CZ4 example, I came up with a PHIUS+15 AHD of about double that of Passive House (9.4 vs. 4.75 kBtu/ft2yr). Wouldn't a similar calculation for estimating peak heating load differences apply:
<(PHIUS+ Peak Heating Load) x (TFA conversion factor)> + (delta peak-load Internal Heat Gain)
= (3.4 BTU/ft2hr x 1.5) + delta IHG
= 5.1 BTU/ft2hr + delta IHG
I don't know the PHIUS+ peak-load IHG assumption (0.51 BTU/ft2hr for Passive House), but even ignoring that, PHIUS+ is about 160% of Passive House (5.1/3.2) for this example.
Moving it from Seattle to Blacksburg, VA (the place I lived in the other CZ4), I come up with a PHIUS+ heating demand of about 190% of Passive House (9.1/4.75):
<(PHIUS+ Annual Heating Demand) x (TFA conversion factor)> + (delta Internal Heat Gain)
= (4.9 x 1.5) + 1.75
= 9.1 kBtu/ft2yr
Similarly, I get a PHIUS+15 peak load of about 180% of Passive House (5.85/3.2):
PHIUS+ Peak Heating load
= (3.9 x 1.5) + delta peak IHG
= 5.85 BTU/ft2hr + delta peak IHG
Moving it to more challenging climates, PHIUS+15 and Passive House move further apart:
Coeur D'Alene, ID: 250% annual demand; 190% peak load
Kalispell, MT: 270% annual demand; 200% peak load
Grand Rapid, MN: 300% annual demand; 220% peak load
Anchorage, AK: 530% annual demand; 190% peak load
There is definitely a lot I don't know about PHIUS+15. Perhaps there is something about its peak load calculations that I'm not thinking about accurately?
...
I'm afraid you've lost me. I don't understand how comparing Passive House and PHIUS+ 15 versions of the same house, while assuming added internal gains for the PHIUS version, can generate meaningful results? Following PHIUS rules, the PHIUS house may also assume higher efficiency for the same HRV. In reality, internal gains and HRV efficiency will be the same in both houses.
Won't the comparison underestimate PHIUS+ heating demand? (Or overestimate Passive House demand, if you look at it from that perspective?)
-Hayden
From: Passive...@googlegroups.com [mailto:Passive...@googlegroups.com] On Behalf Of Adam Cohen
Sent: Wednesday, May 13, 2015 7:52 AM
To: Passive...@googlegroups.com
Subject: Re: Response to Ryan
There is no need for any "correction". As you have pointed out, they are two similar yet different systems, so each system should be run with the systems standard assumptions.
When completed the real telling thing will be the results as i said before:
1. peak loads or more specifically conditioning equipment
2. modeled site & source energy
3. Envelope R/U Values
-Hayden
--
You're right Ryan. There's no uniform correction factor. My calculations looked at one example and was a back-of-envelope estimate. Other factors, such as higher PHIUS occupant-load and HRV-efficiency assumptions could also influence.
I think the take away is that, for the majority of heating-climate buildings, PHIUS+ 15 starts with a bigger demand number, multiplies it over a larger area, and assumes more internal gains. Peak load will tend to follow a similar pattern. This suggests that, in cases where PHIUS+ and Passive House have similar demand numbers, there is something curious happening.
But this brings me back to the long jumpers/high jumpers example. A goal of PHIUS+ is to be less expensive than Passive House.* Nothing wrong with that. The downside is expecting less performance for less money. Perhaps a fairer, more interesting comparison would be $/(kBtu/ft2yr).
-Hayden
* "It is too hard (expensive) to meet the (Passive House) standard in the colder climates. Relax there to increase adoption."
Graham S. Wright, Katrin Klingenberg, "Standard Adaptation: Upcoming changes to PHIUS+ Certification", slide 35, 8th Annual North American Passive House Conference, October 2013
From: Passive...@googlegroups.com [mailto:Passive...@googlegroups.com] On Behalf Of Ryan Abendroth
Sent: Wednesday, May 13, 2015 9:10 AM
To: Passive...@googlegroups.com
Subject: Re: Response to Ryan
I think most of the points have been thoroughly discussed, but here are some comments anyway.
I agree with Adam, that there are too many moving parts to use just a "correction" to determine. However, if a correction is used, Hayden is not that far off, though I would say in my experience, both the TFA to iCFA conversion factor and the IHG factors are higher than I have found in my experience, but even if you add a 1.25 multiplier (for iCFA) and 1.0 kBTU for IHGs there will be a much relaxed rate for heating demand (though cooling is going to get tougher, because those internal heat gains hurt).
The best comment Adam made was "My experience is that in CZ 4, there is not a huge difference between PHIUS+ and PHI envelope requirements to meet the heating and cooling demand and peak." This is a very important distinction. The target numbers may be different, but if the envelope R-values remain similar, the difference between the approaches may not be that large. Admittedly, I haven't done every comparison with my projects, but in the lower Midwest, we are talking about an inch or two of insulation difference (larger differences where its colder, probably no difference in hotter climates). Again, I don't have the magic answer because its much too nuanced for any type of absolute statement, but i do think its very important to look at the end results in addition to what the target is.
