Is Sensitive leakt test / Pneumatic Test can be considered as Substitute.

39 views
Skip to first unread message

pkkani...@gmail.com

unread,
Mar 19, 2016, 12:33:48 AM3/19/16
to Materials & Welding

Dear Members ,

Please clarify that whether in any circumstances we could substitute RT with pressure / any leak test for services where RT is been included as a inspection method.


Regards
Pratish

tdky167

unread,
Mar 19, 2016, 1:42:33 AM3/19/16
to pkkani...@gmail.com, material...@googlegroups.com
Dear Prakash ,

RT is applicable if its a Golden joint .  Hydrotest / pneumatic is done to check the integrity of the whole line.( welds and material ) . There are services which has 100%RT and pneumatic test as well . So I don't think RT is a option.



Sent from my Mi phone
--
http://www.linkedin.com/groups/MaterialsWelding-122787?home=&gid=122787&trk=anet_ug_hm
The views expressed/exchnaged in this group are members personel views and meant for educational purposes only, Users must take their own decisions w.r.t. applicable code/standard/contract documents.
---
You received this message because you are subscribed to the Google Groups "Materials & Welding" group.
To unsubscribe from this group and stop receiving emails from it, send an email to materials-weld...@googlegroups.com.
To post to this group, send email to material...@googlegroups.com.
To view this discussion on the web visit https://groups.google.com/d/msgid/materials-welding/f63a3157-92e6-4f84-aa59-22332c4a67c0%40googlegroups.com.
For more options, visit https://groups.google.com/d/optout.

George V Aliyattukudy

unread,
Mar 19, 2016, 5:57:17 AM3/19/16
to material...@googlegroups.com, pkkani...@gmail.com

Dear Pratish

I am considering the situation you have is on piping weld joint ( it’s not mentioned in your query). An hydrostatic leak test is only substituted with a service leak test when it is not practical to carry out one, the conditions for which are detailed in ASME B 31.3 para 354 Testing.   RT is not a substitute for a hydrostatic leak test.

 

George V Aliyattukudy


For more options, visit https://groups.google.com/d/optout.



This message, together with any attachments, contains confidential information and is intended only for the use of the addressee(s) and may contain information which is covered by legal, professional or other privilege. If you are not the intended recipient, please inform the sender immediately and delete this e-mail. You should not copy this e-mail or use it for any purpose nor disclose its contents to any other person. ENOC does not warrant that this transmission is virus free and will not be liable for any damages resulting from any virus. ENOC, Dubai, UAE

Kannayeram Gnanapandithan

unread,
Mar 19, 2016, 6:56:46 AM3/19/16
to materials-welding
RT has got tolerance ( Some discontinuities are acceptable), so it is better to pressure leak test and RT is not substitute for leak test because while doing leak test some acceptable discontinuities may open which is hindrance in service

THANKS & BEST REGARDS,
KG.PANDITHAN, IWE,  AWS-CWI, CSWIP 3.1,
CONSULTANT-WELDING & QUALITY

Lalu Rajendran

unread,
Mar 19, 2016, 7:10:27 AM3/19/16
to material...@googlegroups.com
Hi,

If RT s not possible, please go for alternate NDE methods such as UT upon your client's approval. We cannot say a joint is sound if it has survived the pressure/leak test. 

regards,
LALU

--

Kannayeram Gnanapandithan

unread,
Mar 19, 2016, 7:58:11 AM3/19/16
to materials-welding
Normally Shop made Piping spools are not leak tested inspite of RT done but it will be done at site. So noway RT can replace leak test??

THANKS & BEST REGARDS,
KG.PANDITHAN, IWE,  AWS-CWI, CSWIP 3.1,
CONSULTANT-WELDING & QUALITY

JIJILAL K M

unread,
Mar 20, 2016, 9:38:10 AM3/20/16
to material...@googlegroups.com
the objectives of RT and Hydro/pneumatic test is different. your quiery is not cleared whether it is related to pipeline,piping ,tank etc.

if ,there is a specific requirement / hindrance  or acquaintance on weld joint quality or integrity , RT is practically advisable  ,with out considering any code requirement.


JIJILAL K.M. 
​QA/QC Manager,Jurong Engineering Ltd​, Bangkok

dili...@gmail.com

unread,
Apr 1, 2016, 12:46:48 AM4/1/16
to Kannayeram Gnanapandithan
Correct