On Wednesday, May 13, 2015 at 9:51:58 AM UTC-5, Adam wrote:
There is no need for any "correction". As you have pointed out, they are two similar yet different systems, so each system should be run with the systems standard assumptions.
When completed the real telling thing will be the results as i said before:
1. peak loads or more specifically conditioning equipment
2. modeled site & source energy
3. Envelope R/U Values
--
Hayden, you must understand that the demand calc uses this higher gain (more NA correct), but the peak calc still assumes the lower IHG since PEAK is used in system sizing conservative numbers are required. The peak cooling is affected much more then the peak heating in PHIUS + compared to PHI, which as someone doing Mixed Climates is a good thing. I have always used my own calculator for PEAK Cooling load, as the PHPP was not giving me what I knew to be a correct PEAK COOLING LOAD.Hayden, I really think if you are running PHPP's you may want to compare since you seem to be interested
On Fri, May 15, 2015 at 10:11 AM, Hayden Robinson <em...@haydenrobinson.com> wrote:
You're right Ryan. There's no uniform correction factor. My calculations looked at one example and was a back-of-envelope estimate. Other factors, such as higher PHIUS occupant-load and HRV-efficiency assumptions could also influence.
I think the take away is that, for the majority of heating-climate buildings, PHIUS+ 15 starts with a bigger demand number, multiplies it over a larger area, and assumes more internal gains. Peak load will tend to follow a similar pattern. This suggests that, in cases where PHIUS+ and Passive House have similar demand numbers, there is something curious happening.
But this brings me back to the long jumpers/high jumpers example. A goal of PHIUS+ is to be less expensive than Passive House.* Nothing wrong with that. The downside is expecting less performance for less money. Perhaps a fairer, more interesting comparison would be $/(kBtu/ft2yr).
-Hayden
* "It is too hard (expensive) to meet the (Passive House) standard in the colder climates. Relax there to increase adoption."
Graham S. Wright, Katrin Klingenberg, "Standard Adaptation: Upcoming changes to PHIUS+ Certification", slide 35, 8th Annual North American Passive House Conference, October 2013
...
Adam,
If I understand you, for peak load, PHIUS+ uses the same per-square-foot internal-heat-gain assumption as Passive House - 0.51 BTU/ft2hr. This suggests that, since PHIUS+ and Passive House use different reference areas, a TFA correction factor is needed for the peak load comparison equation: delta peak-load IHG = 0.51 BTU/ft2hr x (TFA conversion factor - 1). Is this correct?
This would lead to the following equation for converting PHIUS+ peak heating load to Passive House:
<(PHIUS+ Peak Heating Load) x (TFA conversion factor)> + <0.51 BTU/ft2hr x (TFA conversion factor - 1)>
For my Seattle example, this produces:
= (3.4 BTU/ft2hr x 1.5) + <0.51 BTU/ft2hr x (1.5 - 1)> = 5.4 BTU/ft2hr
This yields a PHIUS+ peak load of about 170% of Passive House (5.4/3.2), for this example.
Of course, all of this ignores potential differences in HRV-efficiency assumptions, which could push Passive House and PHIUS+ peak load requirements much further apart.
-Hayden
--
Ryan,
As far as intent goes, PHIUS put it this way: "It is too hard (expensive) to meet the (Passive House) standard in the colder climates. Relax there to increase adoption."*
Regarding PE, for the example I'm looking at, PHIUS+ primary-energy requirements seem to have also been relaxed:
Passive House primary energy:
(11.14 kWh/ft2 per year) x (1,481 ft2) = 16,493 kWh/year
PHIUS+ primary energy:
(6,200 kwh/person per year) x (5 people) = 31,000 kWh/year
Of course, the comparison is complicated by other factors:
· PHIUS's higher PE factor for electricity appears to make things more difficult for PHIUS+ projects, but it also encourages gas furnaces/boilers, water heaters, and clothes dryers which could remove most energy from the equation.
· PHIUS's higher plug-load assumptions will make it harder on one hand, but the resulting added internal heat gains will bring down heating-demand related energy use.
· PHIUS's greater HRV-efficiency assumptions may drop on-paper heating energy demand by 20%, compared to the same HRV looked at through a Passive-House lens.
Regardless, I think it would be a shame if, as you say, PHIUS+ builders end up spending less on enclosure improvements, and more on PV. To me, the dependability, resilience, and durability of enclosure systems are worth a lot. Also, the academic literature suggests that, compared to energy conservation strategies, alternative energy production may be ineffective at limiting CO2 emissions.
-Hayden
*Graham S. Wright, Katrin Klingenberg, "Standard Adaptation: Upcoming changes to PHIUS+ Certification", slide 35, 8th Annual North American Passive House Conference, October 2013
--